	Title	Info	F370	F470	F750	F730	F1255	F1245	F1355	F1345	SMO20	SMO40	VVM225	VVM310	Unit	Size	Factor	Min	Max	Default	Mode
32260	NIBE Inverter 216-state				32260	32260	32260									u8	1	0	0	0	R
40004	BT1 Outdoor Temperature	Current outdoor temperature	40004	40004	40004	40004	40004	40004	40004	40004	40004	40004	40004	40004	°C	s16	10	0	0	0	R
40005	EP23-BT2 Supply temp S4	Supply temperature for system 4	40005	40005	40005	40005	40005	40005	40005	40005		40005	40005	40005	°C	s16	10	0	0	0	R
40006	EP22-BT2 Supply temp S3	Supply temperature for system 3	40006	40006	40006	40006	40006	40006	40006	40006		40006	40006	40006	°C	s16	10	0	0	0	R
40007	EP21-BT2 Supply temp S2	Supply temperature for system 2	40007	40007	40007	40007	40007	40007	40007	40007		40007	40007	40007	°C	s16	10	0	0	0	R
40008	BT2 Supply temp S1	Supply temperature for system 1	40008	40008	40008	40008	40008	40008	40008				40008	40008	°C	s16	10	0	0	0	R
40011	EB100-EP15-BT3 Return temp								40011	40011					°C	s16	10	0	0	0	R
40012	EB100-EP14-BT3 Return temp	Return temperature	40012	40012	40012	40012	40012	40012	40012	40012	40012	40012	40012	40012	°C	s16	10	0	0	0	R
40013	BT7 HW Top	Hot water top temperature, BT7	40013	40013	40013	40013	40013	40013	40013	40013	40013	40013	40013	40013	°C	s16	10	0	0	0	R
40014	BT6 HW Load	Hot water load temperature, BT6	40014	40014	40014	40014	40014	40014	40014	40014	40014	40014	40014	40014	°C	s16	10	0	0	0	R
40015	EB100-EP14-BT10 Brine In Temp	Brine in temperature, BT10					40015	40015	40015	40015					°C	s16	10	0	0	0	R
40016	EB100-EP14-BT11 Brine Out Temp	Brine out temperature, BT11					40016	40016	40016	40016					°C	s16	10	0	0	0	R
40017	EB100-EP14-BT12 Condensor Out	Condensor out temperature, BT12			40017	40017	40017	40017	40017	40017					°C	s16	10	0	0	0	R
40018	EB100-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14			40018	40018	40018	40018	40018	40018					°C	s16	10	0	0	0	R
40019	EB100-EP14-BT15 Liquid Line	Liquid line temperature, BT15			40019	40019	40019	40019	40019	40019					°C	s16	10	0	0	0	R
40020	EB100-BT16 Evaporator temp		40020	40020	40020	40020									°C	s16	10	0	0	0	R
40022	EB100-EP14-BT17 Suction	Suction temperature, BT17	40022	40022	40022	40022	40022	40022	40022	40022					°C	s16	10	0	0	0	R
40023	EB100-BT18 Compressor temp.	Valid only for F3/470	40023	40023											°C	s16	10	0	0	0	R
40024	EB100-BT19 Addition temp.	Valid only for F3/470	40024	40024											°C	s16	10	0	0	0	R
40025	BT20 Exhaust air temp. 1		40025	40025	40025	40025	40025	40025	40025	40025		40025	40025	40025	°C	s16	10	0	0	0	R
40026	BT21 Vented air temp. 1		40026	40026	40026	40026	40026	40026	40026	40026		40026	40026	40026	°C	s16	10	0	0	0	R
40028	AZ1-BT26 Temp Collector in FLM 1	Connected to the FLM module					40028	40028	40028	40028					°C	s16	10	0	0	0	R
40029	AZ1-BT27 Temp Collector out FLM 1	Connected to the FLM module					40029	40029	40029	40029					°C	s16	10	0	0	0	R
40030	EP23-BT50 Room Temp S4		40030	40030	40030	40030	40030	40030	40030	40030		40030	40030	40030	°C	s16	10	0	0	0	R
40031	EP22-BT50 Room Temp S3		40031	40031	40031	40031	40031	40031	40031	40031		40031	40031	40031	°C	s16	10	0	0	0	R
40032	EP21-BT50 Room Temp S2		40032	40032	40032	40032	40032	40032	40032	40032		40032	40032	40032	°C	s16	10	0	0	0	R
40033	BT50 Room Temp S1		40033	40033	40033	40033	40033	40033	40033	40033	40033	40033	40033	40033	°C	s16	10	0	0	0	R
40042	CL11-BT51 Pool 1 Temp	Pool temperature for Pool 1, BT51					40042	40042	40042	40042		40042	40042	40042	°C	s16	10	0	0	0	R
40043	BT53 Solar Panel Temp	Used in Solar and AHPS Docking accessories	40043	40043	40043	40043	40043	40043	40043	40043		40043		40043	°C	s16	10	0	0	0	R
40044	BT54 Solar Load Temp	Used in Solar and AHPS Docking accessories	40044	40044	40044	40044	40044	40044	40044	40044		40044		40044	°C	s16	10	0	0	0	R
40045	EQ1-BT64 Cool Supply Temp	Cool supply temperature, BT64					40045	40045	40045	40045	40045	40045	40045	40045	°C	s16	10	0	0	0	R
40046	EQ1-BT65 Cool Return Temp	Cool return temperature, BT65					40046	40046	40046	40046					°C	s16	10	0	0	0	R
40047	EB100-BT61 Supply Radiator Temp				40047										°C	s16	10	0	0	0	R
40048	EB100-BT62 Return Radiator Temp				40048										°C	s16	10	0	0	0	R
40050	EB100-BS1 Air flow				40050	40050										s16	10	0	0	0	R
40051	EB100-BS1 Air flow unfiltered	Unfiltered air flow value			40051	40051										s16	100	0	0	0	R
40054	EB100-FD1 Temperature limiter		40054	40054	40054	40054	40054	40054	40054	40054	40054	40054	40054	40054		s16	1	0	0	0	R
40067	BT1 Average	EB100-BT1 Outdoor temperature average	40067	40067	40067	40067	40067	40067	40067	40067	40067	40067	40067	40067	°C	s16	10	0	0	0	R
40070	EM1-BT52 Boiler Temperature	Boiler temperature, BT52					40070	40070	40070	40070		40070	40070	40070	°C	s16	10	0	0	0	R
40071	BT25 Ext. Supply	External supply temperature, BT25	40071	40071	40071	40071	40071	40071	40071	40071	40071	40071	40071		°C	s16	10	0	0	0	R
40072	BF1 EP14 Flow	Current flow EP14|Current flow EP15			40072	40072	40072	40072	40072	40072		40072	40072	40072	l/m	s16	10	0	0	0	R
40074	EB100-FR1 Anode Status		40074	40074	40074	40074	40074	40074			40074	40074	40074	40074		s16	1	0	0	0	R
40075	BT22 Supply air temp.		40075	40075			40075	40075	40075	40075		40075	40075	40075	°C	s16	10	0	0	0	R
40076	EP30-BT55 Solar Tank Top Temp		40076	40076											°C	s16	10	0	0	0	R
40077	BT6 external water heater load temp.	Used in DEW, SCA and AHPS Docking accessories			40077	40077									°C	s16	10	0	0	0	R
40078	BT7 external water heater top temp.	Used in DEW, SCA and AHPS Docking accessories			40078	40078									°C	s16	10	0	0	0	R
40079	EB100-BE3 Current		40079	40079	40079	40079	40079	40079	40079	40079		40079	40079	40079	A	u32	10	0	0	0	R
40081	EB100-BE2 Current		40081	40081	40081	40081	40081	40081	40081	40081		40081	40081	40081	A	u32	10	0	0	0	R
40083	EB100-BE1 Current		40083	40083	40083	40083	40083	40083	40083	40083		40083	40083	40083	A	u32	10	0	0	0	R
40085	EB100-EP15-BT11 Brine Out Temp	Brine out temperature, BT11							40085	40085					°C	s16	10	0	0	0	R
40086	EB100-EP15-BT12 Condensor Out	Condensor out temperature, BT12							40086	40086					°C	s16	10	0	0	0	R
40087	EB100-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14							40087	40087					°C	s16	10	0	0	0	R
40088	EB100-EP15-BT15 Liquid Line	Liquid line temperature, BT15							40088	40088					°C	s16	10	0	0	0	R
40089	EB100-EP15-BT17 Suction	Suction temperature, BT17							40089	40089					°C	s16	10	0	0	0	R
40100	EB100-EP15-BT10 Brine In Temp	Brine in temperature, BT10							40100	40100					°C	s16	10	0	0	0	R
40106	CL12-BT51 Pool 2 Temp	Pool temperature for Pool 2, BT51					40106	40106	40106	40106		40106			°C	s16	10	0	0	0	R
40107	BT20 Exhaust air temp. 4						40107	40107	40107	40107					°C	s16	10	0	0	0	R
40108	BT20 Exhaust air temp. 3						40108	40108	40108	40108					°C	s16	10	0	0	0	R
40109	BT20 Exhaust air temp. 2						40109	40109	40109	40109					°C	s16	10	0	0	0	R
40110	BT21 Vented air temp. 4						40110	40110	40110	40110					°C	s16	10	0	0	0	R
40111	BT21 Vented air temp. 3						40111	40111	40111	40111					°C	s16	10	0	0	0	R
40112	BT21 Vented air temp. 2						40112	40112	40112	40112					°C	s16	10	0	0	0	R
40113	AZ4-BT26 Temp Collector in FLM 4	Connected to the FLM module					40113	40113	40113	40113					°C	s16	10	0	0	0	R
40114	AZ3-BT26 Temp Collector in FLM 3	Connected to the FLM module					40114	40114	40114	40114					°C	s16	10	0	0	0	R
40115	AZ2-BT26 Temp Collector in FLM 2	Connected to the FLM module					40115	40115	40115	40115					°C	s16	10	0	0	0	R
40116	AZ4-BT27 Temp Collector out FLM 4	Connected to the FLM module					40116	40116	40116	40116					°C	s16	10	0	0	0	R
40117	AZ3-BT27 Temp Collector out FLM 3	Connected to the FLM module					40117	40117	40117	40117					°C	s16	10	0	0	0	R
40118	AZ2-BT27 Temp Collector out FLM 2	Connected to the FLM module					40118	40118	40118	40118					°C	s16	10	0	0	0	R
40121	BT63 Add Supply Temp										40121	40121	40121	40121	ºC	s16	10	0	0	0	R
40122	BT52 external water heater load temp.	Used in DEH and AHPS Docking accessories	40122	40122	40122										°C	s16	10	0	0	0	R
40127	EP23-BT3 Return temp S4	Return temperature for system 4	40127	40127	40127	40127	40127	40127	40127	40127		40127	40127	40127	°C	s16	10	0	0	0	R
40128	EP22-BT3 Return temp S3	Return temperature for system 3	40128	40128	40128	40128	40128	40128	40128	40128		40128	40128	40128	°C	s16	10	0	0	0	R
40129	EP21-BT3 Return temp S2	Return temperature for system 2	40129	40129	40129	40129	40129	40129	40129	40129		40129	40129	40129	°C	s16	10	0	0	0	R
40131	EB100-EP15-BP8 Pressure Transmitter	Temperature reported by the pressure transmitter							40131	40131					°C	s16	10	0	0	0	R
40132	EB100-EP14-BP8 Pressure Transmitter	Temperature reported by the pressure transmitter							40132	40132					°C	s16	10	0	0	0	R
40141	AZ2-BT22 Supply air temp. SAM				40141										°C	s16	10	0	0	0	R
40142	AZ2-BT23 Outdoor temp. SAM				40142										°C	s16	10	0	0	0	R
40143	AZ2-BT68 Flow temp. SAM	Heat medium flow temperature to SAM module			40143										°C	s16	10	0	0	0	R
40144	AZ2-BT69 Return temp. SAM	Heat medium return temperature from SAM module			40144										°C	s16	10	0	0	0	R
40145	EB100-EP15-BT29 Cpr Oil Temp	Compressor oil temperature, BT29							40145	40145					°C	s16	10	0	0	0	R
40146	EB100-EP14-BT29 Cpr Oil Temp	Compressor oil temperature, BT29					40146		40146	40146					°C	s16	10	0	0	0	R
40147	BT70 HW Comfort Supply Temp.	Hot water comfort supply temperature, BT70					40147	40147	40147	40147		40147	40147		°C	s16	10	0	0	0	R
40152	BT71 Ext. Return Temp	External return temperature, BT71						40152	40152	40152	40152	40152			°C	s16	10	0	0	0	R
40154	EP30-BT51 Solar pool Temp													40154	°C	s16	10	0	0	0	R
40155	EQ1-BT57 Collector Temp.	External collector temperature, BT57, for ACS					40155	40155		40155					°C	s16	10	0	0	0	R
40156	EQ1-BT75 Heatdump Temp.	Heating medium dump temperature, BT75, for ACS					40156	40156		40156					°C	s16	10	0	0	0	R
40157	EP30-BT53 Solar Panel Temp				40157										°C	s16	10	0	0	0	R
40158	EP30-BT54 Solar Load Temp				40158										°C	s16	10	0	0	0	R
40159	EP47-BT2 Supply temp S8	Supply temperature for system 8	40159	40159	40159	40159	40159	40159	40159	40159		40159	40159	40159	°C	s16	10	0	0	0	R
40160	EP46-BT2 Supply temp S7	Supply temperature for system 7	40160	40160	40160	40160	40160	40160	40160	40160		40160	40160	40160	°C	s16	10	0	0	0	R
40161	EP45-BT2 Supply temp S6	Supply temperature for system 6	40161	40161	40161	40161	40161	40161	40161	40161		40161	40161	40161	°C	s16	10	0	0	0	R
40162	EP44-BT2 Supply temp S5	Supply temperature for system 5	40162	40162	40162	40162	40162	40162	40162	40162		40162	40162	40162	°C	s16	10	0	0	0	R
40163	EP47-BT3 Return temp S8	Return temperature for system 8	40163	40163	40163	40163	40163	40163	40163	40163		40163	40163	40163	°C	s16	10	0	0	0	R
40164	EP46-BT3 Return temp S7	Return temperature for system 7	40164	40164	40164	40164	40164	40164	40164	40164		40164	40164	40164	°C	s16	10	0	0	0	R
40165	EP45-BT3 Return temp S6	Return temperature for system 6	40165	40165	40165	40165	40165	40165	40165	40165		40165	40165	40165	°C	s16	10	0	0	0	R
40166	EP44-BT3 Return temp S5	Return temperature for system 5	40166	40166	40166	40166	40166	40166	40166	40166		40166	40166	40166	°C	s16	10	0	0	0	R
40167	EP47-BT50 Room Temp S8		40167	40167	40167	40167	40167	40167	40167	40167		40167	40167	40167	°C	s16	10	0	0	0	R
40168	EP46-BT50 Room Temp S7		40168	40168	40168	40168	40168	40168	40168	40168		40168	40168	40168	°C	s16	10	0	0	0	R
40169	EP45-BT50 Room Temp S6		40169	40169	40169	40169	40169	40169	40169	40169		40169	40169	40169	°C	s16	10	0	0	0	R
40170	EP44-BT50 Room Temp S5		40170	40170	40170	40170	40170	40170	40170	40170		40170	40170	40170	°C	s16	10	0	0	0	R
40179	EP10-BT26 Brine in	Brine in temperature in EP10 module							40179	40179					°C	s16	10	0	0	0	R
40183	AZ30-BT23 Outdoor temp. ERS 1						40183	40183	40183	40183		40183	40183	40183	°C	s16	10	0	0	0	R
40185	BT1 Average, 1h	EB100-BT1 Outdoor temperature average, 1h	40185	40185	40185	40185	40185	40185	40185	40185	40185	40185	40185	40185	°C	s16	10	0	0	0	R
40188	EP47-BT50 Room Temp S8 Average		40188	40188	40188	40188	40188	40188	40188	40188		40188	40188	40188	°C	s16	10	0	0	0	R
40189	EP46-BT50 Room Temp S7 Average		40189	40189	40189	40189	40189	40189	40189	40189		40189	40189	40189	°C	s16	10	0	0	0	R
40190	EP45-BT50 Room Temp S6 Average		40190	40190	40190	40190	40190	40190	40190	40190		40190	40190	40190	°C	s16	10	0	0	0	R
40191	EP44-BT50 Room Temp S5 Average		40191	40191	40191	40191	40191	40191	40191	40191		40191	40191	40191	°C	s16	10	0	0	0	R
40192	EP23-BT50 Room Temp S4 Average		40192	40192	40192	40192	40192	40192	40192	40192		40192	40192	40192	°C	s16	10	0	0	0	R
40193	EP22-BT50 Room Temp S3 Average		40193	40193	40193	40193	40193	40193	40193	40193		40193	40193	40193	°C	s16	10	0	0	0	R
40194	EP21-BT50 Room Temp S2 Average		40194	40194	40194	40194	40194	40194	40194	40194		40194	40194	40194	°C	s16	10	0	0	0	R
40195	BT50 Room Temp S1 Average		40195	40195	40195	40195	40195	40195	40195	40195	40195	40195	40195	40195	°C	s16	10	0	0	0	R
40212	BT74 Average	BT74 heating cooling sensor average	40212	40212	40212	40212	40212	40212	40212	40212	40212	40212	40212	40212	°C	s16	10	0	0	0	R
40215	BF1 EP15 Flow	Current flow EP15							40215	40215					l/m	s16	10	0	0	0	R
40216	BT25 Ext. supply temp, cooling						40216	40216	40216	40216	40216	40216	40216		°C	s16	10	0	0	0	R
40217	Calc. Supply S8	Calculated supply temperature for the climate system	40217	40217	40217	40217	40217	40217	40217	40217		40217	40217	40217	°C	s16	10	0	0	0	R
40218	Calc. Supply S7	Calculated supply temperature for the climate system	40218	40218	40218	40218	40218	40218	40218	40218		40218	40218	40218	°C	s16	10	0	0	0	R
40219	Calc. Supply S6	Calculated supply temperature for the climate system	40219	40219	40219	40219	40219	40219	40219	40219		40219	40219	40219	°C	s16	10	0	0	0	R
40220	Calculated Supply S5	Calculated supply temperature for the climate system	40220	40220	40220	40220	40220	40220	40220	40220		40220	40220	40220	°C	s16	10	0	0	0	R
