Författare Ämne: Kommunikation Mot X11/X15 (Rego800)  (läst 54533 gånger)
SV: Kommunikation Mot X11/X15 (Rego800)
« Svar #60 skrivet: 12 januari 2011, 21:07:01 »
I have to ask this question in English because of my poor Swedish :-)
Which kind of CAN cable it should be for Rego800 controller? Is CAN/RS232 Adapter V3 okay for this purpose? IVT of Finland is not selling their own communication cables so do you know where to buy these?
I have an adapter from Lawicel, http://www.lawicel-shop.se/shop/
Thanks! Do you mean Artikelnr: CAN232 ?
Do you know where to buy connector for IVT CAN bus board (model X11/X15, Interface-konakt IVT 290 A/W)?
Yes, Can232 (Or the USB-variant, wich is the same adapter combined with an FTDI USB-RS232 converter).
There is no special connectors - The canBus-wire is attached to screw terminals in the 290 A/W (The endpoint is at the display board, or at the power guard if installed). At the other end, you use a standard DB9F connector.
Utloggad jone
  • Antal inlägg: 4
« Svar #61 skrivet: 13 januari 2011, 09:00:48 »
Okay, thanks! And you don't need any 120 ohm termination resistor for CAN bus? Does this adapter work in Rego1000 model?
« Svar #62 skrivet: 13 januari 2011, 09:06:23 »
The busmust be terminated at each end. In the pump and boiler you can activate the termination vith a switch. I you connect your adapter to the display card (via a cable) you have to deactivate the termination there and use a resistor at the adapter instead.
This picture shows how the bus is 'routed' through the system:
Utloggad jone
  • Antal inlägg: 4
« Svar #63 skrivet: 13 januari 2011, 11:04:55 »
Okay, I will test when adapter arrive. So do you have knowledge of Rego1000 communication? I mean that does this adapter work in Rego1000 model?
« Svar #64 skrivet: 13 januari 2011, 11:16:16 »
The adapter will work on all systems that uses CanBus.
Utloggad Quart
  • Problemlösare
  • Antal inlägg: 87
  • Sågs senast i Efterlyst på TV3
    • Sundshult.se
« Svar #65 skrivet: 13 januari 2011, 12:11:37 »
Kan man som icke canbus kunnig få lite hjälp att komma igång med loggning, är beredd att betala för att få hjälp  :)
Väderloggande
Elloggande
RC Flygbilder.
http://www.sundshult.se
Utloggad Quart
  • Problemlösare
  • Antal inlägg: 87
    • Sundshult.se
« Svar #66 skrivet: 26 april 2011, 15:28:28 »
bumpar lite.....
Väderloggande
Elloggande
RC Flygbilder.
Utloggad ricott
  • Antal inlägg: 7
« Svar #67 skrivet: 07 augusti 2014, 22:42:23 »
Försöker förstå vart man skall koppla på en canusb om man vill börja labba med datan. Gäller en ivt 200 a/w
Tittat här och förstått att man behöver ett motstånd, http://www.can232.com/?page_id=16.
Har ni ngn speciell kabel från canusb till ivt? Svarta fyrkantiga kontakten verkar smidig, behövs väl även ngt för porten i canusb'n.
Är det här jag skall koppla in mig? Tittade på de andra korten och där verkar kedjan fortsätta.
Som ni förstår är det mkt som är nytt för mig här  dontknow
« Svar #68 skrivet: 08 augusti 2014, 07:05:02 »
Det finns två sätt att koppla in sig. Antingen där bus'en slutar (och termineringsmotståndet är inkopplat med den lilla svarta strömbrytaren. Då får du stänga av termineringen där och terminera med ett motstånd vid datoradaptern istället.
Eller så kopplar du in dig mitt på bussen, dvs tar bort en av kablarna mellan korten i VP'n och sätter dit en kabel som går från ena kortet, via adaptern och till det andra kortet.
Oavsett hur du gör så är det enklast att koppla in sig på de gröna skruvplintarna. Dom är parallellkopplade med de svarta fyrkantiga kontakterna...
Utloggad ricott
  • Antal inlägg: 7
« Svar #69 skrivet: 29 augusti 2014, 21:01:21 »
Det var rätt ställe jag markerat på bilden  tummenupp
En arduino due för $20 och en SN65HVD230 CAN Board för $9 senare så ramlar värdena in snyggt.
