Menu ≡
×
Startsida
Forum
NYA
OLÄSTA
ALLA
Webshop
Köpa värmepump?
Sök
Medlemmar
►
Medlemmar
◄
Visa medlemslistan
Sök efter medlemmar
Logga-in
Vanliga frågor
Registrera
Hjälp
Kontakt
Startsida
Forum
NYA
OLÄSTA
ALLA
Webshop
Köpa värmepump?
Sök
Medlemmar
Visa medlemslistan
Sök efter medlemmar
Logga-in
Vanliga frågor
Registrera
Hjälp
Kontakt
Värmepumpsforum allt om värmepump och värmepumpar
»
VärmepumpsForum Allmänt
»
Värmepumpar och installationsfrågor.
»
Värmepumpar - Mark/Berg och Sjövärmepumpar.
»
Värmepumpar - Märkesspecifikt
»
Nibe
(Moderator:
Bertil
) »
Ämne:
Nibe 1217 -10
Svara
Skicka ämnet
Skriv ut
Sidor: [
1
]
Gå ned
Författare
Ämne: Nibe 1217 -10 (läst 721 gånger)
0 medlemmar och 1 gäst tittar på detta ämne.
Kape1980
Nybörjare
Antal inlägg: 3
Karma +0/-0
Värmepump eller värmepumpar?
Kape1980
Nibe 1217 -10
«
skrivet:
24 juni 2024, 18:22:11 »
Citera
Hello from Osterbothnia!
Now, good advice is needed. Thank you in advance.
The pump, model year 2008 Nibe Fighter 1217, is not producing heat and fails to raise temperatures. The issues are as follows:
• The pump triggers an LP-LARM alarm.
• It does not generate heat.
• It makes an unpleasant noise when starting up, which eventually subsides.
• The hot water indicator light does not stay on continuously, even though the pump should be producing warm water.
These problems first appeared when we had a power failure at the main switch in the spring. After that incident, the pump started working after several attempts.
I initially thought the compressor was faulty, but fortunately, that wasn’t the case.
The situation repeated itself a week ago during a power outage in our area, where the phases were incorrectly connected. Following that, the pump started functioning after a few attempts, although I noticed an odd noise electric noise all the time behind the control panel.
Today, the pump entered LP-LARM mode and exhibits the issues I stated above.
Kaapo
P.S. How can I use the electric resistor to produce hot water if the compressor isn’t doing it?
Loggat
Josth
Dignitär inom värmepump
Stad/land: Stockholm
Antal inlägg: 10195
Karma +4/-2
Kön:
Josth
SV: Nibe 1217 -10
«
Svar #1 skrivet:
24 juni 2024, 18:59:18 »
Citera
Hello!
There are three different user manuals depending on when your F1217 was manufactured in 2008: This is the mid 2008:
https://assetstore.nibe.se/hcms/v2.4/entity/document/29051/storage/MDI5MDUxLzAvbWFzdGVy
. You can read about the LP-alarm and actions that are suggested. Generally hot water can´t be made if there is an alarm, only heat if in reserve mode.
Edit: You can try to activate "Electric boiler only" in settings menu no. 14. It might be possible to get hot water if the LP-alarm has been cleared(?)
«
Senast ändrad: 24 juni 2024, 20:40:33 av Josth
»
Loggat
1½-planshus byggt i slutet av 90-talet. 169 kvm + fristående garage 35 kvm. Kryp-/balkgrund numera tätad och avfuktare DS15 inkopplad. Vattenburet ettrörssystem med radiatorer i fyra slingor. Nibe 310P tillverkad 1997. Service: Kompressorbyte 3 ggr samt byte förångare, expansionsventil, torkmedel, pressostat, elkondensatorer, cirkulationspump, säkerhetsventil och ny kraftigare fläkt.
Kape1980
Nybörjare
Antal inlägg: 3
Karma +0/-0
Värmepump eller värmepumpar?
Kape1980
SV: Nibe 1217 -10
«
Svar #2 skrivet:
24 juni 2024, 19:20:10 »
Citera
Thank you for your answer.
It seems that lp-larm goes away after a while when pump is off. When I start pump I won't see hot water led on or heat rising even when pump is running and there is no more alarms.