40221	Calc. Cooling Supply S8	Calculated supply temperature in cooling mode for the climate system					40221	40221	40221	40221	40221	40221	40221	40221	°C	s16	10	0	0	0	R
40222	Calc. Cooling Supply S7	Calculated supply temperature in cooling mode for the climate system					40222	40222	40222	40222	40222	40222	40222	40222	°C	s16	10	0	0	0	R
40223	Calc. Cooling Supply S6	Calculated supply temperature in cooling mode for the climate system					40223	40223	40223	40223	40223	40223	40223	40223	°C	s16	10	0	0	0	R
40224	Calc. Cooling Supply S5	Calculated supply temperature in cooling mode for the climate system					40224	40224	40224	40224	40224	40224	40224	40224	°C	s16	10	0	0	0	R
40305	Mixing Valve State S8	State of the mixing valve for the climate system	40305	40305	40305	40305	40305	40305	40305	40305		40305	40305	40305		u8	1	0	0	0	R
40306	Mixing Valve State S7	State of the mixing valve for the climate system	40306	40306	40306	40306	40306	40306	40306	40306		40306	40306	40306		u8	1	0	0	0	R
40307	Mixing Valve State S6	State of the mixing valve for the climate system	40307	40307	40307	40307	40307	40307	40307	40307		40307	40307	40307		u8	1	0	0	0	R
40308	Mixing Valve State S5	State of the mixing valve for the climate system	40308	40308	40308	40308	40308	40308	40308	40308		40308	40308	40308		u8	1	0	0	0	R
40310	External ERS 1 accessory relays	Indicates the status of the relays on the ERS accessory. The information is binary encoded. b0: K1, b1: K2, b2: K3, b3: K4					40310	40310	40310	40310		40310	40310	40310		u8	1	0	0	0	R
40311	External ERS 1 accessory GQ2 speed	Indicates the speed of the GQ2 fan speed on the ERS accessory.					40311	40311	40311	40311		40311	40311	40311	%	u8	1	0	0	0	R
40312	External ERS 1 accessory GQ3 speed	Indicates the speed of the GQ3 fan speed on the ERS accessory.					40312	40312	40312	40312		40312	40312	40312	%	u8	1	0	0	0	R
40314	QN10 Need	0=Heating, 1=Hot water							40314	40314						u8	1	0	0	0	R
40316	Inverter limit status				40316		40316									u8	1	0	0	0	R
40317	Inverter drive status				40317	40317	40317		40317							u16	1	0	0	0	R
40321	Compressor Frequency, Request	The compressor frequency that has been requested by the system			40321	40321	40321		40321						Hz	u16	1	0	0	0	R
40322	Max Compressor Frequency, Heating	The maximum frequency of the compressor in heating mode			40322	40322	40322		40322						Hz	u16	100	0	0	0	R
40323	Inverter alarm code				40323	40323	40323		40323							u16	1	0	0	0	R
40324	Inverter fault code				40324	40324	40324		40324							u16	1	0	0	0	R
40326	Inverter drive command				40326	40326	40326		40326							u16	1	0	0	0	R
40327	NIBE Inverter Pic version				40327	40327	40327		40327							u16	1	0	0	0	R
40328	NIBE Inverter 8051 version				40328	40328	40328		40328							u16	1	0	0	0	R
40329	NIBE Inverter Def. Wizard				40329	40329	40329		40329							u16	1	0	0	0	R
40330	NIBE Inverter Mce version				40330	40330	40330		40330							u16	1	0	0	0	R
40331	NIBE Inverter Hw version				40331	40331	40331		40331							u16	1	0	0	0	R
40332	NIBE Inverter Hw type				40332	40332	40332		40332							u16	1	0	0	0	R
40339	External adjustment activated via input S8		40339	40339	40339	40339	40339	40339	40339	40339		40339	40339	40339		u8	1	0	0	0	R
40340	External adjustment activated via input S7		40340	40340	40340	40340	40340	40340	40340	40340		40340	40340	40340		u8	1	0	0	0	R
40341	External adjustment activated via input S6		40341	40341	40341	40341	40341	40341	40341	40341		40341	40341	40341		u8	1	0	0	0	R
40342	External adjustment activated via input S5		40342	40342	40342	40342	40342	40342	40342	40342		40342	40342	40342		u8	1	0	0	0	R
40364	AHPS Docking blocked	0 = unblocked, 1 = blocked			40364											u8	1	0	0	0	R
40365	Extra heating system pump S8		40365	40365	40365	40365	40365	40365	40365	40365		40365	40365	40365		u8	1	0	0	0	R
40366	Extra heating system pump S7		40366	40366	40366	40366	40366	40366	40366	40366		40366	40366	40366		u8	1	0	0	0	R
40367	Extra heating system pump S6		40367	40367	40367	40367	40367	40367	40367	40367		40367	40367	40367		u8	1	0	0	0	R
40368	Extra heating system pump S5		40368	40368	40368	40368	40368	40368	40368	40368		40368	40368	40368		u8	1	0	0	0	R
40369	Extra cooling HPAC, ACS						40369	40369	40369	40369						u8	1	0	0	0	R
40370	AHPS Docking accessory relays	0=Off, 1=On. b0:EM1-GP4, b1:Cool need, b2:QN32, b3:QN11 close, b4:EP30-GP4, b5:QN11 open ,b6:Ext add			40370											u8	1	0	0	0	R
40607	Heat Meter - HW Cpr and Add EP15	Accumulated energy production as calculated by the heat meter							40607	40607					kWh	u32	10	0	0	0	R
40609	Heat Meter - Heat Cpr and Add EP15	Accumulated energy production as calculated by the heat meter							40609	40609					kWh	u32	10	0	0	0	R
40611	Heat Meter - Cooling Cpr EP15	Accumulated energy production as calculated by the heat meter							40611	40611					kWh	u32	10	0	0	0	R
40613	Heat Meter - Pool Cpr EP15	Accumulated energy production as calculated by the heat meter							40613	40613					kWh	u32	10	0	0	0	R
40615	Heat Meter - HW Cpr EP15	Accumulated energy production as calculated by the heat meter							40615	40615					kWh	u32	10	0	0	0	R
40617	Heat Meter - Heat Cpr EP15	Accumulated energy production as calculated by the heat meter							40617	40617					kWh	u32	10	0	0	0	R
40625	BT82 HW Comfort Return Temp						40625	40625	40625	40625		40625	40625		°C	s16	10	0	0	0	R
40626	BT83 HW Comfort Cylinder Temp						40626	40626	40626	40626		40626	40626		°C	s16	10	0	0	0	R
40627	MP brine pump.	Motor protection brine pump								40627						s16	1	0	0	0	R
40647	EB108-EP15 Tot. Cooling op.time compr							40647	40647	40647					h	u32	1	0	0	0	R
40649	EB108-EP15 Tot. Pool1 op.time compr							40649	40649	40649					h	u32	1	0	0	0	R
40651	EB108-EP15 Tot. Pool2 op.time compr							40651	40651	40651					h	u32	1	0	0	0	R
40653	EB108-EP14 Tot. Cooling op.time compr							40653	40653	40653		40653			h	u32	1	0	9999999	0	R
40655	EB108-EP14 Tot. Pool1 op.time compr							40655	40655	40655		40655			h	u32	1	0	9999999	0	R
40657	EB108-EP14 Tot. Pool2 op.time compr							40657	40657	40657		40657			h	u32	1	0	9999999	0	R
40659	EB107-EP15 Tot. Cooling op.time compr							40659	40659	40659					h	u32	1	0	0	0	R
40661	EB107-EP15 Tot. Pool1 op.time compr							40661	40661	40661					h	u32	1	0	0	0	R
40663	EB107-EP15 Tot. Pool2 op.time compr							40663	40663	40663					h	u32	1	0	0	0	R
40665	EB107-EP14 Tot. Cooling op.time compr							40665	40665	40665		40665			h	u32	1	0	9999999	0	R
40667	EB107-EP14 Tot. Pool1 op.time compr							40667	40667	40667		40667			h	u32	1	0	9999999	0	R
40669	EB107-EP14 Tot. Pool2 op.time compr							40669	40669	40669		40669			h	u32	1	0	9999999	0	R
40671	EB106-EP15 Tot. Cooling op.time compr							40671	40671	40671					h	u32	1	0	0	0	R
40673	EB106-EP15 Tot. Pool1 op.time compr							40673	40673	40673					h	u32	1	0	0	0	R
40675	EB106-EP15 Tot. Pool2 op.time compr							40675	40675	40675					h	u32	1	0	0	0	R
40677	EB106-EP14 Tot. Cooling op.time compr							40677	40677	40677		40677			h	u32	1	0	9999999	0	R
40679	EB106-EP14 Tot. Pool1 op.time compr							40679	40679	40679		40679			h	u32	1	0	9999999	0	R
40681	EB106-EP14 Tot. Pool2 op.time compr							40681	40681	40681		40681			h	u32	1	0	9999999	0	R
40683	EB105-EP15 Tot. Cooling op.time compr							40683	40683	40683					h	u32	1	0	0	0	R
40685	EB105-EP15 Tot. Pool1 op.time compr							40685	40685	40685					h	u32	1	0	0	0	R
40687	EB105-EP15 Tot. Pool2 op.time compr							40687	40687	40687					h	u32	1	0	0	0	R
40689	EB105-EP14 Tot. Cooling op.time compr							40689	40689	40689		40689			h	u32	1	0	9999999	0	R
40691	EB105-EP14 Tot. Pool1 op.time compr							40691	40691	40691		40691			h	u32	1	0	9999999	0	R
40693	EB105-EP14 Tot. Pool2 op.time compr							40693	40693	40693		40693			h	u32	1	0	9999999	0	R
40695	EB104-EP15 Tot. Cooling op.time compr							40695	40695	40695					h	u32	1	0	0	0	R
40697	EB104-EP15 Tot. Pool1 op.time compr							40697	40697	40697					h	u32	1	0	0	0	R
40699	EB104-EP15 Tot. Pool2 op.time compr							40699	40699	40699					h	u32	1	0	0	0	R
40701	EB104-EP14 Tot. Cooling op.time compr							40701	40701	40701		40701			h	u32	1	0	9999999	0	R
40703	EB104-EP14 Tot. Pool1 op.time compr							40703	40703	40703		40703			h	u32	1	0	9999999	0	R
40705	EB104-EP14 Tot. Pool2 op.time compr							40705	40705	40705		40705			h	u32	1	0	9999999	0	R
40707	EB103-EP15 Tot. Cooling op.time compr							40707	40707	40707					h	u32	1	0	0	0	R
40709	EB103-EP15 Tot. Pool1 op.time compr							40709	40709	40709					h	u32	1	0	0	0	R
40711	EB103-EP15 Tot. Pool2 op.time compr							40711	40711	40711					h	u32	1	0	0	0	R
40713	EB103-EP14 Tot. Cooling op.time compr							40713	40713	40713		40713			h	u32	1	0	9999999	0	R
40715	EB103-EP14 Tot. Pool1 op.time compr							40715	40715	40715		40715			h	u32	1	0	9999999	0	R
40717	EB103-EP14 Tot. Pool2 op.time compr							40717	40717	40717		40717			h	u32	1	0	9999999	0	R
40719	EB102-EP15 Tot. Cooling op.time compr							40719	40719	40719					h	u32	1	0	0	0	R
40721	EB102-EP15 Tot. Pool1 op.time compr							40721	40721	40721					h	u32	1	0	0	0	R
40723	EB102-EP15 Tot. Pool2 op.time compr							40723	40723	40723					h	u32	1	0	0	0	R
40725	EB102-EP14 Tot. Cooling op.time compr							40725	40725	40725		40725			h	u32	1	0	9999999	0	R
40727	EB102-EP14 Tot. Pool1 op.time compr							40727	40727	40727		40727			h	u32	1	0	9999999	0	R
40729	EB102-EP14 Tot. Pool2 op.time compr							40729	40729	40729		40729			h	u32	1	0	9999999	0	R
40731	EB101-EP15 Tot. Cooling op.time compr							40731	40731	40731					h	u32	1	0	0	0	R
40733	EB101-EP15 Tot. Pool1 op.time compr							40733	40733	40733					h	u32	1	0	0	0	R
40735	EB101-EP15 Tot. Pool2 op.time compr							40735	40735	40735					h	u32	1	0	0	0	R
40737	EB101-EP14 Tot. Cooling op.time compr							40737	40737	40737	40737	40737	40737	40737	h	u32	1	0	9999999	0	R
40739	EB101-EP14 Tot. Pool1 op.time compr							40739	40739	40739	40739	40739	40739	40739	h	u32	1	0	9999999	0	R
40741	EB101-EP14 Tot. Pool2 op.time compr							40741	40741	40741	40741	40741	40741	40741	h	u32	1	0	9999999	0	R
40755	Tot. ext. HW add op.time	Total external hw-electric additive operation time	40755	40755	40755	40755	40755	40755	40755	40755	40755	40755	40755	40755	h	s32	10	0	9999999	0	R
40760	Hz unlimited				40760											u8	1	0	0	0	R
40762	Reg. state AHPS Docking shunt	10 = Off, 20 = Running			40762											u8	1	0	0	0	R
40763	AHPS Docking calc. supply temp.				40763											s16	10	0	0	0	R
40769	Heat Meter - Pool2 Cpr EP15	Accumulated energy production as calculated by the heat meter							40769	40769					kWh	u32	10	0	0	0	R
40771	Heat Meter - Pool2 Cpr EP14	Accumulated energy production as calculated by the heat meter			40771	40771	40771	40771	40771	40771			40771	40771	kWh	u32	10	0	0	0	R
40775	EB108 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40775	40775	40775	40775	Hz	u8	1	0	0	0	R
40776	EB107 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40776	40776	40776	40776	Hz	u8	1	0	0	0	R
40777	EB106 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40777	40777	40777	40777	Hz	u8	1	0	0	0	R
40778	EB105 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40778	40778	40778	40778	Hz	u8	1	0	0	0	R
40779	EB104 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40779	40779	40779	40779	Hz	u8	1	0	0	0	R
40780	EB103 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40780	40780	40780	40780	Hz	u8	1	0	0	0	R
40781	EB102 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40781	40781	40781	40781	Hz	u8	1	0	0	0	R
40782	EB101 Cpr Frequency Desired F2040	The desired frequency as shown in service info									40782	40782	40782	40782	Hz	u8	1	0	0	0	R
40792	OPT state	Indicates the state of the boiler connected through the OPT accessory.					40792	40792	40792	40792		40792	40792	40792		u8	1	0	0	0	R
40793	OPT version	Version of the OPT PCBA software					40793	40793	40793	40793		40793	40793	40793		u16	1	0	0	0	R
40801	OPT rel. modulation level	OPT relative modulation level					40801	40801	40801	40801		40801	40801	40801	%	s16	10	0	0	0	R
40802	OPT boiler temperature	OPT boiler temperature					40802	40802	40802	40802		40802	40802	40802	°C	s16	10	0	0	0	R
40806	OPT boiler op. time	OPT boiler operation time					40806	40806	40806	40806		40806	40806	40806	h	u16	1	0	0	0	R
40813	Compressor slow down reason	Bitmap telling the reason to why the compressor slows down. b0:inverter b1:brine b2:current b3:high cond b4:hot gas b5:evaporator				40813	40813									u8	1	0	0	0	R
40818	Available Heat Compressors	Number of compressors available for heating				40818		40818	40818	40818		40818				u8	1	0	0	0	R
40819	Available Hot Water Compressors	Number of compressors available for to hot water				40819		40819	40819	40819		40819				u8	1	0	0	0	R
40820	Available Pool 1 Compressors	Number of compressors available for pool 1						40820	40820	40820		40820				u8	1	0	0	0	R
40821	Available Pool 2 Compressors	Number of compressors available for pool 2						40821	40821	40821		40821				u8	1	0	0	0	R
40822	Available Cool Compressors	Number of compressors available for cooling						40822	40822	40822		40822				u8	1	0	0	0	R
40823	Available External Compressors	Number of compressors available for external control						40823	40823	40823						u8	1	0	0	0	R
40834	BM1 Humidity 						40834	40834	40834	40834		40834	40834	40834	%	s16	10	0	0	0	R
40856	BM1 BT50 Room temp.						40856	40856	40856	40856		40856	40856	40856	°C	s16	10	0	0	0	R
40857	BM1 Pressure 						40857	40857	40857	40857		40857	40857	40857	kPa	s16	10	0	0	0	R
40858	BM1 Dewpoint						40858	40858	40858	40858		40858	40858	40858	°C	s16	10	0	0	0	R
40868	+Adjust AUX Port		40868	40868	40868										1	u8	1	0	0	0	R
40870	+Adjust OP mode	Tells if plusadjust system calls for heat or cool	40870	40870	40870											u8	1	0	0	0	R
40871	+Adjust Comfort mode	Which comfort mode	40871	40871	40871											u8	1	0	0	0	R
40872	+Adjust Parallell adjustment	requested adjustment	40872	40872	40872											s8	1	0	0	0	R
40873	+Adjust Humidity	Humidity	40873	40873	40873										%RH	s16	10	0	0	0	R