Kör med pumpdata.xsl som jag laddade ner från ett tidigare inlägg i denna tråd, matchar mina värden rakt av. Ovärderligt att kunna kopiera can bus id'n rakt av, betydelsen av dem alltså. Stort tack till alla som gjort detta möjligt.
Inte klar i mitt tänk kring gateway, tänker bygga in mer loggning/automation i huset och har tittat mkt på mysensors.org, tänker dock inte köra med Vera. Inte fått allt jag beställt så kan inte börja bygga fler sensorer ännu.
Utloggad LHelge
  • Antal inlägg: 5
« Svar #70 skrivet: 25 september 2014, 22:28:34 »
Väldigt intressant! Jag ska ta med mig jobbdatorn hem i helgen och logga lite CAN-trafik från min pump. Är lite sugen på att sätta ihop en logger med en STM32 processor, CAN-interface och WLAN-modul som petar in data på en server. Finns det någon sammanställning över CAN-fynden såhär långt? då menar jag ID:n, bithastighet, DLC, byte-order osv...
För att hjälpa processen framåt lite kan jag avslöja kodningen på temperaturerna. Rätt självklart om man tittar på vilken siffra som representerar 25 grader. Bosch har varit så slöa att de skickar värdet för AD-omvandlaren direkt ut på bussen. Någon nämnde att det är 4,7 kOhm NTC-resistorer som används som givare. Med ett lika stort förkopplingsmotstånd, 3.3 V spänningsreferens och en 10-bitars AD-omvandlare får man följande funktion för att räkna ut temperaturen.
Kodstycke: [Välj]
U_ref = 3.3;
R_pre = 4700;
R_ref = 4700;
A1 = 3.354016e-3;
B1 = 2.569850e-4;
C1 = 2.620131e-6;
D1 = 6.383091e-8;
U = U_ref * (ad+1)/1024;
R = U*R_pre/(U_ref-U);
T = 1/(A1 + B1*log(R/R_ref) + C1*log(R/R_ref)^2 + D1*log(R/R_ref)^3) - 273.15;
Värdena för A1, B2, C1 och D1 är hämtade från denna:
https://www.elfa.se/elfa3~se_sv/elfa/init.do?item=60-260-25&toc=19509
Följande plot visar ett svep från 0 till 1023 i blått med agw:s värden i rött ovanför.
Utloggad LHelge
  • Antal inlägg: 5
« Svar #71 skrivet: 25 september 2014, 22:30:20 »
Gjorde två lookup-tables med, en för flyttal och en för heltal multiplicerat med 10.
Kodstycke: [Välj]
static const float TempLookup[1024] = { 322.9453,  270.9837,  244.3900,  226.9534,  214.1624,  204.1503,  195.9738,  189.0937,  183.1740,  177.9923,  173.3940,  169.2675,  165.5300,
162.1182,  158.9827,  156.0845,  153.3919,  150.8793,  148.5253,  146.3121,  144.2246,  142.2500,  140.3774,  138.5972,  136.9012,  135.2822,
133.7338,  132.2504,  130.8270,  129.4592,  128.1430,  126.8748,  125.6513,  124.4698,  123.3274,  122.2219,  121.1510,  120.1126,  119.1050,
118.1265,  117.1754,  116.2504,  115.3501,  114.4732,  113.6187,  112.7854,  111.9724,  111.1787,  110.4034,  109.6458,  108.9051,  108.1805,
107.4714,  106.7772,  106.0973,  105.4311,  104.7780,  104.1377,  103.5095,  102.8932,  102.2881,  101.6941,  101.1105,  100.5372,   99.9737,
99.4198,   98.8751,   98.3393,   97.8121,   97.2933,   96.7826,   96.2798,   95.7846,   95.2968,   94.8161,   94.3425,   93.8756,   93.4153,
92.9615,   92.5138,   92.0722,   91.6366,   91.2066,   90.7823,   90.3634,   89.9498,   89.5414,   89.1381,   88.7397,   88.3461,   87.9571,
