Ops, it is correct that the radiator return is connected to the return on the mixing valve?In that case you probably need to switch radiator return and underfloor heating return.It might work half decent, as it is. The mixing valve is otherwise correct mounted, 0 will take whole flow from return and 10 will take whole flow from heatpump to the underfloor flow.
If I understand correctly:- The flow to the underfloor should be mixed with the return from the underfloor- The return from the radiators should go to the heatpumpWhat is the delta the pump sees with this configuration you have?
Yes, that how it is now.The valve is correct mounted, upside down is correct here.
Well, I have found a manual on Barberi homepage....Maybe the valve is not correct mounted.It seems like it close the flow to the underfloor heating when it is closed.But you can change the valve to the right position according to the manual.Can you move the flat part on the shaft uppwords?
It is an ESBE valve you have and according to the connection it is like this. Left picture You can turn the arrows all the arrows to the opposite. Then it will be a return to the middle. And from VP at the bottom and at the top out to the floor This valve works by reversing the flow direction. Check the little black flap, which shows where it closes a gate. Do you have a motor that regulates the heat