40874	+Adjust Temp indoor	Average of all room sensors	40874	40874	40874										°C	s16	10	0	0	0	R
40875	+Adjust Temp outdoor	Outdoor temp	40875	40875	40875										°C	s16	10	0	0	0	R
40876	+Adjust Version	PCA input version	40876	40876	40876											u16	1	0	0	0	R
40877	+Adjust Activated	If plusadjust accessory is activated	40877	40877	40877											u8	1	0	0	0	R
40878	+Adjust Need	If plusadjust system calls for heat	40878	40878	40878											u8	1	0	0	0	R
40879	+Adjust Parallell factor		40879	40879											1	s8	1	1	10	5	R/W
40880	+Adjust Max change	Largest allowed change	40880	40880												s8	1	0	0	0	R/W
40881	+Adjust Affect system8	System affected by paralell change	40881	40881												u8	1	0	1	0	R/W
40882	+Adjust Affect system7	System affected by paralell change	40882	40882												u8	1	0	1	0	R/W
40883	+Adjust Affect system6	System affected by paralell change	40883	40883												u8	1	0	1	0	R/W
40884	+Adjust Affect system5	System affected by paralell change	40884	40884												u8	1	0	1	0	R/W
40885	+Adjust Affect system4	System affected by paralell change	40885	40885												u8	1	0	1	0	R/W
40886	+Adjust Affect system3	System affected by paralell change	40886	40886												u8	1	0	1	0	R/W
40887	+Adjust Affect system2	System affected by paralell change	40887	40887												u8	1	0	1	0	R/W
40888	+Adjust Affect system1	System affected by paralell change	40888	40888												u8	1	0	1	0	R/W
40889	BT64 Average	BT64 Cooling supply average	40889	40889	40889	40889	40889	40889	40889	40889	40889	40889	40889	40889	°C	s16	10	0	0	0	R
40912	EQ1 State ACS Thermostat	10=off,40=active wait,50=active					40912	40912	40912	40912						u8	1	0	0	0	R
40913	EQ1 State ACS Thermostat Heat Dump	10=shunt off,20=shunt open,30=shunt closed					40913	40913	40913	40913						u8	1	0	0	0	R
40918	EB100-FD3 Temperature limiter				40918	40918										s16	1	0	0	0	R
40919	State Outdoor Air Mixing	The state of the Outdoor Air Mixing function				40919										u8	1	0	0	0	R
40928	AZ10 Number of Starts											40928	40928	40928		u32	1	0	9999999	0	R
40930	AZ10 Total Operating Time											40930	40930	40930	h	u32	1	0	9999999	0	R
40932	Kind of defrost	Kind of defrost: 0 = No defrost, 1 = Passive defrost, 2 = Active defrost			40932	40932										u8	1	0	0	0	R
40934	Active defrosting time	Calculated time for active defrosting of the compressor.			40934	40934									s	s16	1	0	0	0	R
40935	Passive defrosting time	Calculated time for passive defrosting of the compressor.			40935	40935									s	s16	1	0	0	0	R
40940	Degree Minutes (32 bit)	Degree minutes, 32bit value. Full resolution.			40940	40940	40940	40940	40940	40940	40940	40940	40940	40940		s32	10	-30000	30000	0	R/W
40942	External ERS 1 accessory block status	Indicates if the ERS accessory is externaly blocked.					40942	40942	40942	40942		40942	40942	40942		u8	1	0	0	0	R
40943	External ERS 1 accessory EB17	Indicates if the status of ERS accessory EB17. I = closed, 0 = open.					40943	40943	40943	40943		40943	40943	40943		u8	1	0	0	0	R
40947	F135 AZ10-BT12 Cond. out											40947	40947	40947	°C	s16	10	0	0	0	R
40948	F135 AZ10-BT13 Cond. in											40948	40948	40948	°C	s16	10	0	0	0	R
40949	F135 AZ10-BT16 Evaporator temp											40949	40949	40949	°C	s16	10	0	0	0	R
40950	F135 AZ10-BT76 Defrosting temp											40950	40950	40950	°C	s16	10	0	0	0	R
40951	F135 AZ10-BT77 Air in temp											40951	40951	40951	°C	s16	10	0	0	0	R
40952	F135 AZ10 Active Alarm Number											40952	40952	40952		u16	1	0	0	0	R
40954	F135 AZ10 Defrosting	1 = Yes, 0 = No										40954	40954	40954		u8	1	0	0	0	R
40955	F135 AZ10 Relay Status											40955	40955	40955		u8	1	0	0	0	R
40961	F135 AZ10 Pump Speed											40961	40961	40961	%	u8	1	0	0	0	R
40962	F135 AZ10 Fan Speed											40962	40962	40962	%	u8	1	0	0	0	R
40964	F135 AZ10 Version											40964	40964	40964		u16	1	0	0	0	R
40993	Inverter min speed				40993	40993	40993		40993							u16	1	0	0	0	R
40994	Inverter max speed				40994	40994	40994		40994							u16	1	0	0	0	R
40995	External Energy Meter 2 Accumulated Energy				40995	40995	40995	40995	40995	40995		40995	40995	40995	kWh	u32	100	0	2147483647	0	R
40997	External Energy Meter 1 Accumulated Energy				40997	40997	40997	40997	40997	40997		40997	40997	40997	kWh	u32	100	0	2147483647	0	R
41000	EB101 F2120 Alarm Number										41000	41000	41000	41000		u8	1	0	0	0	R
41002	EB101 F2120 Fan Speed	F2120 Current Fan Speed									41002	41002	41002	41002	rpm	u16	1	0	0	0	R
41003	EB101 F2120 Max Fan Speed	F2120 Current Max Fan Speed									41003	41003	41003	41003	rpm	u16	1	0	0	0	R
41004	EB101 F2120 Min Fan Speed	F2120 Current Min Fan Speed									41004	41004	41004	41004	rpm	u16	1	0	0	0	R
41005	EB101 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed									41005	41005	41005	41005	Hz	u16	10	0	0	0	R
41006	EB101 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed									41006	41006	41006	41006	Hz	u16	10	0	0	0	R
41007	EB101 F2120 Calculated Power	F2120 Current Calculated Power									41007	41007	41007	41007	kW	u16	10	0	0	0	R
41008	EB101 F2120 Time To Defrost										41008	41008	41008	41008	min	u16	1	0	0	0	R
41026	EB100-Adjusted BS1 Air flow				41026	41026										s16	10	0	0	0	R
41027	Humidity average	Humidity average	41027	41027	41027	41027	41027	41027	41027	41027	41027	41027	41027	41027	%	s16	10	0	0	0	R
41050	EB108-EP14-BP8 LP Dew Pressure Sensor											41050			°C	s16	10	0	0	0	R
41051	EB108-EP14-BP9 HP Dew Pressure Sensor											41051			°C	s16	10	0	0	0	R
41052	EB108-EP14-BT81 Evi Temp											41052			°C	s16	10	0	0	0	R
41053	EB108-EP14-BP11 Evi Pressure											41053			bar	s16	10	0	0	0	R
41054	EB108-EP14-BP11 Evi Dew Pressure											41054			°C	s16	10	0	0	0	R
41055	EB108-EP14-BT84 Evaptor temp											41055			°C	s16	10	0	0	0	R
41056	EB108-EP14 Fan Status											41056				u8	1	0	0	0	R
41057	EB108-EP14 Fan Set											41057			rpm	u16	1	0	0	0	R
41066	EB107-EP14-BP8 LP Dew Pressure Sensor											41066			°C	s16	10	0	0	0	R
41067	EB107-EP14-BP9 HP Dew Pressure Sensor											41067			°C	s16	10	0	0	0	R
41068	EB107-EP14-BT81 Evi Temp											41068			°C	s16	10	0	0	0	R
41069	EB107-EP14-BP11 Evi Pressure											41069			bar	s16	10	0	0	0	R
41070	EB107-EP14-BP11 Evi Dew Pressure											41070			°C	s16	10	0	0	0	R
41071	EB107-EP14-BT84 Evaptor temp											41071			°C	s16	10	0	0	0	R
41072	EB107-EP14 Fan Status											41072				u8	1	0	0	0	R
41073	EB107-EP14 Fan Set											41073			rpm	u16	1	0	0	0	R
41082	EB106-EP14-BP8 LP Dew Pressure Sensor											41082			°C	s16	10	0	0	0	R
41083	EB106-EP14-BP9 HP Dew Pressure Sensor											41083			°C	s16	10	0	0	0	R
41084	EB106-EP14-BT81 Evi Temp											41084			°C	s16	10	0	0	0	R
41085	EB106-EP14-BP11 Evi Pressure											41085			bar	s16	10	0	0	0	R
41086	EB106-EP14-BP11 Evi Dew Pressure											41086			°C	s16	10	0	0	0	R
41087	EB106-EP14-BT84 Evaptor temp											41087			°C	s16	10	0	0	0	R
41088	EB106-EP14 Fan Status											41088				u8	1	0	0	0	R
41089	EB106-EP14 Fan Set											41089			rpm	u16	1	0	0	0	R
41098	EB105-EP14-BP8 LP Dew Pressure Sensor											41098			°C	s16	10	0	0	0	R
41099	EB105-EP14-BP9 HP Dew Pressure Sensor											41099			°C	s16	10	0	0	0	R
41100	EB105-EP14-BT81 Evi Temp											41100			°C	s16	10	0	0	0	R
41101	EB105-EP14-BP11 Evi Pressure											41101			bar	s16	10	0	0	0	R
41102	EB105-EP14-BP11 Evi Dew Pressure											41102			°C	s16	10	0	0	0	R
41103	EB105-EP14-BT84 Evaptor temp											41103			°C	s16	10	0	0	0	R
41104	EB105-EP14 Fan Status											41104				u8	1	0	0	0	R
41105	EB105-EP14 Fan Set											41105			rpm	u16	1	0	0	0	R
41114	EB104-EP14-BP8 LP Dew Pressure Sensor											41114			°C	s16	10	0	0	0	R
41115	EB104-EP14-BP9 HP Dew Pressure Sensor											41115			°C	s16	10	0	0	0	R
41116	EB104-EP14-BT81 Evi Temp											41116			°C	s16	10	0	0	0	R
41117	EB104-EP14-BP11 Evi Pressure											41117			bar	s16	10	0	0	0	R
41118	EB104-EP14-BP11 Evi Dew Pressure											41118			°C	s16	10	0	0	0	R
41119	EB104-EP14-BT84 Evaptor temp											41119			°C	s16	10	0	0	0	R
41120	EB104-EP14 Fan Status											41120				u8	1	0	0	0	R
41121	EB104-EP14 Fan Set											41121			rpm	u16	1	0	0	0	R
41130	EB103-EP14-BP8 LP Dew Pressure Sensor											41130			°C	s16	10	0	0	0	R
41131	EB103-EP14-BP9 HP Dew Pressure Sensor											41131			°C	s16	10	0	0	0	R
41132	EB103-EP14-BT81 Evi Temp											41132			°C	s16	10	0	0	0	R
41133	EB103-EP14-BP11 Evi Pressure											41133			bar	s16	10	0	0	0	R
41134	EB103-EP14-BP11 Evi Dew Pressure											41134			°C	s16	10	0	0	0	R
41135	EB103-EP14-BT84 Evaptor temp											41135			°C	s16	10	0	0	0	R
41136	EB103-EP14 Fan Status											41136				u8	1	0	0	0	R
41137	EB103-EP14 Fan Set											41137			rpm	u16	1	0	0	0	R
41146	EB102-EP14-BP8 LP Dew Pressure Sensor											41146			°C	s16	10	0	0	0	R
41147	EB102-EP14-BP9 HP Dew Pressure Sensor											41147			°C	s16	10	0	0	0	R
41148	EB102-EP14-BT81 Evi Temp											41148			°C	s16	10	0	0	0	R
41149	EB102-EP14-BP11 Evi Pressure											41149			bar	s16	10	0	0	0	R
41150	EB102-EP14-BP11 Evi Dew Pressure											41150			°C	s16	10	0	0	0	R
41151	EB102-EP14-BT84 Evaptor temp											41151			°C	s16	10	0	0	0	R
41152	EB102-EP14 Fan Status											41152				u8	1	0	0	0	R
41153	EB102-EP14 Fan Set											41153			rpm	u16	1	0	0	0	R
41162	EB101-EP14-BP8 LP Dew Pressure Sensor										41162	41162	41162	41162	°C	s16	10	0	0	0	R
41163	EB101-EP14-BP9 HP Dew Pressure Sensor										41163	41163	41163	41163	°C	s16	10	0	0	0	R
41164	EB101-EP14-BT81 Evi Temp										41164	41164	41164	41164	°C	s16	10	0	0	0	R
41165	EB101-EP14-BP11 Evi Pressure										41165	41165	41165	41165	bar	s16	10	0	0	0	R
41166	EB101-EP14-BP11 Evi Dew Pressure										41166	41166	41166	41166	°C	s16	10	0	0	0	R
41167	EB101-EP14-BT84 Evaptor temp										41167	41167	41167	41167	°C	s16	10	0	0	0	R
41168	EB101-EP14 Fan Status										41168	41168	41168	41168		u8	1	0	0	0	R
41169	EB101-EP14 Fan Set										41169	41169	41169	41169	rpm	u16	1	0	0	0	R
41186	Set point OPT boiler	Set point OPT boiler					41186	41186	41186	41186		41186	41186	41186	°C	s16	10	0	0	0	R
41187	AZ10 High Condenser Out Alarm											41187	41187	41187		u8	1	0	0	0	R
41188	AZ10 High Condenser In Alarm											41188	41188	41188		u8	1	0	0	0	R
41189	AA20-BE5 EME10 Current		41189	41189	41189	41189	41189	41189							A	s16	10	0	0	0	R
41190	AA20-BE5 EME10 Average Current		41190	41190	41190	41190	41190	41190							A	s16	10	0	0	0	R
41191	PV Panel State		41191	41191	41191	41191	41191	41191	41191	41191	41191	41191	41191	41191		u8	1	0	0	0	R
41210	AZ4-BT50 Room temp	AZ4-BT50 Room temp					41210	41210	41210	41210					°C	s16	10	0	0	0	R
41211	AZ3-BT50 Room temp	AZ3-BT50 Room temp					41211	41211	41211	41211					°C	s16	10	0	0	0	R
41212	AZ2-BT50 Room temp	AZ2-BT50 Room temp					41212	41212	41212	41212					°C	s16	10	0	0	0	R
41213	AZ1-BT50 Room temp	AZ1-BT50 Room temp					41213	41213	41213	41213					°C	s16	10	0	0	0	R
41214	OEK accessory block status	Indicates if the OEK accessory is externally blocked.			41214	41214										u8	1	0	0	0	R
41215	OEK state	Indicates the internal state of the OEK accessory. Inactive states: 10, 40:. Active states: 20, 30, 50, 60, 70.				41215										u8	1	0	0	0	R
41216	OEK accessory relays	b0:QN38 outdoor air damper, b1-b7: 0 (not used)				41216										u8	1	0	0	0	R
41256	Fan speed current	The current fan speed after scheduling and blocks are considered	41256	41256	41256	41256	41256	41256	41256	41256					%	u8	1	0	0	0	R
41257	Fan speed current	The current fan speed after scheduling and blocks are considered	41257	41257	41257	41257	41257	41257	41257	41257					%	u8	1	0	0	0	R
41258	Fan speed current	The current fan speed after scheduling and blocks are considered	41258	41258	41258	41258	41258	41258	41258	41258					%	u8	1	0	0	0	R
41265	Smart Home Mode	Current smart home mode, 0=Default,1=Away from home,2=Vacation	41265	41265	41265	41265	41265	41265	41265	41265	41265	41265	41265	41265		u8	1	0	0	0	R
41266	Offset to smart home system	Offset to smart home system	41266	41266	41266	41266	41266	41266	41266	41266	41266	41266	41266	41266	°C	s8	10	0	0	0	R
41267	Smart Home ctrl syst 8	Smart Home is controlling the system	41267	41267	41267	41267	41267	41267	41267	41267	41267	41267	41267	41267		u8	1	0	0	0	R
41268	Smart Home ctrl syst 7	Smart Home is controlling the system	41268	41268	41268	41268	41268	41268	41268	41268	41268	41268	41268	41268		u8	1	0	0	0	R
41269	Smart Home ctrl syst 6	Smart Home is controlling the system	41269	41269	41269	41269	41269	41269	41269	41269	41269	41269	41269	41269		u8	1	0	0	0	R
41270	Smart Home ctrl syst 5	Smart Home is controlling the system	41270	41270	41270	41270	41270	41270	41270	41270	41270	41270	41270	41270		u8	1	0	0	0	R
41271	Smart Home ctrl syst 4	Smart Home is controlling the system	41271	41271	41271	41271	41271	41271	41271	41271	41271	41271	41271	41271		u8	1	0	0	0	R
41272	Smart Home ctrl syst 3	Smart Home is controlling the system	41272	41272	41272	41272	41272	41272	41272	41272	41272	41272	41272	41272		u8	1	0	0	0	R
41273	Smart Home ctrl syst 2	Smart Home is controlling the system	41273	41273	41273	41273	41273	41273	41273	41273	41273	41273	41273	41273		u8	1	0	0	0	R
41274	Smart Home ctrl syst 1	Smart Home is controlling the system	41274	41274	41274	41274	41274	41274	41274	41274	41274	41274	41274	41274		u8	1	0	0	0	R
41287	OPT boiler has priority hot water	OPT boiler has priority hot water					41287	41287	41287	41287		41287	41287	41287		u8	1	0	0	0	R
41393	Smart energy source, energy source prio 7, start DM	Energy source prio 7, start DM					41393	41393	41393	41393		41393	41393	41393		s32	1	0	0	0	R
41395	Smart energy source, energy source prio 6, start DM	Energy source prio 6, start DM					41395	41395	41395	41395		41395	41395	41395		s32	1	0	0	0	R
41397	Smart energy source, energy source prio 5, start DM	Energy source prio 5, start DM					41397	41397	41397	41397		41397	41397	41397		s32	1	0	0	0	R