87.5728,   87.1929,   86.8174,   86.4462,   86.0791,   85.7161,   85.3571,   85.0020,   84.6507,   84.3032,   83.9593,   83.6189,   83.2821,
82.9487,   82.6186,   82.2918,   81.9683,   81.6479,   81.3305,   81.0163,   80.7049,   80.3965,   80.0910,   79.7883,   79.4883,   79.1910,
78.8963,   78.6043,   78.3148,   78.0278,   77.7433,   77.4612,   77.1815,   76.9041,   76.6290,   76.3561,   76.0855,   75.8171,   75.5507,
75.2865,   75.0244,   74.7643,   74.5062,   74.2501,   73.9959,   73.7436,   73.4932,   73.2446,   72.9979,   72.7529,   72.5097,   72.2683,
72.0285,   71.7905,   71.5541,   71.3193,   71.0861,   70.8546,   70.6245,   70.3961,   70.1691,   69.9436,   69.7196,   69.4971,   69.2760,
69.0563,   68.8380,   68.6210,   68.4055,   68.1912,   67.9783,   67.7667,   67.5563,   67.3473,   67.1394,   66.9328,   66.7274,   66.5233,
66.3203,   66.1184,   65.9177,   65.7182,   65.5198,   65.3225,   65.1263,   64.9311,   64.7371,   64.5441,   64.3521,   64.1612,   63.9713,
63.7824,   63.5945,   63.4075,   63.2216,   63.0366,   62.8525,   62.6694,   62.4872,   62.3059,   62.1255,   61.9460,   61.7674,   61.5897,
61.4128,   61.2368,   61.0616,   60.8872,   60.7137,   60.5410,   60.3691,   60.1980,   60.0277,   59.8581,   59.6894,   59.5214,   59.3541,
59.1876,   59.0218,   58.8568,   58.6925,   58.5289,   58.3660,   58.2038,   58.0423,   57.8815,   57.7214,   57.5619,   57.4031,   57.2450,
57.0875,   56.9306,   56.7744,   56.6189,   56.4639,   56.3096,   56.1559,   56.0028,   55.8503,   55.6983,   55.5470,   55.3963,   55.2461,
55.0965,   54.9475,   54.7990,   54.6511,   54.5037,   54.3569,   54.2106,   54.0649,   53.9197,   53.7750,   53.6308,   53.4872,   53.3440,
53.2014,   53.0593,   52.9176,   52.7765,   52.6358,   52.4956,   52.3559,   52.2167,   52.0779,   51.9396,   51.8018,   51.6644,   51.5275,
51.3910,   51.2550,   51.1194,   50.9842,   50.8495,   50.7152,   50.5813,   50.4479,   50.3148,   50.1822,   50.0500,   49.9182,   49.7868,
49.6558,   49.5252,   49.3950,   49.2652,   49.1357,   49.0067,   48.8780,   48.7497,   48.6218,   48.4943,   48.3671,   48.2403,   48.1138,
47.9877,   47.8620,   47.7366,   47.6115,   47.4868,   47.3625,   47.2385,   47.1148,   46.9914,   46.8684,   46.7458,   46.6234,   46.5014,
46.3797,   46.2583,   46.1372,   46.0164,   45.8960,   45.7758,   45.6560,   45.5365,   45.4172,   45.2983,   45.1797,   45.0613,   44.9433,
44.8255,   44.7080,   44.5908,   44.4739,   44.3573,   44.2410,   44.1249,   44.0091,   43.8936,   43.7783,   43.6633,   43.5486,   43.4341,
43.3199,   43.2059,   43.0923,   42.9788,   42.8656,   42.7527,   42.6400,   42.5276,   42.4154,   42.3034,   42.1917,   42.0803,   41.9690,
41.8580,   41.7473,   41.6367,   41.5264,   41.4164,   41.3065,   41.1969,   41.0875,   40.9783,   40.8694,   40.7606,   40.6521,   40.5438,
40.4357,   40.3278,   40.2202,   40.1127,   40.0054,   39.8984,   39.7915,   39.6849,   39.5784,   39.4722,   39.3661,   39.2603,   39.1546,
39.0491,   38.9438,   38.8387,   38.7338,   38.6291,   38.5246,   38.4202,   38.3161,   38.2121,   38.1083,   38.0047,   37.9012,   37.7979,