Loggat
Rickard
Rickard
Administratör
Dignitär inom värmepump
Stad/land: Piteå
Antal inlägg: 35470
Karma +56/-45
Kön:
Ägare av forumet
Rickard
SV: Nibe 1217 -10
«
Svar #3 skrivet:
25 juni 2024, 08:04:59 »
Citera
After power outages, it sometimes happens that one of the phases can get a lower voltage than the the other two.
It can be a faulty connection i the main central, out in the street fuse box, in any of the terminals inside the heatpump, on one of the 2 relays that starts the kompressor.
The "electric noise" is probably on of the contactors/relays that has started to get bad, what you hear is probably the coil in the contactor humming.
If you measure the voltage between phases when the compressor is running and get the same (+-0-3V) this is not the problem, but if you measure a larger difference, start locking where the voltage drop occurs.
Low voltage on any of the phases means that the compressor coils get warm, and the compressor might get så hot the coils inside are damaged.
There is a relay protecting the compressor for things like this, but they are usually adjusted to protect for complete power failure on one of the phases, not just lower voltage.
I dont know if your model has got a soft start relay, but if it has, this has also been a quite common problem, they break and can lead to kompressor failiure if not diagnosed quite rapidly.
Also, if voltage gets low on the phase that supplies the pump for brine fluid, LP alarm can be triggered due to low pump capacity.
It might also effect the circuit bords in the heatpump not to work properly.
I would start checking voltage between phases on the last terminal closest to the kompressor when the compressor runs.
Loggat
Webbshop för energisparare:
www.energibutiken.se
Till forumets kostnadsfria Offerttjänst
:
https://www.energioffert.se
Min loggade anläggning:
https://e-logger.se/pub?rmarklund
Mina andra forum:
www.poolforum.se
och:
www.atvforum.se
Konverterat från direktverkande elradiatorer till vattenburet och värmepump 2003. Hus: Älvsbyhus -75, Ort PITEÅ, uppvärmd yta ca 170 m2. Värmepump Nibe 1255-12, 500 meter ytjord-kollektor i en slinga, 14 st Korado radiatorer,2-rörs vattenburet system. Utomhuspool 4 X 8 meter som värms med värmepump till ca 32 grader under maj-sept.
38 stycken solceller, Hanersun TCP18-54HB415W, Total teoretisk effekt 15770 W.
Invertern är en Hybrid från Growatt på 15 kW, och batterierna är Growatt APX HV Battery 15 kW, Power Module APX 98020-P1/APX 98034-P2
Yrke: Egen företagare, bakgrund: Systemtekniker med inriktning mot styr/regler. 3 års yrkesutbildning + diverse internutbildningar, 20 års yrkeserfarenhet.
Allt om mig:
http://www.varmepumpsforum.com/vpforum/index.php?topic=5196.msg48236#msg48236
Kape1980
Nybörjare
Antal inlägg: 3
Karma +0/-0
Värmepump eller värmepumpar?
Kape1980
SV: Nibe 1217 -10
«
Svar #4 skrivet:
25 juni 2024, 16:50:07 »
Citera
Thank you Rickard!
I was suspecting soft start relay. I found good Nibe mechanic not so far away. He promised to visit friday. He also have soft start relays in his van. Let's hope it's some of the relays and it hasn't done much damage to compressor yet.
I will let you know how things turn out.
Loggat
Svara
Skicka ämnet
Skriv ut
Sidor: [
1
]
Gå upp
Värmepumpsforum allt om värmepump och värmepumpar
»
VärmepumpsForum Allmänt
»
Värmepumpar och installationsfrågor.
»
Värmepumpar - Mark/Berg och Sjövärmepumpar.
»
Värmepumpar - Märkesspecifikt
»
Nibe
(Moderator:
Bertil
) »
Ämne:
Nibe 1217 -10
Annonser
Right Block
Online just nu!
gäster: 1523
dolda: 0
användare: 9
Användare online
:
danne824
AÖd
EvertL
TS Comfort AB
alvinpalv
rocas
Essel
T Ramsmark
BiggerDigger
Cookies hjälper oss att ge dig en bättre upplevelse av vår webbsida. Genom att använda vår webbplats godkänner du även användningen av cookies.
OK
Mer info