41399	Smart energy source, energy source prio 4, start DM	Energy source prio 4, start DM					41399	41399	41399	41399		41399	41399	41399		s32	1	0	0	0	R
41401	Smart energy source, energy source prio 3, start DM	Energy source prio 3, start DM					41401	41401	41401	41401		41401	41401	41401		s32	1	0	0	0	R
41403	Smart energy source, energy source prio 2, start DM	Energy source prio 2, start DM					41403	41403	41403	41403		41403	41403	41403		s32	1	0	0	0	R
41405	Smart energy source, energy source prio 1, start DM	Energy source prio 1, start DM					41405	41405	41405	41405		41405	41405	41405		s32	1	0	0	0	R
41421	Smart energy source, degree minute min value	Smart energy source, degree minute min value in Smart energy source system					41421	41421	41421	41421		41421	41421	41421		s32	1	0	0	0	R
41424	Smart energy source, actual OPT10 addition price	Smart energy source, actual OPT10 addition price.					41424	41424	41424	41424		41424	41424	41424		u16	1	0	0	0	R
41425	Smart energy source, actual shunt add price	Smart energy source, actual external step addition price.					41425	41425	41425	41425		41425	41425	41425		u16	1	0	0	0	R
41426	Smart energy source, actual ext. step add price	Smart energy source, actual external step add price.					41426	41426	41426	41426		41426	41426	41426		u16	1	0	0	0	R
41427	Smart energy source, actual electricity price	Smart energy source, actual electricity price.					41427	41427	41427	41427		41427	41427	41427		u16	1	0	0	0	R
41429	EP12-BT57 Collector In						41429	41429	41429	41429					°C	s16	10	0	0	0	R
41430	EP12-BT58 Collector Out						41430	41430	41430	41430					°C	s16	10	0	0	0	R
41446	Smart energy source prioritze OPT10 in hot water											41446	41446	41446		u8	1	0	0	0	R
41458	wood boiler, 1= active, 0 = not active										41458					u8	1	0	0	0	R
41468	EB108 F2120 Alarm Number											41468				u8	1	0	0	0	R
41469	EB108 F2120 Fan Speed	F2120 Current Fan Speed										41469			rpm	u16	1	0	0	0	R
41470	EB108 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41470			rpm	u16	1	0	0	0	R
41471	EB108 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41471			rpm	u16	1	0	0	0	R
41472	EB108 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41472			Hz	u16	10	0	0	0	R
41473	EB108 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41473			Hz	u16	10	0	0	0	R
41474	EB108 F2120 Calculated Power	F2120 Current Calculated Power										41474			kW	u16	10	0	0	0	R
41475	EB108 F2120 Time To Defrost											41475			min	u16	1	0	0	0	R
41493	EB107 F2120 Alarm Number											41493				u8	1	0	0	0	R
41494	EB107 F2120 Fan Speed	F2120 Current Fan Speed										41494			rpm	u16	1	0	0	0	R
41495	EB107 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41495			rpm	u16	1	0	0	0	R
41496	EB107 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41496			rpm	u16	1	0	0	0	R
41497	EB107 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41497			Hz	u16	10	0	0	0	R
41498	EB107 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41498			Hz	u16	10	0	0	0	R
41499	EB107 F2120 Calculated Power	F2120 Current Calculated Power										41499			kW	u16	10	0	0	0	R
41500	EB107 F2120 Time To Defrost											41500			min	u16	1	0	0	0	R
41518	EB106 F2120 Alarm Number											41518				u8	1	0	0	0	R
41519	EB106 F2120 Fan Speed	F2120 Current Fan Speed										41519			rpm	u16	1	0	0	0	R
41520	EB106 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41520			rpm	u16	1	0	0	0	R
41521	EB106 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41521			rpm	u16	1	0	0	0	R
41522	EB106 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41522			Hz	u16	10	0	0	0	R
41523	EB106 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41523			Hz	u16	10	0	0	0	R
41524	EB106 F2120 Calculated Power	F2120 Current Calculated Power										41524			kW	u16	10	0	0	0	R
41525	EB106 F2120 Time To Defrost											41525			min	u16	1	0	0	0	R
41543	EB105 F2120 Alarm Number											41543				u8	1	0	0	0	R
41544	EB105 F2120 Fan Speed	F2120 Current Fan Speed										41544			rpm	u16	1	0	0	0	R
41545	EB105 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41545			rpm	u16	1	0	0	0	R
41546	EB105 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41546			rpm	u16	1	0	0	0	R
41547	EB105 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41547			Hz	u16	10	0	0	0	R
41548	EB105 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41548			Hz	u16	10	0	0	0	R
41549	EB105 F2120 Calculated Power	F2120 Current Calculated Power										41549			kW	u16	10	0	0	0	R
41550	EB105 F2120 Time To Defrost											41550			min	u16	1	0	0	0	R
41568	EB104 F2120 Alarm Number											41568				u8	1	0	0	0	R
41569	EB104 F2120 Fan Speed	F2120 Current Fan Speed										41569			rpm	u16	1	0	0	0	R
41570	EB104 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41570			rpm	u16	1	0	0	0	R
41571	EB104 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41571			rpm	u16	1	0	0	0	R
41572	EB104 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41572			Hz	u16	10	0	0	0	R
41573	EB104 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41573			Hz	u16	10	0	0	0	R
41574	EB104 F2120 Calculated Power	F2120 Current Calculated Power										41574			kW	u16	10	0	0	0	R
41575	EB104 F2120 Time To Defrost											41575			min	u16	1	0	0	0	R
41593	EB103 F2120 Alarm Number											41593				u8	1	0	0	0	R
41594	EB103 F2120 Fan Speed	F2120 Current Fan Speed										41594			rpm	u16	1	0	0	0	R
41595	EB103 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41595			rpm	u16	1	0	0	0	R
41596	EB103 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41596			rpm	u16	1	0	0	0	R
41597	EB103 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41597			Hz	u16	10	0	0	0	R
41598	EB103 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41598			Hz	u16	10	0	0	0	R
41599	EB103 F2120 Calculated Power	F2120 Current Calculated Power										41599			kW	u16	10	0	0	0	R
41600	EB103 F2120 Time To Defrost											41600			min	u16	1	0	0	0	R
41618	EB102 F2120 Alarm Number											41618				u8	1	0	0	0	R
41619	EB102 F2120 Fan Speed	F2120 Current Fan Speed										41619			rpm	u16	1	0	0	0	R
41620	EB102 F2120 Max Fan Speed	F2120 Current Max Fan Speed										41620			rpm	u16	1	0	0	0	R
41621	EB102 F2120 Min Fan Speed	F2120 Current Min Fan Speed										41621			rpm	u16	1	0	0	0	R
41622	EB102 F2120 Max Compressor Speed	F2120 Current Max Compressor Speed										41622			Hz	u16	10	0	0	0	R
41623	EB102 F2120 Min Compressor Speed	F2120 Current Min Compressor Speed										41623			Hz	u16	10	0	0	0	R
41624	EB102 F2120 Calculated Power	F2120 Current Calculated Power										41624			kW	u16	10	0	0	0	R
41625	EB102 F2120 Time To Defrost											41625			min	u16	1	0	0	0	R
41705	Smart energy source prioritze in hot water	Smart energy source prioritze in hot water, 0 = Compressor, 1 = OPT10, 2 = Internal addition										41705	41705	41705		u8	1	0	0	0	R
41742	EB108-EP15 Alarm condensor in level	Alarm condensor in level						41742	41742	41742					°C	s16	10	0	0	0	R
41743	EB108-EP15 Alarm condensor out level	Alarm condensor out level						41743	41743	41743					°C	s16	10	0	0	0	R
41744	EB108-EP14 Alarm condensor in level	Alarm condensor in level						41744	41744	41744		41744			°C	s16	10	0	0	0	R
41745	EB108-EP14 Alarm condensor out level	Alarm condensor out level						41745	41745	41745		41745			°C	s16	10	0	0	0	R
41746	EB107-EP15 Alarm condensor in level	Alarm condensor in level						41746	41746	41746					°C	s16	10	0	0	0	R
41747	EB107-EP15 Alarm condensor out level	Alarm condensor out level						41747	41747	41747					°C	s16	10	0	0	0	R
41748	EB107-EP14 Alarm condensor in level	Alarm condensor in level						41748	41748	41748		41748			°C	s16	10	0	0	0	R
41749	EB107-EP14 Alarm condensor out level	Alarm condensor out level						41749	41749	41749		41749			°C	s16	10	0	0	0	R
41750	EB106-EP15 Alarm condensor in level	Alarm condensor in level						41750	41750	41750					°C	s16	10	0	0	0	R
41751	EB106-EP15 Alarm condensor out level	Alarm condensor out level						41751	41751	41751					°C	s16	10	0	0	0	R
41752	EB106-EP14 Alarm condensor in level	Alarm condensor in level						41752	41752	41752		41752			°C	s16	10	0	0	0	R
41753	EB106-EP14 Alarm condensor out level	Alarm condensor out level						41753	41753	41753		41753			°C	s16	10	0	0	0	R
41754	EB105-EP15 Alarm condensor in level	Alarm condensor in level						41754	41754	41754					°C	s16	10	0	0	0	R
41755	EB105-EP15 Alarm condensor out level	Alarm condensor out level						41755	41755	41755					°C	s16	10	0	0	0	R
41756	EB105-EP14 Alarm condensor in level	Alarm condensor in level						41756	41756	41756		41756			°C	s16	10	0	0	0	R
41757	EB105-EP14 Alarm condensor out level	Alarm condensor out level						41757	41757	41757		41757			°C	s16	10	0	0	0	R
41758	EB104-EP15 Alarm condensor in level	Alarm condensor in level						41758	41758	41758					°C	s16	10	0	0	0	R
41759	EB104-EP15 Alarm condensor out level	Alarm condensor out level						41759	41759	41759					°C	s16	10	0	0	0	R
41760	EB104-EP14 Alarm condensor in level	Alarm condensor in level						41760	41760	41760		41760			°C	s16	10	0	0	0	R
41761	EB104-EP14 Alarm condensor out level	Alarm condensor out level						41761	41761	41761		41761			°C	s16	10	0	0	0	R
41762	EB103-EP15 Alarm condensor in level	Alarm condensor in level						41762	41762	41762					°C	s16	10	0	0	0	R
41763	EB103-EP15 Alarm condensor out level	Alarm condensor out level						41763	41763	41763					°C	s16	10	0	0	0	R
41764	EB103-EP14 Alarm condensor in level	Alarm condensor in level						41764	41764	41764		41764			°C	s16	10	0	0	0	R
41765	EB103-EP14 Alarm condensor out level	Alarm condensor out level						41765	41765	41765		41765			°C	s16	10	0	0	0	R
41766	EB102-EP15 Alarm condensor in level	Alarm condensor in level						41766	41766	41766					°C	s16	10	0	0	0	R
41767	EB102-EP15 Alarm condensor out level	Alarm condensor out level						41767	41767	41767					°C	s16	10	0	0	0	R
41768	EB102-EP14 Alarm condensor in level	Alarm condensor in level						41768	41768	41768		41768			°C	s16	10	0	0	0	R
41769	EB102-EP14 Alarm condensor out level	Alarm condensor out level						41769	41769	41769		41769			°C	s16	10	0	0	0	R
41770	EB101-EP15 Alarm condensor in level	Alarm condensor in level						41770	41770	41770					°C	s16	10	0	0	0	R
41771	EB101-EP15 Alarm condensor out level	Alarm condensor out level						41771	41771	41771					°C	s16	10	0	0	0	R
41772	EB101-EP14 Alarm condensor in level	Alarm condensor in level						41772	41772	41772	41772	41772	41772	41772	°C	s16	10	0	0	0	R
41773	EB101-EP14 Alarm condensor out level	Alarm condensor out level						41773	41773	41773	41773	41773	41773	41773	°C	s16	10	0	0	0	R
41787	EB100-BL3 Condensation water level guard					41787										s16	1	0	0	0	R
41789	EB108 Compressor EP15 size								41789	41789					kW	u8	1	0	0	0	R
41793	EB107 Compressor EP15 size								41793	41793					kW	u8	1	0	0	0	R
41797	EB106 Compressor EP15 size								41797	41797					kW	u8	1	0	0	0	R
41801	EB105 Compressor EP15 size								41801	41801					kW	u8	1	0	0	0	R
41805	EB104 Compressor EP15 size								41805	41805					kW	u8	1	0	0	0	R
41809	EB103 Compressor EP15 size								41809	41809					kW	u8	1	0	0	0	R
41813	EB102 Compressor EP15 size								41813	41813					kW	u8	1	0	0	0	R
41817	EB101 Compressor EP15 size								41817	41817					kW	u8	1	0	0	0	R
41846	HP consumed energy due to ventilation					41846									kWh	u32	10	0	2147483647	0	R
41848	HP consumed energy due to hot water					41848									kWh	u32	10	0	2147483647	0	R
41850	HP consumed energy due to heating					41850									kWh	u32	10	0	2147483647	0	R
41862	EB108-EP15 set point for BT12	set point for BT12							41862						°C	s16	1	0	0	0	R
41863	EB108-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41863						Hz	u8	1	0	0	0	R
41864	EB108-EP14 set point for BT12	set point for BT12							41864						°C	s16	1	0	0	0	R
41865	EB108-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41865						Hz	u8	1	0	0	0	R
41866	EB107-EP15 set point for BT12	set point for BT12							41866						°C	s16	1	0	0	0	R
41867	EB107-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41867						Hz	u8	1	0	0	0	R
41868	EB107-EP14 set point for BT12	set point for BT12							41868						°C	s16	1	0	0	0	R
41869	EB107-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41869						Hz	u8	1	0	0	0	R
41870	EB106-EP15 set point for BT12	set point for BT12							41870						°C	s16	1	0	0	0	R
41871	EB106-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41871						Hz	u8	1	0	0	0	R
41872	EB106-EP14 set point for BT12	set point for BT12							41872						°C	s16	1	0	0	0	R
41873	EB106-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41873						Hz	u8	1	0	0	0	R
41874	EB105-EP15 set point for BT12	set point for BT12							41874						°C	s16	1	0	0	0	R
41875	EB105-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41875						Hz	u8	1	0	0	0	R
41876	EB105-EP14 set point for BT12	set point for BT12							41876						°C	s16	1	0	0	0	R
41877	EB105-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41877						Hz	u8	1	0	0	0	R
41878	EB104-EP15 set point for BT12	set point for BT12							41878						°C	s16	1	0	0	0	R
41879	EB104-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41879						Hz	u8	1	0	0	0	R
41880	EB104-EP14 set point for BT12	set point for BT12							41880						°C	s16	1	0	0	0	R
41881	EB104-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41881						Hz	u8	1	0	0	0	R
41882	EB103-EP15 set point for BT12	set point for BT12							41882						°C	s16	1	0	0	0	R
41883	EB103-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41883						Hz	u8	1	0	0	0	R
41884	EB103-EP14 set point for BT12	set point for BT12							41884						°C	s16	1	0	0	0	R
41885	EB103-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41885						Hz	u8	1	0	0	0	R
41886	EB102-EP15 set point for BT12	set point for BT12							41886						°C	s16	1	0	0	0	R
41887	EB102-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41887						Hz	u8	1	0	0	0	R
41888	EB102-EP14 set point for BT12	set point for BT12							41888						°C	s16	1	0	0	0	R