37.6948,   37.5919,   37.4892,   37.3866,   37.2842,   37.1819,   37.0798,   36.9779,   36.8762,   36.7746,   36.6731,   36.5719,   36.4707,
36.3698,   36.2690,   36.1683,   36.0679,   35.9675,   35.8673,   35.7673,   35.6674,   35.5677,   35.4681,   35.3686,   35.2693,   35.1702,
35.0711,   34.9723,   34.8735,   34.7749,   34.6765,   34.5781,   34.4799,   34.3819,   34.2840,   34.1862,   34.0885,   33.9910,   33.8936,
33.7963,   33.6992,   33.6021,   33.5052,   33.4085,   33.3118,   33.2153,   33.1189,   33.0226,   32.9264,   32.8304,   32.7344,   32.6386,
32.5429,   32.4473,   32.3518,   32.2564,   32.1612,   32.0660,   31.9710,   31.8761,   31.7812,   31.6865,   31.5919,   31.4974,   31.4030,
31.3087,   31.2145,   31.1204,   31.0264,   30.9325,   30.8387,   30.7449,   30.6513,   30.5578,   30.4644,   30.3711,   30.2778,   30.1847,
30.0916,   29.9986,   29.9058,   29.8130,   29.7203,   29.6277,   29.5351,   29.4427,   29.3503,   29.2580,   29.1658,   29.0737,   28.9817,
28.8897,   28.7979,   28.7061,   28.6143,   28.5227,   28.4311,   28.3396,   28.2482,   28.1569,   28.0656,   27.9744,   27.8833,   27.7922,
27.7012,   27.6103,   27.5195,   27.4287,   27.3379,   27.2473,   27.1567,   27.0662,   26.9757,   26.8853,   26.7950,   26.7047,   26.6145,
26.5243,   26.4342,   26.3442,   26.2542,   26.1643,   26.0744,   25.9846,   25.8948,   25.8051,   25.7155,   25.6259,   25.5363,   25.4468,
25.3574,   25.2680,   25.1786,   25.0893,   25.0000,   24.9108,   24.8217,   24.7325,   24.6435,   24.5544,   24.4654,   24.3765,   24.2876,
24.1987,   24.1099,   24.0211,   23.9323,   23.8436,   23.7550,   23.6663,   23.5777,   23.4891,   23.4006,   23.3121,   23.2236,   23.1352,
23.0468,   22.9584,   22.8701,   22.7818,   22.6935,   22.6052,   22.5170,   22.4288,   22.3406,   22.2525,   22.1643,   22.0762,   21.9882,
21.9001,   21.8121,   21.7241,   21.6361,   21.5481,   21.4601,   21.3722,   21.2843,   21.1964,   21.1085,   21.0206,   20.9328,   20.8449,
20.7571,   20.6693,   20.5815,   20.4937,   20.4059,   20.3181,   20.2304,   20.1426,   20.0549,   19.9672,   19.8794,   19.7917,   19.7040,
19.6163,   19.5286,   19.4409,   19.3532,   19.2655,   19.1778,   19.0901,   19.0024,   18.9147,   18.8270,   18.7392,   18.6515,   18.5638,
18.4761,   18.3884,   18.3007,   18.2129,   18.1252,   18.0375,   17.9497,   17.8619,   17.7742,   17.6864,   17.5986,   17.5108,   17.4229,
17.3351,   17.2473,   17.1594,   17.0715,   16.9836,   16.8957,   16.8078,   16.7198,   16.6318,   16.5439,   16.4558,   16.3678,   16.2798,
16.1917,   16.1036,   16.0155,   15.9273,   15.8391,   15.7509,   15.6627,   15.5744,   15.4861,   15.3978,   15.3095,   15.2211,   15.1327,
15.0443,   14.9558,   14.8673,   14.7787,   14.6901,   14.6015,   14.5129,   14.4242,   14.3354,   14.2467,   14.1579,   14.0690,   13.9801,
13.8912,   13.8022,   13.7132,   13.6241,   13.5350,   13.4458,   13.3566,   13.2673,   13.1780,   13.0887,   12.9992,   12.9098,   12.8203,
12.7307,   12.6411,   12.5514,   12.4617,   12.3719,   12.2820,   12.1921,   12.1021,   12.0121,   11.9220,   11.8319,   11.7417,   11.6514,
11.5610,   11.4706,   11.3801,   11.2896,   11.1990,   11.1083,   11.0176,   10.9267,   10.8358,   10.7449,   10.6538,   10.5627,   10.4715,
10.3803,   10.2889,   10.1975,   10.1060,   10.0144,    9.9227,    9.8310,    9.7391,    9.6472,    9.5552,    9.4631,    9.3709,    9.2787,
  9.1863,    9.0939,    9.0013,    8.9087,    8.8160,    8.7231,    8.6302,    8.5372,    8.4441,    8.3509,    8.2575,    8.1641,    8.0706,
  7.9770,    7.8832,    7.7894,    7.6955,    7.6014,    7.5073,    7.4130,    7.3186,    7.2241,    7.1295,    7.0348,    6.9399,    6.8449,
  6.7499,    6.6547,    6.5593,    6.4639,    6.3683,    6.2726,    6.1768,    6.0808,    5.9847,    5.8885,    5.7922,    5.6957,    5.5991,
  5.5023,    5.4054,    5.3084,    5.2112,    5.1139,    5.0164,    4.9188,    4.8211,    4.7232,    4.6251,    4.5269,    4.4286,    4.3301,
  4.2314,    4.1326,    4.0336,    3.9345,    3.8352,    3.7357,    3.6361,    3.5363,    3.4363,    3.3362,    3.2359,    3.1354,    3.0348,
  2.9339,    2.8329,    2.7317,    2.6304,    2.5288,    2.4271,    2.3251,    2.2230,    2.1207,    2.0182,    1.9155,    1.8126,    1.7095,
  1.6062,    1.5027,    1.3990,    1.2951,    1.1910,    1.0867,    0.9821,    0.8774,    0.7724,    0.6672,    0.5618,    0.4561,    0.3503,
  0.2442,    0.1378,    0.0313,   -0.0755,   -0.1826,   -0.2898,   -0.3974,   -0.5051,   -0.6131,   -0.7214,   -0.8299,   -0.9387,   -1.0477,
-1.1570,   -1.2665,   -1.3764,   -1.4865,   -1.5968,   -1.7074,   -1.8183,   -1.9295,   -2.0410,   -2.1528,   -2.2648,   -2.3771,   -2.4898,
-2.6027,   -2.7159,   -2.8295,   -2.9433,   -3.0575,   -3.1719,   -3.2867,   -3.4018,   -3.5172,   -3.6330,   -3.7491,   -3.8655,   -3.9823,
-4.0994,   -4.2168,   -4.3346,   -4.4527,   -4.5712,   -4.6901,   -4.8093,   -4.9289,   -5.0489,   -5.1692,   -5.2900,   -5.4111,   -5.5326,
-5.6545,   -5.7768,   -5.8995,   -6.0226,   -6.1461,   -6.2700,   -6.3944,   -6.5192,   -6.6444,   -6.7700,   -6.8961,   -7.0226,   -7.1496,
-7.2771,   -7.4050,   -7.5334,   -7.6622,   -7.7916,   -7.9214,   -8.0517,   -8.1825,   -8.3138,   -8.4456,   -8.5780,   -8.7108,   -8.8442,
-8.9781,   -9.1126,   -9.2476,   -9.3832,   -9.5193,   -9.6560,   -9.7933,   -9.9311,  -10.0696,  -10.2087,  -10.3483,  -10.4886,  -10.6295,
-10.7711,  -10.9132,  -11.0561,  -11.1996,  -11.3437,  -11.4886,  -11.6341,  -11.7803,  -11.9272,  -12.0749,  -12.2232,  -12.3723,  -12.5222,
-12.6728,  -12.8242,  -12.9763,  -13.1293,  -13.2830,  -13.4376,  -13.5930,  -13.7492,  -13.9063,  -14.0642,  -14.2231,  -14.3828,  -14.5434,
-14.7050,  -14.8675,  -15.0309,  -15.1953,  -15.3607,  -15.5270,  -15.6944,  -15.8628,  -16.0323,  -16.2028,  -16.3745,  -16.5472,  -16.7210,
-16.8960,  -17.0721,  -17.2494,  -17.4279,  -17.6077,  -17.7887,  -17.9709,  -18.1545,  -18.3393,  -18.5255,  -18.7131,  -18.9020,  -19.0924,
-19.2842,  -19.4775,  -19.6723,  -19.8686,  -20.0665,  -20.2659,  -20.4671,  -20.6698,  -20.8743,  -21.0805,  -21.2885,  -21.4982,  -21.7099,
-21.9234,  -22.1388,  -22.3562,  -22.5757,  -22.7972,  -23.0208,  -23.2466,  -23.4746,  -23.7049,  -23.9375,  -24.1725,  -24.4100,  -24.6499,