41889	EB102-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41889						Hz	u8	1	0	0	0	R
41890	EB101-EP15 set point for BT12	set point for BT12							41890						°C	s16	1	0	0	0	R
41891	EB101-EP15 start up frequency for inverter module	start up frequency in heating for inverter module							41891						Hz	u8	1	0	0	0	R
41892	EB101-EP14 set point for BT12	set point for BT12							41892						°C	s16	1	0	0	0	R
41893	EB101-EP14 start up frequency for inverter module	start up frequency in heating for inverter module							41893						Hz	u8	1	0	0	0	R
41928	Smart Price Adaption Price	The current electric price	41928	41928	41928	41928	41928	41928	41928	41928	41928	41928	41928	41928		u16	100	0	0	0	R
41929	Smart Price Adaption Price Level	Whether the current price is unknown (0), low (1), medium (2), high (3)	41929	41929	41929	41929	41929	41929	41929	41929	41929	41929	41929	41929		u8	1	0	0	0	R
41930	AA23-BE5 Power 10		41930	41930	41930	41930	41930	41930	41930	41930	41930	41930	41930	41930	W	u16	1	0	0	0	R
41931	AA23-BE5 Power 9		41931	41931	41931	41931	41931	41931	41931	41931	41931	41931	41931	41931	W	u16	1	0	0	0	R
41932	AA23-BE5 Power 8		41932	41932	41932	41932	41932	41932	41932	41932	41932	41932	41932	41932	W	u16	1	0	0	0	R
41933	AA23-BE5 Power 7		41933	41933	41933	41933	41933	41933	41933	41933	41933	41933	41933	41933	W	u16	1	0	0	0	R
41934	AA23-BE5 Power 6		41934	41934	41934	41934	41934	41934	41934	41934	41934	41934	41934	41934	W	u16	1	0	0	0	R
41935	AA23-BE5 Power 5		41935	41935	41935	41935	41935	41935	41935	41935	41935	41935	41935	41935	W	u16	1	0	0	0	R
41936	AA23-BE5 Power 4		41936	41936	41936	41936	41936	41936	41936	41936	41936	41936	41936	41936	W	u16	1	0	0	0	R
41937	AA23-BE5 Power 3		41937	41937	41937	41937	41937	41937	41937	41937	41937	41937	41937	41937	W	u16	1	0	0	0	R
41938	AA23-BE5 Power 2		41938	41938	41938	41938	41938	41938	41938	41938	41938	41938	41938	41938	W	u16	1	0	0	0	R
41939	AA23-BE5 Power 1		41939	41939	41939	41939	41939	41939	41939	41939	41939	41939	41939	41939	W	u16	1	0	0	0	R
41940	AA23-BE5 Error High 10		41940	41940	41940	41940	41940	41940	41940	41940	41940	41940	41940	41940	W	u16	1	0	0	0	R
41941	AA23-BE5 Error High 9		41941	41941	41941	41941	41941	41941	41941	41941	41941	41941	41941	41941	W	u16	1	0	0	0	R
41942	AA23-BE5 Error High 8		41942	41942	41942	41942	41942	41942	41942	41942	41942	41942	41942	41942	W	u16	1	0	0	0	R
41943	AA23-BE5 Error High 7		41943	41943	41943	41943	41943	41943	41943	41943	41943	41943	41943	41943	W	u16	1	0	0	0	R
41944	AA23-BE5 Error High 6		41944	41944	41944	41944	41944	41944	41944	41944	41944	41944	41944	41944	W	u16	1	0	0	0	R
41945	AA23-BE5 Error High 5		41945	41945	41945	41945	41945	41945	41945	41945	41945	41945	41945	41945	W	u16	1	0	0	0	R
41946	AA23-BE5 Error High 4		41946	41946	41946	41946	41946	41946	41946	41946	41946	41946	41946	41946	W	u16	1	0	0	0	R
41947	AA23-BE5 Error High 3		41947	41947	41947	41947	41947	41947	41947	41947	41947	41947	41947	41947	W	u16	1	0	0	0	R
41948	AA23-BE5 Error High 2		41948	41948	41948	41948	41948	41948	41948	41948	41948	41948	41948	41948	W	u16	1	0	0	0	R
41949	AA23-BE5 Error High 1		41949	41949	41949	41949	41949	41949	41949	41949	41949	41949	41949	41949	W	u16	1	0	0	0	R
41950	AA23-BE5 Error Low 10		41950	41950	41950	41950	41950	41950	41950	41950	41950	41950	41950	41950	W	u16	1	0	0	0	R
41951	AA23-BE5 Error Low 9		41951	41951	41951	41951	41951	41951	41951	41951	41951	41951	41951	41951	W	u16	1	0	0	0	R
41952	AA23-BE5 Error Low 8		41952	41952	41952	41952	41952	41952	41952	41952	41952	41952	41952	41952	W	u16	1	0	0	0	R
41953	AA23-BE5 Error Low 7		41953	41953	41953	41953	41953	41953	41953	41953	41953	41953	41953	41953	W	u16	1	0	0	0	R
41954	AA23-BE5 Error Low 6		41954	41954	41954	41954	41954	41954	41954	41954	41954	41954	41954	41954	W	u16	1	0	0	0	R
41955	AA23-BE5 Error Low 5		41955	41955	41955	41955	41955	41955	41955	41955	41955	41955	41955	41955	W	u16	1	0	0	0	R
41956	AA23-BE5 Error Low 4		41956	41956	41956	41956	41956	41956	41956	41956	41956	41956	41956	41956	W	u16	1	0	0	0	R
41957	AA23-BE5 Error Low 3		41957	41957	41957	41957	41957	41957	41957	41957	41957	41957	41957	41957	W	u16	1	0	0	0	R
41958	AA23-BE5 Error Low 2		41958	41958	41958	41958	41958	41958	41958	41958	41958	41958	41958	41958	W	u16	1	0	0	0	R
41959	AA23-BE5 Error Low 1		41959	41959	41959	41959	41959	41959	41959	41959	41959	41959	41959	41959	W	u16	1	0	0	0	R
41960	AA23-BE5 Com Percentage 10		41960	41960	41960	41960	41960	41960	41960	41960	41960	41960	41960	41960	%	u8	1	0	0	0	R
41961	AA23-BE5 Com Percentage 9		41961	41961	41961	41961	41961	41961	41961	41961	41961	41961	41961	41961	%	u8	1	0	0	0	R
41962	AA23-BE5 Com Percentage 8		41962	41962	41962	41962	41962	41962	41962	41962	41962	41962	41962	41962	%	u8	1	0	0	0	R
41963	AA23-BE5 Com Percentage 7		41963	41963	41963	41963	41963	41963	41963	41963	41963	41963	41963	41963	%	u8	1	0	0	0	R
41964	AA23-BE5 Com Percentage 6		41964	41964	41964	41964	41964	41964	41964	41964	41964	41964	41964	41964	%	u8	1	0	0	0	R
41965	AA23-BE5 Com Percentage 5		41965	41965	41965	41965	41965	41965	41965	41965	41965	41965	41965	41965	%	u8	1	0	0	0	R
41966	AA23-BE5 Com Percentage 4		41966	41966	41966	41966	41966	41966	41966	41966	41966	41966	41966	41966	%	u8	1	0	0	0	R
41967	AA23-BE5 Com Percentage 3		41967	41967	41967	41967	41967	41967	41967	41967	41967	41967	41967	41967	%	u8	1	0	0	0	R
41968	AA23-BE5 Com Percentage 2		41968	41968	41968	41968	41968	41968	41968	41968	41968	41968	41968	41968	%	u8	1	0	0	0	R
41969	AA23-BE5 Com Percentage 1		41969	41969	41969	41969	41969	41969	41969	41969	41969	41969	41969	41969	%	u8	1	0	0	0	R
41980	AA23-BE5 Voltage1 10		41980	41980	41980	41980	41980	41980	41980	41980	41980	41980	41980	41980	V	u16	10	0	0	0	R
41981	AA23-BE5 Voltage1 9		41981	41981	41981	41981	41981	41981	41981	41981	41981	41981	41981	41981	V	u16	10	0	0	0	R
41982	AA23-BE5 Voltage1 8		41982	41982	41982	41982	41982	41982	41982	41982	41982	41982	41982	41982	V	u16	10	0	0	0	R
41983	AA23-BE5 Voltage1 7		41983	41983	41983	41983	41983	41983	41983	41983	41983	41983	41983	41983	V	u16	10	0	0	0	R
41984	AA23-BE5 Voltage1 6		41984	41984	41984	41984	41984	41984	41984	41984	41984	41984	41984	41984	V	u16	10	0	0	0	R
41985	AA23-BE5 Voltage1 5		41985	41985	41985	41985	41985	41985	41985	41985	41985	41985	41985	41985	V	u16	10	0	0	0	R
41986	AA23-BE5 Voltage1 4		41986	41986	41986	41986	41986	41986	41986	41986	41986	41986	41986	41986	V	u16	10	0	0	0	R
41987	AA23-BE5 Voltage1 3		41987	41987	41987	41987	41987	41987	41987	41987	41987	41987	41987	41987	V	u16	10	0	0	0	R
41988	AA23-BE5 Voltage1 2		41988	41988	41988	41988	41988	41988	41988	41988	41988	41988	41988	41988	V	u16	10	0	0	0	R
41989	AA23-BE5 Voltage1 1		41989	41989	41989	41989	41989	41989	41989	41989	41989	41989	41989	41989	V	u16	10	0	0	0	R
41990	AA23-BE5 Voltage2 10		41990	41990	41990	41990	41990	41990	41990	41990	41990	41990	41990	41990	V	u16	10	0	0	0	R
41991	AA23-BE5 Voltage2 9		41991	41991	41991	41991	41991	41991	41991	41991	41991	41991	41991	41991	V	u16	10	0	0	0	R
41992	AA23-BE5 Voltage2 8		41992	41992	41992	41992	41992	41992	41992	41992	41992	41992	41992	41992	V	u16	10	0	0	0	R
41993	AA23-BE5 Voltage2 7		41993	41993	41993	41993	41993	41993	41993	41993	41993	41993	41993	41993	V	u16	10	0	0	0	R
41994	AA23-BE5 Voltage2 6		41994	41994	41994	41994	41994	41994	41994	41994	41994	41994	41994	41994	V	u16	10	0	0	0	R
41995	AA23-BE5 Voltage2 5		41995	41995	41995	41995	41995	41995	41995	41995	41995	41995	41995	41995	V	u16	10	0	0	0	R
41996	AA23-BE5 Voltage2 4		41996	41996	41996	41996	41996	41996	41996	41996	41996	41996	41996	41996	V	u16	10	0	0	0	R
41997	AA23-BE5 Voltage2 3		41997	41997	41997	41997	41997	41997	41997	41997	41997	41997	41997	41997	V	u16	10	0	0	0	R
41998	AA23-BE5 Voltage2 2		41998	41998	41998	41998	41998	41998	41998	41998	41998	41998	41998	41998	V	u16	10	0	0	0	R
41999	AA23-BE5 Voltage2 1		41999	41999	41999	41999	41999	41999	41999	41999	41999	41999	41999	41999	V	u16	10	0	0	0	R
42000	AA23-BE5 Temperature 10		42000	42000	42000	42000	42000	42000	42000	42000	42000	42000	42000	42000	°C	u16	10	0	0	0	R
42001	AA23-BE5 Temperature 9		42001	42001	42001	42001	42001	42001	42001	42001	42001	42001	42001	42001	°C	u16	10	0	0	0	R
42002	AA23-BE5 Temperature 8		42002	42002	42002	42002	42002	42002	42002	42002	42002	42002	42002	42002	°C	u16	10	0	0	0	R
42003	AA23-BE5 Temperature 7		42003	42003	42003	42003	42003	42003	42003	42003	42003	42003	42003	42003	°C	u16	10	0	0	0	R
42004	AA23-BE5 Temperature 6		42004	42004	42004	42004	42004	42004	42004	42004	42004	42004	42004	42004	°C	u16	10	0	0	0	R
42005	AA23-BE5 Temperature 5		42005	42005	42005	42005	42005	42005	42005	42005	42005	42005	42005	42005	°C	u16	10	0	0	0	R
42006	AA23-BE5 Temperature 4		42006	42006	42006	42006	42006	42006	42006	42006	42006	42006	42006	42006	°C	u16	10	0	0	0	R
42007	AA23-BE5 Temperature 3		42007	42007	42007	42007	42007	42007	42007	42007	42007	42007	42007	42007	°C	u16	10	0	0	0	R
42008	AA23-BE5 Temperature 2		42008	42008	42008	42008	42008	42008	42008	42008	42008	42008	42008	42008	°C	u16	10	0	0	0	R
42009	AA23-BE5 Temperature 1		42009	42009	42009	42009	42009	42009	42009	42009	42009	42009	42009	42009	°C	u16	10	0	0	0	R
42010	AA23-BE5 Energy 10		42010	42010	42010	42010	42010	42010	42010	42010	42010	42010	42010	42010	kWh	u32	10	0	0	0	R
42012	AA23-BE5 Energy 9		42012	42012	42012	42012	42012	42012	42012	42012	42012	42012	42012	42012	kWh	u32	10	0	0	0	R
42014	AA23-BE5 Energy 8		42014	42014	42014	42014	42014	42014	42014	42014	42014	42014	42014	42014	kWh	u32	10	0	0	0	R
42016	AA23-BE5 Energy 7		42016	42016	42016	42016	42016	42016	42016	42016	42016	42016	42016	42016	kWh	u32	10	0	0	0	R
42018	AA23-BE5 Energy 6		42018	42018	42018	42018	42018	42018	42018	42018	42018	42018	42018	42018	kWh	u32	10	0	0	0	R
42020	AA23-BE5 Energy 5		42020	42020	42020	42020	42020	42020	42020	42020	42020	42020	42020	42020	kWh	u32	10	0	0	0	R
42022	AA23-BE5 Energy 4		42022	42022	42022	42022	42022	42022	42022	42022	42022	42022	42022	42022	kWh	u32	10	0	0	0	R
42024	AA23-BE5 Energy 3		42024	42024	42024	42024	42024	42024	42024	42024	42024	42024	42024	42024	kWh	u32	10	0	0	0	R
42026	AA23-BE5 Energy 2		42026	42026	42026	42026	42026	42026	42026	42026	42026	42026	42026	42026	kWh	u32	10	0	0	0	R
42028	AA23-BE5 Energy 1		42028	42028	42028	42028	42028	42028	42028	42028	42028	42028	42028	42028	kWh	u32	10	0	0	0	R
42030	AA23-BE5 EME20 Version		42030	42030	42030	42030	42030	42030	42030	42030	42030	42030	42030	42030		u16	1	0	0	0	R
42033	PV Panel Heat Offset		42033	42033	42033	42033	42033	42033	42033	42033	42033	42033	42033	42033	°C	u8	10	0	0	0	R
42034	PV Panel Pool Offset		42034	42034	42034	42034	42034	42034	42034	42034		42034	42034	42034	°C	u8	10	0	0	0	R
42035	AA23-BE5 EME20 Total Power		42035	42035	42035	42035	42035	42035	42035	42035	42035	42035	42035	42035	W	u32	1	0	0	0	R
42037	AA23-BE5 EME20 Total Average Power		42037	42037	42037	42037	42037	42037	42037	42037	42037	42037	42037	42037	W	u32	1	0	0	0	R
42075	AA23-BE5 EME20 Total Energy		42075	42075	42075	42075	42075	42075	42075	42075	42075	42075	42075	42075	kWh	u32	10	0	0	0	R
42080	AA23-BE5 Alarm 504		42080	42080	42080	42080	42080	42080	42080	42080	42080	42080	42080	42080		u8	1	0	0	0	R
42081	AA23-BE5 Alarm 505		42081	42081	42081	42081	42081	42081	42081	42081	42081	42081	42081	42081		u8	1	0	0	0	R
42082	AA23-BE5 Alarm 506		42082	42082	42082	42082	42082	42082	42082	42082	42082	42082	42082	42082		u8	1	0	0	0	R
42083	AA23-BE5 Alarm 507		42083	42083	42083	42083	42083	42083	42083	42083	42083	42083	42083	42083		u8	1	0	0	0	R
42084	AA23-BE5 Alarm 508		42084	42084	42084	42084	42084	42084	42084	42084	42084	42084	42084	42084		u8	1	0	0	0	R
42085	AA23-BE5 Alarm 509		42085	42085	42085	42085	42085	42085	42085	42085	42085	42085	42085	42085		u8	1	0	0	0	R
42086	AA23-BE5 Alarm 510		42086	42086	42086	42086	42086	42086	42086	42086	42086	42086	42086	42086		u8	1	0	0	0	R
42087	AA23-BE5 Alarm 511		42087	42087	42087	42087	42087	42087	42087	42087	42087	42087	42087	42087		u8	1	0	0	0	R
42093	External SAM accessory GQ3 speed	Indicates the speed of the GQ3 fan speed in the SAM accessory.			42093										%	u8	1	0	0	0	R
42097	Ground water pump auto speed	Ground water pump auto speed					42097	42097	42097	42097						s8	1	0	0	0	R/W
42100	BT1 Average, 24h	EB100-BT1 Outdoor temperature average, 24h	42100	42100	42100	42100	42100	42100	42100	42100	42100	42100	42100	42100	°C	s16	10	0	0	0	R
42101	Used heating power average, 24h	Used heating power average, 24h	42101	42101	42101	42101	42101	42101	42101	42101	42101	42101	42101	42101	°C	s16	10	0	0	0	R
42136	BT22 Supply air temp.									42136		42136	42136	42136	°C	s16	10	0	0	0	R
42137	BT22 Supply air temp.									42137		42137	42137	42137	°C	s16	10	0	0	0	R
42138	BT22 Supply air temp.									42138		42138	42138	42138	°C	s16	10	0	0	0	R
42139	AZ30-BT23 Outdoor temp. ERS 4						42139	42139	42139	42139		42139	42139	42139	°C	s16	10	0	0	0	R
42140	AZ30-BT23 Outdoor temp. ERS 3						42140	42140	42140	42140		42140	42140	42140	°C	s16	10	0	0	0	R
42141	AZ30-BT23 Outdoor temp. ERS 2						42141	42141	42141	42141		42141	42141	42141	°C	s16	10	0	0	0	R
42150	External ERS 4 accessory relays	Indicates the status of the relays on the ERS accessory. The information is binary encoded. b0: K1, b1: K2, b2: K3, b3: K4					42150	42150	42150	42150		42150	42150	42150		u8	1	0	0	0	R
42151	External ERS 3 accessory relays	Indicates the status of the relays on the ERS accessory. The information is binary encoded. b0: K1, b1: K2, b2: K3, b3: K4					42151	42151	42151	42151		42151	42151	42151		u8	1	0	0	0	R
42152	External ERS 2 accessory relays	Indicates the status of the relays on the ERS accessory. The information is binary encoded. b0: K1, b1: K2, b2: K3, b3: K4					42152	42152	42152	42152		42152	42152	42152		u8	1	0	0	0	R
42153	External ERS 4 accessory GQ2 speed	Indicates the speed of the GQ2 fan speed on the ERS accessory.					42153	42153	42153	42153		42153	42153	42153	%	u8	1	0	0	0	R
42154	External ERS 3 accessory GQ2 speed	Indicates the speed of the GQ2 fan speed on the ERS accessory.					42154	42154	42154	42154		42154	42154	42154	%	u8	1	0	0	0	R