-24.8924,  -25.1376,  -25.3855,  -25.6361,  -25.8897,  -26.1461,  -26.4056,  -26.6682,  -26.9340,  -27.2030,  -27.4755,  -27.7515,  -28.0310,
-28.3143,  -28.6014,  -28.8925,  -29.1876,  -29.4870,  -29.7907,  -30.0989,  -30.4118,  -30.7296,  -31.0523,  -31.3803,  -31.7136,  -32.0526,
-32.3974,  -32.7482,  -33.1054,  -33.4691,  -33.8397,  -34.2175,  -34.6027,  -34.9958,  -35.3971,  -35.8069,  -36.2258,  -36.6542,  -37.0925,
-37.5413,  -38.0012,  -38.4729,  -38.9569,  -39.4541,  -39.9653,  -40.4914,  -41.0334,  -41.5923,  -42.1695,  -42.7662,  -43.3839,  -44.0245,
-44.6898,  -45.3820,  -46.1036,  -46.8575,  -47.6470,  -48.4760,  -49.3490,  -50.2714,  -51.2498,  -52.2920,  -53.4077,  -54.6091,  -55.9118,
-57.3360,  -58.9090,  -60.6685,  -62.6693,  -64.9950,  -67.7838,  -71.2897,  -76.0689,  -83.8330, -273.1500 };
static const uint32_t TempLookup[1024] = { 3229, 2710, 2444, 2270, 2142, 2042, 1960, 1891, 1832, 1780,
1734, 1693, 1655, 1621, 1590, 1561, 1534, 1509, 1485, 1463,
1442, 1422, 1404, 1386, 1369, 1353, 1337, 1323, 1308, 1295,
1281, 1269, 1257, 1245, 1233, 1222, 1212, 1201, 1191, 1181,
1172, 1163, 1154, 1145, 1136, 1128, 1120, 1112, 1104, 1096,
1089, 1082, 1075, 1068, 1061, 1054, 1048, 1041, 1035, 1029,
1023, 1017, 1011, 1005, 1000,  994,  989,  983,  978,  973,
968,  963,  958,  953,  948,  943,  939,  934,  930,  925,
921,  916,  912,  908,  904,  899,  895,  891,  887,  883,
880,  876,  872,  868,  864,  861,  857,  854,  850,  847,
843,  840,  836,  833,  829,  826,  823,  820,  816,  813,
810,  807,  804,  801,  798,  795,  792,  789,  786,  783,
780,  777,  775,  772,  769,  766,  764,  761,  758,  756,
753,  750,  748,  745,  743,  740,  737,  735,  732,  730,
728,  725,  723,  720,  718,  716,  713,  711,  709,  706,
704,  702,  699,  697,  695,  693,  691,  688,  686,  684,
682,  680,  678,  676,  673,  671,  669,  667,  665,  663,
661,  659,  657,  655,  653,  651,  649,  647,  645,  644,
642,  640,  638,  636,  634,  632,  630,  629,  627,  625,
623,  621,  619,  618,  616,  614,  612,  611,  609,  607,
605,  604,  602,  600,  599,  597,  595,  594,  592,  590,
589,  587,  585,  584,  582,  580,  579,  577,  576,  574,
572,  571,  569,  568,  566,  565,  563,  562,  560,  559,
557,  555,  554,  552,  551,  549,  548,  547,  545,  544,
542,  541,  539,  538,  536,  535,  533,  532,  531,  529,
528,  526,  525,  524,  522,  521,  519,  518,  517,  515,
514,  513,  511,  510,  508,  507,  506,  504,  503,  502,
501,  499,  498,  497,  495,  494,  493,  491,  490,  489,
487,  486,  485,  484,  482,  481,  480,  479,  477,  476,
475,  474,  472,  471,  470,  469,  467,  466,  465,  464,
463,  461,  460,  459,  458,  457,  455,  454,  453,  452,
451,  449,  448,  447,  446,  445,  444,  442,  441,  440,
439,  438,  437,  435,  434,  433,  432,  431,  430,  429,
428,  426,  425,  424,  423,  422,  421,  420,  419,  417,
416,  415,  414,  413,  412,  411,  410,  409,  408,  407,
405,  404,  403,  402,  401,  400,  399,  398,  397,  396,
395,  394,  393,  392,  390,  389,  388,  387,  386,  385,
384,  383,  382,  381,  380,  379,  378,  377,  376,  375,
374,  373,  372,  371,  370,  369,  368,  367,  366,  365,
364,  363,  362,  361,  360,  359,  358,  357,  356,  355,
354,  353,  352,  351,  350,  349,  348,  347,  346,  345,
344,  343,  342,  341,  340,  339,  338,  337,  336,  335,
334,  333,  332,  331,  330,  329,  328,  327,  326,  325,
324,  324,  323,  322,  321,  320,  319,  318,  317,  316,
315,  314,  313,  312,  311,  310,  309,  308,  307,  307,
306,  305,  304,  303,  302,  301,  300,  299,  298,  297,
296,  295,  294,  294,  293,  292,  291,  290,  289,  288,
287,  286,  285,  284,  283,  282,  282,  281,  280,  279,
278,  277,  276,  275,  274,  273,  272,  272,  271,  270,
269,  268,  267,  266,  265,  264,  263,  263,  262,  261,
260,  259,  258,  257,  256,  255,  254,  254,  253,  252,
251,  250,  249,  248,  247,  246,  246,  245,  244,  243,
242,  241,  240,  239,  238,  238,  237,  236,  235,  234,
233,  232,  231,  230,  230,  229,  228,  227,  226,  225,
224,  223,  223,  222,  221,  220,  219,  218,  217,  216,
215,  215,  214,  213,  212,  211,  210,  209,  208,  208,
207,  206,  205,  204,  203,  202,  201,  201,  200,  199,
198,  197,  196,  195,  194,  194,  193,  192,  191,  190,
189,  188,  187,  187,  186,  185,  184,  183,  182,  181,
180,  179,  179,  178,  177,  176,  175,  174,  173,  172,
172,  171,  170,  169,  168,  167,  166,  165,  165,  164,
163,  162,  161,  160,  159,  158,  158,  157,  156,  155,
154,  153,  152,  151,  150,  150,  149,  148,  147,  146,
145,  144,  143,  142,  142,  141,  140,  139,  138,  137,
136,  135,  134,  134,  133,  132,  131,  130,  129,  128,
127,  126,  126,  125,  124,  123,  122,  121,  120,  119,
118,  117,  117,  116,  115,  114,  113,  112,  111,  110,
109,  108,  107,  107,  106,  105,  104,  103,  102,  101,
100,   99,   98,   97,   96,   96,   95,   94,   93,   92,
  91,   90,   89,   88,   87,   86,   85,   84,   84,   83,
  82,   81,   80,   79,   78,   77,   76,   75,   74,   73,
  72,   71,   70,   69,   68,   67,   67,   66,   65,   64,
  63,   62,   61,   60,   59,   58,   57,   56,   55,   54,
  53,   52,   51,   50,   49,   48,   47,   46,   45,   44,
  43,   42,   41,   40,   39,   38,   37,   36,   35,   34,
  33,   32,   31,   30,   29,   28,   27,   26,   25,   24,
  23,   22,   21,   20,   19,   18,   17,   16,   15,   14,
  13,   12,   11,   10,    9,    8,    7,    6,    5,    4,
   2,    1,    0,   -1,   -2,   -3,   -4,   -5,   -6,   -7,
  -8,   -9,  -10,  -12,  -13,  -14,  -15,  -16,  -17,  -18,
-19,  -20,  -22,  -23,  -24,  -25,  -26,  -27,  -28,  -29,
-31,  -32,  -33,  -34,  -35,  -36,  -37,  -39,  -40,  -41,
-42,  -43,  -45,  -46,  -47,  -48,  -49,  -50,  -52,  -53,
-54,  -55,  -57,  -58,  -59,  -60,  -61,  -63,  -64,  -65,
-66,  -68,  -69,  -70,  -71,  -73,  -74,  -75,  -77,  -78,
-79,  -81,  -82,  -83,  -84,  -86,  -87,  -88,  -90,  -91,
-92,  -94,  -95,  -97,  -98,  -99, -101, -102, -103, -105,
-106, -108, -109, -111, -112, -113, -115, -116, -118, -119,
-121, -122, -124, -125, -127, -128, -130, -131, -133, -134,