42155	External ERS 2 accessory GQ2 speed	Indicates the speed of the GQ2 fan speed on the ERS accessory.					42155	42155	42155	42155		42155	42155	42155	%	u8	1	0	0	0	R
42156	External ERS 4 accessory GQ3 speed	Indicates the speed of the GQ3 fan speed on the ERS accessory.					42156	42156	42156	42156		42156	42156	42156	%	u8	1	0	0	0	R
42157	External ERS 3 accessory GQ3 speed	Indicates the speed of the GQ3 fan speed on the ERS accessory.					42157	42157	42157	42157		42157	42157	42157	%	u8	1	0	0	0	R
42158	External ERS 2 accessory GQ3 speed	Indicates the speed of the GQ3 fan speed on the ERS accessory.					42158	42158	42158	42158		42158	42158	42158	%	u8	1	0	0	0	R
42159	External ERS 4 accessory block status	Indicates if the ERS accessory is externaly blocked.					42159	42159	42159	42159		42159	42159	42159		u8	1	0	0	0	R
42160	External ERS 3 accessory block status	Indicates if the ERS accessory is externaly blocked.					42160	42160	42160	42160		42160	42160	42160		u8	1	0	0	0	R
42161	External ERS 2 accessory block status	Indicates if the ERS accessory is externaly blocked.					42161	42161	42161	42161		42161	42161	42161		u8	1	0	0	0	R
42162	External ERS 4 accessory EB17	Indicates if the status of ERS accessory EB17. I = closed, 0 = open.					42162	42162	42162	42162		42162	42162	42162		u8	1	0	0	0	R
42163	External ERS 3 accessory EB17	Indicates if the status of ERS accessory EB17. I = closed, 0 = open.					42163	42163	42163	42163		42163	42163	42163		u8	1	0	0	0	R
42164	External ERS 2 accessory EB17	Indicates if the status of ERS accessory EB17. I = closed, 0 = open.					42164	42164	42164	42164		42164	42164	42164		u8	1	0	0	0	R
42166	EB108-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42166	42166					kWh	u32	10	0	0	0	R
42168	EB108-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42168	42168	42168					kWh	u32	10	0	0	0	R
42170	EB108-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42170	42170	42170					kWh	u32	10	0	0	0	R
42172	EB108-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42172	42172	42172					kWh	u32	10	0	0	0	R
42174	EB108-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42174	42174	42174					kWh	u32	10	0	0	0	R
42176	EB108-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42176	42176	42176					kWh	u32	10	0	0	0	R
42178	EB108-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42178	42178	42178					kWh	u32	10	0	0	0	R
42181	EB108-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42181	42181					kWh	u32	10	0	0	0	R
42183	EB108-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42183	42183	42183					kWh	u32	10	0	0	0	R
42185	EB108-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42185	42185	42185					kWh	u32	10	0	0	0	R
42187	EB108-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42187	42187	42187					kWh	u32	10	0	0	0	R
42189	EB108-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42189	42189	42189					kWh	u32	10	0	0	0	R
42191	EB108-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42191	42191	42191					kWh	u32	10	0	0	0	R
42193	EB108-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42193	42193	42193					kWh	u32	10	0	0	0	R
42196	EB107-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42196	42196					kWh	u32	10	0	0	0	R
42198	EB107-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42198	42198	42198					kWh	u32	10	0	0	0	R
42200	EB107-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42200	42200	42200					kWh	u32	10	0	0	0	R
42202	EB107-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42202	42202	42202					kWh	u32	10	0	0	0	R
42204	EB107-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42204	42204	42204					kWh	u32	10	0	0	0	R
42206	EB107-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42206	42206	42206					kWh	u32	10	0	0	0	R
42208	EB107-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42208	42208	42208					kWh	u32	10	0	0	0	R
42211	EB107-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42211	42211					kWh	u32	10	0	0	0	R
42213	EB107-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42213	42213	42213					kWh	u32	10	0	0	0	R
42215	EB107-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42215	42215	42215					kWh	u32	10	0	0	0	R
42217	EB107-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42217	42217	42217					kWh	u32	10	0	0	0	R
42219	EB107-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42219	42219	42219					kWh	u32	10	0	0	0	R
42221	EB107-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42221	42221	42221					kWh	u32	10	0	0	0	R
42223	EB107-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42223	42223	42223					kWh	u32	10	0	0	0	R
42226	EB106-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42226	42226					kWh	u32	10	0	0	0	R
42228	EB106-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42228	42228	42228					kWh	u32	10	0	0	0	R
42230	EB106-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42230	42230	42230					kWh	u32	10	0	0	0	R
42232	EB106-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42232	42232	42232					kWh	u32	10	0	0	0	R
42234	EB106-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42234	42234	42234					kWh	u32	10	0	0	0	R
42236	EB106-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42236	42236	42236					kWh	u32	10	0	0	0	R
42238	EB106-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42238	42238	42238					kWh	u32	10	0	0	0	R
42241	EB106-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42241	42241					kWh	u32	10	0	0	0	R
42243	EB106-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42243	42243	42243					kWh	u32	10	0	0	0	R
42245	EB106-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42245	42245	42245					kWh	u32	10	0	0	0	R
42247	EB106-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42247	42247	42247					kWh	u32	10	0	0	0	R
42249	EB106-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42249	42249	42249					kWh	u32	10	0	0	0	R
42251	EB106-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42251	42251	42251					kWh	u32	10	0	0	0	R
42253	EB106-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42253	42253	42253					kWh	u32	10	0	0	0	R
42256	EB105-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42256	42256					kWh	u32	10	0	0	0	R
42258	EB105-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42258	42258	42258					kWh	u32	10	0	0	0	R
42260	EB105-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42260	42260	42260					kWh	u32	10	0	0	0	R
42262	EB105-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42262	42262	42262					kWh	u32	10	0	0	0	R
42264	EB105-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42264	42264	42264					kWh	u32	10	0	0	0	R
42266	EB105-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42266	42266	42266					kWh	u32	10	0	0	0	R
42268	EB105-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42268	42268	42268					kWh	u32	10	0	0	0	R
42271	EB105-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42271	42271					kWh	u32	10	0	0	0	R
42273	EB105-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42273	42273	42273					kWh	u32	10	0	0	0	R
42275	EB105-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42275	42275	42275					kWh	u32	10	0	0	0	R
42277	EB105-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42277	42277	42277					kWh	u32	10	0	0	0	R
42279	EB105-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42279	42279	42279					kWh	u32	10	0	0	0	R
42281	EB105-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42281	42281	42281					kWh	u32	10	0	0	0	R
42283	EB105-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42283	42283	42283					kWh	u32	10	0	0	0	R
42286	EB104-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42286	42286					kWh	u32	10	0	0	0	R
42288	EB104-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42288	42288	42288					kWh	u32	10	0	0	0	R
42290	EB104-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42290	42290	42290					kWh	u32	10	0	0	0	R
42292	EB104-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42292	42292	42292					kWh	u32	10	0	0	0	R
42294	EB104-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42294	42294	42294					kWh	u32	10	0	0	0	R
42296	EB104-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42296	42296	42296					kWh	u32	10	0	0	0	R
42298	EB104-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42298	42298	42298					kWh	u32	10	0	0	0	R
42301	EB104-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42301	42301					kWh	u32	10	0	0	0	R
42303	EB104-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42303	42303	42303					kWh	u32	10	0	0	0	R
42305	EB104-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42305	42305	42305					kWh	u32	10	0	0	0	R
42307	EB104-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42307	42307	42307					kWh	u32	10	0	0	0	R
42309	EB104-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42309	42309	42309					kWh	u32	10	0	0	0	R
42311	EB104-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42311	42311	42311					kWh	u32	10	0	0	0	R
42313	EB104-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42313	42313	42313					kWh	u32	10	0	0	0	R
42316	EB103-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42316	42316					kWh	u32	10	0	0	0	R
42318	EB103-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42318	42318	42318					kWh	u32	10	0	0	0	R
42320	EB103-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42320	42320	42320					kWh	u32	10	0	0	0	R
42322	EB103-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42322	42322	42322					kWh	u32	10	0	0	0	R
42324	EB103-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42324	42324	42324					kWh	u32	10	0	0	0	R
42326	EB103-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42326	42326	42326					kWh	u32	10	0	0	0	R
42328	EB103-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42328	42328	42328					kWh	u32	10	0	0	0	R
42331	EB103-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42331	42331					kWh	u32	10	0	0	0	R
42333	EB103-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42333	42333	42333					kWh	u32	10	0	0	0	R
42335	EB103-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42335	42335	42335					kWh	u32	10	0	0	0	R
42337	EB103-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42337	42337	42337					kWh	u32	10	0	0	0	R
42339	EB103-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42339	42339	42339					kWh	u32	10	0	0	0	R
42341	EB103-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42341	42341	42341					kWh	u32	10	0	0	0	R
42343	EB103-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42343	42343	42343					kWh	u32	10	0	0	0	R
42346	EB102-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42346	42346					kWh	u32	10	0	0	0	R
42348	EB102-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42348	42348	42348					kWh	u32	10	0	0	0	R
42350	EB102-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42350	42350	42350					kWh	u32	10	0	0	0	R
42352	EB102-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42352	42352	42352					kWh	u32	10	0	0	0	R
42354	EB102-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42354	42354	42354					kWh	u32	10	0	0	0	R
42356	EB102-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42356	42356	42356					kWh	u32	10	0	0	0	R
42358	EB102-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42358	42358	42358					kWh	u32	10	0	0	0	R
42361	EB102-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42361	42361					kWh	u32	10	0	0	0	R
42363	EB102-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42363	42363	42363					kWh	u32	10	0	0	0	R
42365	EB102-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42365	42365	42365					kWh	u32	10	0	0	0	R
42367	EB102-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42367	42367	42367					kWh	u32	10	0	0	0	R
42369	EB102-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42369	42369	42369					kWh	u32	10	0	0	0	R
42371	EB102-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42371	42371	42371					kWh	u32	10	0	0	0	R
42373	EB102-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42373	42373	42373					kWh	u32	10	0	0	0	R
42376	EB101-EP15 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42376	42376					kWh	u32	10	0	0	0	R
42378	EB101-EP15 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42378	42378	42378					kWh	u32	10	0	0	0	R
42380	EB101-EP15 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42380	42380	42380					kWh	u32	10	0	0	0	R
42382	EB101-EP15 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42382	42382	42382					kWh	u32	10	0	0	0	R
42384	EB101-EP15 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42384	42384	42384					kWh	u32	10	0	0	0	R
42386	EB101-EP15 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42386	42386	42386					kWh	u32	10	0	0	0	R
42388	EB101-EP15 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42388	42388	42388					kWh	u32	10	0	0	0	R
42391	EB101-EP14 Heat Meter - Pool2 Cpr	Accumulated energy production as calculated by the heat meter							42391	42391					kWh	u32	10	0	0	0	R
42393	EB101-EP14 Heat Meter - HW Cpr and Add	Accumulated energy production as calculated by the heat meter						42393	42393	42393			42393	42393	kWh	u32	10	0	0	0	R
42395	EB101-EP14 Heat Meter - Heat Cpr and Add	Accumulated energy production as calculated by the heat meter						42395	42395	42395			42395	42395	kWh	u32	10	0	0	0	R
42397	EB101-EP14 Heat Meter - Cooling Cpr	Accumulated energy production as calculated by the heat meter						42397	42397	42397			42397	42397	kWh	u32	10	0	0	0	R
42399	EB101-EP14 Heat Meter - Pool Cpr	Accumulated energy production as calculated by the heat meter						42399	42399	42399			42399	42399	kWh	u32	10	0	0	0	R
42401	EB101-EP14 Heat Meter - HW Cpr	Accumulated energy production as calculated by the heat meter						42401	42401	42401			42401	42401	kWh	u32	10	0	0	0	R
42403	EB101-EP14 Heat Meter - Heat Cpr	Accumulated energy production as calculated by the heat meter						42403	42403	42403			42403	42403	kWh	u32	10	0	0	0	R
42435	Heat Meter - HW Cpr and Add - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system							42435	42435			42435	42435	kWh	u32	10	0	0	0	R