-136, -137, -139, -141, -142, -144, -145, -147, -149, -150,
-152, -154, -155, -157, -159, -160, -162, -164, -165, -167,
-169, -171, -172, -174, -176, -178, -180, -182, -183, -185,
-187, -189, -191, -193, -195, -197, -199, -201, -203, -205,
-207, -209, -211, -213, -215, -217, -219, -221, -224, -226,
-228, -230, -232, -235, -237, -239, -242, -244, -246, -249,
-251, -254, -256, -259, -261, -264, -267, -269, -272, -275,
-278, -280, -283, -286, -289, -292, -295, -298, -301, -304,
-307, -311, -314, -317, -321, -324, -327, -331, -335, -338,
-342, -346, -350, -354, -358, -362, -367, -371, -375, -380,
-385, -390, -395, -400, -405, -410, -416, -422, -428, -434,
-440, -447, -454, -461, -469, -476, -485, -493, -503, -512,
-523, -534, -546, -559, -573, -589, -607, -627, -650, -678,
-713, -761, -838,-2732 };
Utloggad agw
  • Antal inlägg: 40
« Svar #72 skrivet: 01 juni 2016, 16:18:58 »
Tiden går fort när man har annat att göra. Mitt Canbusprojekt dog i en överspänningsspik tillsammans med all elektronik i Värmepumpen typ 2010...
Nu några år senare blev jag sugen igen och har återskapat det mesta av projektet med hjälp av gamla filer och loggar. Hittade nu den här gamla tråden och tänkte bara bumpa lite.
Det har ju hänt en del på 6 år, jag beställde nu en Raspberry PI och ett PICAN2 interface. Rullade på ubuntu, drog igång wireless, kopplade in mig i min IVT (REGO1000), skrev #candump -t A can0 och såg välbekanta CID:ar rulla in :)
Vet att flera tagit sina projekt hög nivå men min kunskapsbrist i programmering tvingar mig till enkla lösningar.
Har ett antal script som snyggar till datan och använder MRTG som plottar fina grafer. Enkelt och överskådligt.
MVH
/AGW
Utloggad MortenOlesen
  • Antal inlägg: 3
« Svar #73 skrivet: 17 juli 2016, 20:50:18 »
Hi agw
I too have a Raspberry Pi 2 with a PICAN 2 module, but I'm not getting any data.
1. Which Baudrate did you use in the ip link line?
I use
Kodstycke: [Välj]
sudo /sbin/ip link set can0 up type can bitrate 14400but the bitrate may be wrong?
2. How did you connect the PICAN 2 to the heatpump?
I have an IVT Greenline HE E9 (I think the controller is a REGO 1000) and I connected using the black screw connector on the I/O board with numbers 35-38 like this:
35 - PICAN 2 Ground
36 - PICAN 2 Can L
37 - PICAN 2 Can H
38 - PICAN 2 +12V (I have the version with SMPS on board to power the Pi)
I shorted the JP3 on PICAN 2 to enable the 120 Ohm termination and I moved the switch on the I/O board away from "Term". This way I hope to move the termination to the PICAN 2 as the last node.
Did you do anything different to make it work?
BTW I'm hoping to use TaloLoggerPi and I'm in communication with the author in order to integrate PICAN 2 with his system.
Thanks Morten
« Senast ändrad: 17 juli 2016, 20:56:38 av MortenOlesen »
Utloggad agw
  • Antal inlägg: 40
« Svar #74 skrivet: 17 juli 2016, 21:26:27 »
/sbin/ip link set can0 up type can bitrate 125000 is correct for the REGO 1000
The bitrate seems quite important, If you try like 500 000 you will cause the system to die with a "dying gasp."
Please let me know if this solves it.
BR
/AGW