42437	Heat Meter - HW Cpr and Add - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system			42437	42437	42437	42437					42437	42437	kWh	u32	10	0	0	0	R
42439	Heat Meter - Heat Cpr and Add - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system			42439	42439	42439	42439	42439	42439			42439	42439	kWh	u32	10	0	0	0	R
42441	Heat Meter - Cooling Cpr - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system					42441	42441	42441	42441			42441	42441	kWh	u32	10	0	0	0	R
42443	Heat Meter - Pool Cpr - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system			42443	42443	42443	42443	42443	42443			42443	42443	kWh	u32	10	0	0	0	R
42445	Heat Meter - HW Cpr - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system			42445	42445	42445	42445	42445	42445			42445	42445	kWh	u32	10	0	0	0	R
42447	Heat Meter - Heat Cpr - Total system	Accumulated energy production as calculated by the heat meter, summaries of all heat pumps in system			42447	42447	42447	42447	42447	42447			42447	42447	kWh	u32	10	0	0	0	R
42464	External ERS 4 fire place guard						42464	42464	42464	42464		42464	42464	42464		u8	1	0	0	0	R
42465	External ERS 3 fire place guard						42465	42465	42465	42465		42465	42465	42465		u8	1	0	0	0	R
42466	External ERS 2 fire place guard						42466	42466	42466	42466		42466	42466	42466		u8	1	0	0	0	R
42467	External ERS 1 fire place guard						42467	42467	42467	42467		42467	42467	42467		u8	1	0	0	0	R
42468	EB108 External Energy Meter 2 Accumulated Energy							42468	42468	42468		42468			kWh	u32	1	0	0	0	R
42470	EB108 External Energy Meter 1 Accumulated Energy							42470	42470	42470		42470			kWh	u32	1	0	0	0	R
42472	EB107 External Energy Meter 2 Accumulated Energy							42472	42472	42472		42472			kWh	u32	1	0	0	0	R
42474	EB107 External Energy Meter 1 Accumulated Energy							42474	42474	42474		42474			kWh	u32	1	0	0	0	R
42476	EB106 External Energy Meter 2 Accumulated Energy							42476	42476	42476		42476			kWh	u32	1	0	0	0	R
42478	EB106 External Energy Meter 1 Accumulated Energy							42478	42478	42478		42478			kWh	u32	1	0	0	0	R
42480	EB105 External Energy Meter 2 Accumulated Energy							42480	42480	42480		42480			kWh	u32	1	0	0	0	R
42482	EB105 External Energy Meter 1 Accumulated Energy							42482	42482	42482		42482			kWh	u32	1	0	0	0	R
42484	EB104 External Energy Meter 2 Accumulated Energy							42484	42484	42484		42484			kWh	u32	1	0	0	0	R
42486	EB104 External Energy Meter 1 Accumulated Energy							42486	42486	42486		42486			kWh	u32	1	0	0	0	R
42488	EB103 External Energy Meter 2 Accumulated Energy							42488	42488	42488		42488			kWh	u32	1	0	0	0	R
42490	EB103 External Energy Meter 1 Accumulated Energy							42490	42490	42490		42490			kWh	u32	1	0	0	0	R
42492	EB102 External Energy Meter 2 Accumulated Energy							42492	42492	42492		42492			kWh	u32	1	0	0	0	R
42494	EB102 External Energy Meter 1 Accumulated Energy							42494	42494	42494		42494			kWh	u32	1	0	0	0	R
42496	EB101 External Energy Meter 2 Accumulated Energy							42496	42496	42496		42496	42496	42496	kWh	u32	1	0	0	0	R
42498	EB101 External Energy Meter 1 Accumulated Energy							42498	42498	42498		42498	42498	42498	kWh	u32	1	0	0	0	R
42504	External Energy Meter Accumulated System				42504	42504	42504	42504	42504	42504		42504	42504	42504	kWh	u32	1	0	0	0	R
43001	Software version		43001	43001	43001	43001	43001	43001	43001	43001	43001	43001	43001	43001		u16	1	0	0	0	R
43005	Degree Minutes (16 bit)	Degree minutes, 16bit value (-32768 < x < 32767). Values outside valid values are rounded to the closest valid value.			43005	43005	43005	43005	43005	43005	43005	43005	43005	43005		s16	10	-30000	30000	0	R/W
43006	Calc. Supply S4	Calculated supply temperature for the climate system	43006	43006	43006	43006	43006	43006	43006	43006		43006	43006	43006	°C	s16	10	0	0	0	R
43007	Calc. Supply S3	Calculated supply temperature for the climate system	43007	43007	43007	43007	43007	43007	43007	43007		43007	43007	43007	°C	s16	10	0	0	0	R
43008	Calc. Supply S2	Calculated supply temperature for the climate system	43008	43008	43008	43008	43008	43008	43008	43008		43008	43008	43008	°C	s16	10	0	0	0	R
43009	Calc. Supply S1	Calculated supply temperature for the climate system	43009	43009	43009	43009	43009	43009	43009	43009	43009	43009	43009	43009	°C	s16	10	0	0	0	R
43013	Freeze Protection Status	1 = Freeze protection active	43013	43013	43013	43013	43013	43013	43013	43013	43013	43013	43013	43013		u8	1	0	0	0	R
43024	Status Cooling	 0=Off 1=On					43024	43024			43024	43024	43024	43024		u8	1	0	0	0	R
43061	t. after start timer				43061											u8	1	0	0	0	R
43062	t. after mode change	Time after mode change			43062	43062										u8	1	0	0	0	R
43064	Heat Medium Flow dT Set Point	Set point delta T for the heat medium flow			43064	43064	43064	43064	43064	43064						s16	10	0	0	0	R
43065	Heat Medium Flow dT Actual	Current value of the delta T for the heat medium flow			43065	43065	43065	43065	43065	43065	43065	43065		43065		s16	10	0	0	0	R
43066	Defrosting time	Defrosting time			43066	43066									s	s16	1	0	0	0	R
43081	Tot. op.time add.	Total electric additive operation time	43081	43081	43081	43081	43081	43081	43081	43081	43081	43081	43081	43081	h	s32	10	0	1000000	0	R
43084	Int. el.add. Power	Current power from the internal electrical addition	43084	43084	43084	43084	43084	43084	43084	43084	43084	43084	43084	43084	kW	s16	100	0	0	0	R
43086	Prio	Indicates what heating action (HW/heat/pool) currently prioritised 10=Off 20=Hot Water 30=Heat 40=Pool 41=Pool 2 50=Transfer 60=Cooling	43086	43086	43086	43086	43086	43086	43086	43086	43086	43086	43086	43086		u8	1	0	0	0	R
43091	Int. el.add. State	Number of steps active for internal step-controlled addition	43091	43091	43091	43091	43091	43091	43091	43091	43091	43091	43091	43091		u8	1	0	0	0	R
43093	Mixing Valve State S4	State of the mixing valve for the climate system	43093	43093	43093	43093	43093	43093	43093	43093		43093	43093	43093		u8	1	0	0	0	R
43094	Mixing Valve State S3	State of the mixing valve for the climate system	43094	43094	43094	43094	43094	43094	43094	43094		43094	43094	43094		u8	1	0	0	0	R
43095	Mixing Valve State S2	State of the mixing valve for the climate system	43095	43095	43095	43095	43095	43095	43095	43095		43095	43095	43095		u8	1	0	0	0	R
43096	Mixing Valve State S1	State of the mixing valve for the climate system	43096	43096	43096	43096	43096	43096	43096	43096	43096	43096	43096	43096		u8	1	0	0	0	R
43097	Status of the shunt controlled additional heat accessory	10 = Off, 20 = Running, 30 = Passive			43097		43097	43097	43097	43097		43097	43097			u8	1	0	0	0	R
43103	HPAC state	State of the HPAC cooling accessory.					43103	43103	43103	43103						u8	1	0	0	0	R
43105	Status FJVM	The state of the FJVM accessory	43105	43105												u8	1	0	0	0	R
43108	Fan speed current	The current fan speed after scheduling and blocks are considered	43108	43108	43108	43108	43108	43108	43108	43108					%	u8	1	0	0	0	R
43122	Compr. current min.freq.	The current minimum frequency of the compressor			43122	43122	43122		43122						Hz	s16	1	0	0	0	R
43123	Compr. current max.freq.	The current maximum frequency of the compressor			43123	43123	43123								Hz	s16	1	0	0	0	R
43124	Airflow ref.	Reference value for the airflow.			43124	43124										s16	10	0	0	0	R
43132	Inverter com. timer	This value shows the time since last communication with the inverter			43132	43132	43132		43132						sec	u16	1	0	0	0	R
43136	Compressor Frequency, Actual	The compressor frequency the compressor is currently running at			43136	43136	43136		43136						Hz	u16	10	0	0	0	R
43140	Inverter Temperature	Current inverter temparture			43140	43140	43140		43140						°C	s16	10	0	0	0	R
43141	compr. in power	The power delivered from the inverter to the compressor			43141	43141	43141		43141						W	u16	1	0	0	0	R
43144	Compr. energy total	Total compressor energy in kWh			43144										kWh	u32	100	0	9999999	0	R
43147	Compr. in current	The current delivered from the inverter to the compressor			43147	43147	43147		43147						A	s16	1	0	0	0	R
43152	Internal cooling blocked						43152	43152								u8	1	0	0	0	R
43158	External adjustment activated via input S4		43158	43158	43158	43158	43158	43158	43158	43158		43158	43158	43158		u8	1	0	0	0	R
43159	External adjustment activated via input S3		43159	43159	43159	43159	43159	43159	43159	43159		43159	43159	43159		u8	1	0	0	0	R
43160	External adjustment activated via input S2		43160	43160	43160	43160	43160	43160	43160	43160		43160	43160	43160		u8	1	0	0	0	R
43161	External adjustment activated via input S1		43161	43161	43161	43161	43161	43161	43161	43161	43161	43161	43161	43161		u8	1	0	0	0	R
43163	Blocking status of the shunt controlled add heat acc	0 = Unblocked, 1 = Blocked					43163	43163	43163	43163		43163	43163			u8	1	0	0	0	R
43164	Cooling blocked	Whether cooling is blocked					43164	43164	43164	43164						u8	1	0	0	0	R
43171	Blocking status of the step controlled add heat acc	0 = Unblocked, 1 = Blocked					43171	43171	43171	43171	43171	43171	43171	43171		u8	1	0	0	0	R
43180	HWC Pump Status GP11	Hot water circulation pump status. 1=on, 0=off	43180	43180	43180		43180	43180	43180	43180				43180		u8	1	0	0	0	R
43181	Chargepump speed				43181										%	u8	1	0	0	0	R
43182	Compressor Frequency, Target	The targeted compressor frequency, before excluding any blocked frequencies			43182	43182	43182								Hz	u16	1	0	0	0	R
43189	GP10 Ext. Supply Pump Status	External supply pump status. 1=on,0=off				43189		43189	43189	43189	43189	43189				u8	1	0	0	0	R
43230	Heat Meter (OBSOLETE)	Obsolete since v4798 of the controller software						43230				43230	43230	43230	kWh	u32	10	0	9999999	0	R
43239	Tot. HW op.time add.	Total electric additive operation time in hot water mode	43239	43239	43239	43239	43239	43239	43239	43239	43239	43239	43239	43239	h	s32	10	0	9999999	0	R
43305	Compr. energy HW	Compressor energy during hot water production in kWh			43305										kWh	u32	100	0	9999999	0	R
43371	Hot gas limit status				43371											u8	1	0	0	0	R
43372	Evaporater limit status				43372											u8	1	0	0	0	R
43375	compr. in power mean	Mean power delivered from the inverter to the compressor. Mean is calculated every 10 seconds.			43375	43375	43375		43375						W	s16	1	0	0	0	R
43382	Inverter mem error code				43382											u16	1	0	0	0	R
43383	FJVM Relays	Indicates the active relays on the FJVM accessory. The information is binary encoded	43383	43383												u8	1	0	0	0	R
43395	HPAC Relays	Indicates the active relays on the HPAC accessory. The information is binary encoded					43395	43395								u8	1	0	0	0	R
43414	Compressor starts EB100-EP15	Number of compressorer starts							43414	43414						s32	1	0	0	0	R
43416	Compressor starts EB100-EP14	Number of compressorer starts	43416	43416	43416	43416	43416	43416	43416	43416						s32	1	0	9999999	0	R
43418	Tot. op.time compr. EB100-EP15	Total compressorer operation time							43418	43418					h	s32	1	0	0	0	R
43420	Tot. op.time compr. EB100-EP14	Total compressorer operation time	43420	43420	43420	43420	43420	43420	43420	43420					h	s32	1	0	9999999	0	R
43422	Tot. HW op.time compr. EB100-EP15	Total compressorer operation time in hot water mode							43422	43422					h	s32	1	0	0	0	R
43424	Tot. HW op.time compr. EB100-EP14	Total compressorer operation time in hot water mode	43424	43424	43424	43424	43424	43424	43424	43424					h	s32	1	0	9999999	0	R
43426	Compressor State EP15	20 = Stopped, 40 = Starting, 60 = Running, 100 = Stopping							43426	43426						u8	1	0	0	0	R
43427	Compressor State EP14	20 = Stopped, 40 = Starting, 60 = Running, 100 = Stopping	43427	43427	43427	43427	43427	43427	43427	43427						u8	1	0	0	0	R
43430	Supply Pump State EP15	10=off,15=starting,20=on,40=10-day mode,80=calibration							43430	43430						u8	1	0	0	0	R
43431	Supply Pump State EP14	10=off,15=starting,20=on,40=10-day mode,80=calibration	43431	43431	43431	43431	43431	43431	43431	43431						u8	1	0	0	0	R
43432	Brine Pump State EP15	10=off,15=starting,20=on,40=10-day mode,80=calibration							43432	43432						u8	1	0	0	0	R
43433	Brine Pump State EP14	10=off,15=starting,20=on,40=10-day mode,80=calibration					43433	43433	43433	43433						u8	1	0	0	0	R
43434	Cpr Status EP15	Status of the compressor. 1=on,0=off 0=Off 1=On							43434	43434						u8	1	0	0	0	R
43435	Cpr Status EP14	Status of the compressor. 1=on,0=off 0=Off 1=On	43435	43435	43435	43435	43435	43435	43435	43435						u8	1	0	0	0	R
43436	Supply Pump Speed EP15	Supply pump speed in %							43436	43436					%	u8	1	0	0	0	R
43437	Supply Pump Speed EP14	Supply pump speed in %			43437	43437	43437	43437	43437	43437			43437	43437	%	u8	1	0	0	0	R
43438	EP15-GP2 Brine Pump Status	Brine pump speed in %							43438	43438					%	u8	1	0	0	0	R
43439	EP14-GP2 Brine Pump Status EP14	Brine pump speed in %					43439	43439	43439	43439					%	u8	1	0	0	0	R
43444	State OEK	The state of the OEK accessory			43444											u8	1	0	0	0	R
43460	State DEH	The state of the DEH accessory	43460	43460												u8	1	0	0	0	R
43473	Docked Heat Compressors	Number of compressors docked to heating						43473	43473	43473	43473	43473	43473	43473		u8	1	0	0	0	R
43474	Docked Hot Water Compressors	Number of compressors docked to hot water						43474	43474	43474	43474	43474	43474	43474		u8	1	0	0	0	R
43475	Docked Pool 1 Compressors	Number of compressors docked to pool 1						43475	43475	43475		43475	43475	43475		u8	1	0	0	0	R
43481	QN10 State	0=Heating, 1=Hot water							43481	43481						u8	1	0	0	0	R
43484	FLM 4 Cooling Status	Whether FLM cooling is active, 1=yes, 0=no					43484	43484	43484	43484						u8	1	0	0	0	R
43485	FLM 3 Cooling Status	Whether FLM cooling is active, 1=yes, 0=no					43485	43485	43485	43485						u8	1	0	0	0	R
43486	FLM 2 Cooling Status	Whether FLM cooling is active, 1=yes, 0=no					43486	43486	43486	43486						u8	1	0	0	0	R
43487	FLM 1 Cooling Status	Whether FLM cooling is active, 1=yes, 0=no					43487	43487	43487	43487						u8	1	0	0	0	R
43490	Steps ext. add.	Number of steps active external addition							43490	43490			43490	43490		u8	1	0	0	0	R
43513	EB100-EP15 PCA Base Relays	Indicates active relays on the PCA Base card. Please refer to the wiring diagram for relay description. Binary encoded. 1=on, 0=off. Bit0=K4,Bit1=K3,Bit2=K2,Bit3=K1							43513	43513						u8	1	0	0	0	R
43514	EB100-EP14 PCA Base Relays	Indicates active relays on the PCA Base card. Please refer to the wiring diagram for relay description. Binary encoded. 1=on, 0=off. Bit0=K4,Bit1=K3,Bit2=K2,Bit3=K1	43514	43514	43514	43514	43514	43514	43514	43514	43514	43514	43514	43514		u8	1	0	0	0	R
43516	PCA-Power Relays EP14	Indicates the active relays on the PCA-Power card. The information is binary encoded	43516	43516	43516	43516	43516	43516	43516	43516	43516	43516	43516	43516		u8	1	0	0	0	R
43536	Ext. Addition Blocked													43536		u8	1	0	0	0	R
43542	Calculated supply air temp.				43542		43542								°C	s16	10	0	0	0	R
43555	HW Comfort Shunt State	10=shunt off,20=shunt open,30=shunt closed					43555	43555	43555	43555		43555	43555			u8	1	0	0	0	R
43556	HW Comfort Add Status	1=on,0=off					43556	43556	43556	43556		43556	43556			u8	1	0	0	0	R
43560	Pool 2 blocked						43560	43560	43560	43560		43560				u8	1	0	0	0	R
43561	Pool 1 blocked				43561		43561	43561	43561	43561		43561	43561	43561		u8	1	0	0	0	R
43563	GP9 Pool 2 Valve						43563	43563	43563	43563		43563				u8	1	0	0	0	R
43564	GP9 Pool 1 Valve						43564	43564	43564	43564		43564	43564	43564		u8	1	0	0	0	R
43577	Docked Pool 2 Compressors	Number of compressors docked to pool 2						43577	43577	43577		43577				u8	1	0	0	0	R
43580	EB108 Version							43580	43580	43580		43580				u16	1	0	0	0	R
43598	EB108 Slave Type							43598	43598	43598		43598				u8	1	0	0	0	R
43599	EB108 Compressor EP14 Size							43599	43599	43599		43599			kW	u8	1	0	0	0	R
43600	EB108-EP15-BT3 Return Temp.	Return temperature, BT3						43600	43600	43600					°C	s16	10	0	0	0	R
43601	EB108-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43601	43601	43601					°C	s16	10	0	0	0	R
43602	EB108-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43602	43602	43602					°C	s16	10	0	0	0	R
43603	EB108-EP15-BT12 Condensor Out	Condensor temperature, BT12						43603	43603	43603					°C	s16	10	0	0	0	R
43604	EB108-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43604	43604	43604					°C	s16	10	0	0	0	R
43605	EB108-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43605	43605	43605					°C	s16	10	0	0	0	R
43606	EB108-EP15-BT17 Suction	Suction temperature, BT17						43606	43606	43606					°C	s16	10	0	0	0	R
43607	EB108-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43607	43607	43607					°C	s16	10	0	0	0	R
43608	EB108-EP15-BP8 Pressure Transmitter							43608	43608	43608					°C	s16	10	0	0	0	R
43609	EB108-EP15 Compressor State	On/Off						43609	43609	43609						u8	1	0	0	0	R
43610	EB108-EP15 Compr. time to start							43610	43610	43610						u8	1	0	0	0	R
43611	EB108-EP15 Relay status							43611	43611	43611						u16	1	0	0	0	R
43612	EB108-EP15 Heat med. pump status							43612	43612	43612					%	u8	1	0	0	0	R
43613	EB108-EP15 Brine pump status							43613	43613	43613					%	u8	1	0	0	0	R
43614	EB108-EP15 Compressor starts							43614	43614	43614						u32	1	0	0	0	R
43616	EB108-EP15 Tot. op.time compr							43616	43616	43616					h	u32	1	0	0	0	R
43618	EB108-EP15 Tot. HW op.time compr							43618	43618	43618					h	u32	1	0	0	0	R
43620	EB108-EP15 Alarm number	The value indicates the most severe current alarm						43620	43620	43620						u16	1	0	0	0	R
43621	EB108-EP14-BT3 Return Temp.	Return temperature, BT3						43621	43621	43621		43621			°C	s16	10	0	0	0	R
43622	EB108-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43622	43622	43622					°C	s16	10	0	0	0	R
43623	EB108-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43623	43623	43623					°C	s16	10	0	0	0	R
43624	EB108-EP14-BT12 Condensor Out	Condensor temperature, BT12						43624	43624	43624		43624			°C	s16	10	0	0	0	R
43625	EB108-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43625	43625	43625		43625			°C	s16	10	0	0	0	R
43626	EB108-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43626	43626	43626		43626			°C	s16	10	0	0	0	R
43627	EB108-EP14-BT17 Suction	Suction temperature, BT17						43627	43627	43627		43627			°C	s16	10	0	0	0	R
43628	EB108-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43628	43628	43628					°C	s16	10	0	0	0	R
43629	EB108-EP14-BP8 Pressure Transmitter							43629	43629	43629					°C	s16	10	0	0	0	R
43630	EB108-EP14 Compressor State	On/Off						43630	43630	43630						u8	1	0	0	0	R
43631	EB108-EP14 Compr. time to start							43631	43631	43631		43631				u8	1	0	0	0	R
43632	EB108-EP14 Relay status							43632	43632	43632						u16	1	0	0	0	R
43633	EB108-EP14 Heat med. pump status							43633	43633	43633					%	u8	1	0	0	0	R
43634	EB108-EP14 Brine pump status							43634	43634	43634					%	u8	1	0	0	0	R
43635	EB108-EP14 Compressor starts							43635	43635	43635		43635				u32	1	0	9999999	0	R
43637	EB108-EP14 Tot. op.time compr							43637	43637	43637		43637			h	u32	1	0	9999999	0	R
43639	EB108-EP14 Tot. HW op.time compr							43639	43639	43639		43639			h	u32	1	0	9999999	0	R
43641	EB108-EP14 Alarm number	The value indicates the most severe current alarm						43641	43641	43641		43641				u16	1	0	0	0	R
43642	EB107 Version							43642	43642	43642		43642				u16	1	0	0	0	R
43660	EB107 Slave Type							43660	43660	43660		43660				u8	1	0	0	0	R
43661	EB107 Compressor EP14 Size							43661	43661	43661		43661			kW	u8	1	0	0	0	R
43662	EB107-EP15-BT3 Return Temp.	Return temperature, BT3						43662	43662	43662					°C	s16	10	0	0	0	R
43663	EB107-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43663	43663	43663					°C	s16	10	0	0	0	R
43664	EB107-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43664	43664	43664					°C	s16	10	0	0	0	R
43665	EB107-EP15-BT12 Condensor Out	Condensor temperature, BT12						43665	43665	43665					°C	s16	10	0	0	0	R
43666	EB107-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43666	43666	43666					°C	s16	10	0	0	0	R
43667	EB107-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43667	43667	43667					°C	s16	10	0	0	0	R
43668	EB107-EP15-BT17 Suction	Suction temperature, BT17						43668	43668	43668					°C	s16	10	0	0	0	R
43669	EB107-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43669	43669	43669					°C	s16	10	0	0	0	R
43670	EB107-EP15-BP8 Pressure Transmitter							43670	43670	43670					°C	s16	10	0	0	0	R
43671	EB107-EP15 Compressor State	On/Off						43671	43671	43671						u8	1	0	0	0	R
43672	EB107-EP15 Compr. time to start							43672	43672	43672						u8	1	0	0	0	R
43673	EB107-EP15 Relay status							43673	43673	43673						u16	1	0	0	0	R
43674	EB107-EP15 Heat med. pump status							43674	43674	43674					%	u8	1	0	0	0	R
43675	EB107-EP15 Brine pump status							43675	43675	43675					%	u8	1	0	0	0	R
43676	EB107-EP15 Compressor starts							43676	43676	43676						u32	1	0	0	0	R
43678	EB107-EP15 Tot. op.time compr							43678	43678	43678					h	u32	1	0	0	0	R
43680	EB107-EP15 Tot. HW op.time compr							43680	43680	43680					h	u32	1	0	0	0	R
43682	EB107-EP15 Alarm number	The value indicates the most severe current alarm						43682	43682	43682						u16	1	0	0	0	R
43683	EB107-EP14-BT3 Return Temp.	Return temperature, BT3						43683	43683	43683		43683			°C	s16	10	0	0	0	R
43684	EB107-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43684	43684	43684					°C	s16	10	0	0	0	R
43685	EB107-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43685	43685	43685					°C	s16	10	0	0	0	R
43686	EB107-EP14-BT12 Condensor Out	Condensor temperature, BT12						43686	43686	43686		43686			°C	s16	10	0	0	0	R
43687	EB107-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43687	43687	43687		43687			°C	s16	10	0	0	0	R
43688	EB107-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43688	43688	43688		43688			°C	s16	10	0	0	0	R
43689	EB107-EP14-BT17 Suction	Suction temperature, BT17						43689	43689	43689		43689			°C	s16	10	0	0	0	R
43690	EB107-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43690	43690	43690					°C	s16	10	0	0	0	R
43691	EB107-EP14-BP8 Pressure Transmitter							43691	43691	43691					°C	s16	10	0	0	0	R
43692	EB107-EP14 Compressor State							43692	43692	43692		43692				u8	1	0	0	0	R
43693	EB107-EP14 Compr. time to start							43693	43693	43693		43693				u8	1	0	0	0	R
43694	EB107-EP14 Relay status							43694	43694	43694						u16	1	0	0	0	R
43695	EB107-EP14 Heat med. pump status							43695	43695	43695					%	u8	1	0	0	0	R
43696	EB107-EP14 Brine pump status							43696	43696	43696					%	u8	1	0	0	0	R
43697	EB107-EP14 Compressor starts							43697	43697	43697		43697				u32	1	0	9999999	0	R
43699	EB107-EP14 Tot. op.time compr							43699	43699	43699		43699			h	u32	1	0	9999999	0	R
43701	EB107-EP14 Tot. HW op.time compr							43701	43701	43701		43701			h	u32	1	0	9999999	0	R
43703	EB107-EP14 Alarm number	The value indicates the most severe current alarm						43703	43703	43703		43703				u16	1	0	0	0	R
43704	EB106 Version							43704	43704	43704		43704				u16	1	0	0	0	R
43722	EB106 Slave Type							43722	43722	43722		43722				u8	1	0	0	0	R
43723	EB106 Compressor EP14 Size							43723	43723	43723		43723			kW	u8	1	0	0	0	R
43724	EB106-EP15-BT3 Return Temp.	Return temperature, BT3						43724	43724	43724					°C	s16	10	0	0	0	R
43725	EB106-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43725	43725	43725					°C	s16	10	0	0	0	R
43726	EB106-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43726	43726	43726					°C	s16	10	0	0	0	R
43727	EB106-EP15-BT12 Condensor Out	Condensor temperature, BT12						43727	43727	43727					°C	s16	10	0	0	0	R
43728	EB106-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43728	43728	43728					°C	s16	10	0	0	0	R
43729	EB106-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43729	43729	43729					°C	s16	10	0	0	0	R
43730	EB106-EP15-BT17 Suction	Suction temperature, BT17						43730	43730	43730					°C	s16	10	0	0	0	R
43731	EB106-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43731	43731	43731					°C	s16	10	0	0	0	R
43732	EB106-EP15-BP8 Pressure Transmitter							43732	43732	43732					°C	s16	10	0	0	0	R
43733	EB106-EP15 Compressor State	On/Off						43733	43733	43733						u8	1	0	0	0	R
43734	EB106-EP15 Compr. time to start							43734	43734	43734						u8	1	0	0	0	R
43735	EB106-EP15 Relay status							43735	43735	43735						u16	1	0	0	0	R
43736	EB106-EP15 Heat med. pump status							43736	43736	43736					%	u8	1	0	0	0	R
43737	EB106-EP15 Brine pump status							43737	43737	43737					%	u8	1	0	0	0	R
43738	EB106-EP15 Compressor starts							43738	43738	43738						u32	1	0	0	0	R
43740	EB106-EP15 Tot. op.time compr							43740	43740	43740					h	u32	1	0	0	0	R
43742	EB106-EP15 Tot. HW op.time compr							43742	43742	43742					h	u32	1	0	0	0	R
43744	EB106-EP15 Alarm number	The value indicates the most severe current alarm						43744	43744	43744						u16	1	0	0	0	R
43745	EB106-EP14-BT3 Return Temp.	Return temperature, BT3						43745	43745	43745		43745			°C	s16	10	0	0	0	R
43746	EB106-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43746	43746	43746					°C	s16	10	0	0	0	R
43747	EB106-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43747	43747	43747					°C	s16	10	0	0	0	R
43748	EB106-EP14-BT12 Condensor Out	Condensor temperature, BT12						43748	43748	43748		43748			°C	s16	10	0	0	0	R
43749	EB106-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43749	43749	43749		43749			°C	s16	10	0	0	0	R
43750	EB106-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43750	43750	43750		43750			°C	s16	10	0	0	0	R
43751	EB106-EP14-BT17 Suction	Suction temperature, BT17						43751	43751	43751		43751			°C	s16	10	0	0	0	R
43752	EB106-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43752	43752	43752					°C	s16	10	0	0	0	R
43753	EB106-EP14-BP8 Pressure Transmitter							43753	43753	43753					°C	s16	10	0	0	0	R
43754	EB106-EP14 Compressor State	On/Off						43754	43754	43754						u8	1	0	0	0	R
43755	EB106-EP14 Compr. time to start							43755	43755	43755		43755				u8	1	0	0	0	R
43756	EB106-EP14 Relay status							43756	43756	43756						u16	1	0	0	0	R
43757	EB106-EP14 Heat med. pump status							43757	43757	43757					%	u8	1	0	0	0	R
43758	EB106-EP14 Brine pump status							43758	43758	43758					%	u8	1	0	0	0	R
43759	EB106-EP14 Compressor starts							43759	43759	43759		43759				u32	1	0	9999999	0	R
43761	EB106-EP14 Tot. op.time compr							43761	43761	43761		43761			h	u32	1	0	9999999	0	R
43763	EB106-EP14 Tot. HW op.time compr							43763	43763	43763		43763			h	u32	1	0	9999999	0	R
43765	EB106-EP14 Alarm number	The value indicates the most severe current alarm						43765	43765	43765		43765				u16	1	0	0	0	R
43766	EB105 Version							43766	43766	43766		43766				u16	1	0	0	0	R
43784	EB105 Slave Type							43784	43784	43784		43784				u8	1	0	0	0	R
43785	EB105 Compressor EP14 Size							43785	43785	43785		43785			kW	u8	1	0	0	0	R
43786	EB105-EP15-BT3 Return Temp.	Return temperature, BT3						43786	43786	43786					°C	s16	10	0	0	0	R
43787	EB105-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43787	43787	43787					°C	s16	10	0	0	0	R
43788	EB105-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43788	43788	43788					°C	s16	10	0	0	0	R
43789	EB105-EP15-BT12 Condensor Out	Condensor temperature, BT12						43789	43789	43789					°C	s16	10	0	0	0	R
43790	EB105-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43790	43790	43790					°C	s16	10	0	0	0	R
43791	EB105-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43791	43791	43791					°C	s16	10	0	0	0	R
43792	EB105-EP15-BT17 Suction	Suction temperature, BT17						43792	43792	43792					°C	s16	10	0	0	0	R
43793	EB105-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43793	43793	43793					°C	s16	10	0	0	0	R
43794	EB105-EP15-BP8 Pressure Transmitter							43794	43794	43794					°C	s16	10	0	0	0	R
43795	EB105-EP15 Compressor State	On/Off						43795	43795	43795						u8	1	0	0	0	R
43796	EB105-EP15 Compr. time to start							43796	43796	43796						u8	1	0	0	0	R
43797	EB105-EP15 Relay status							43797	43797	43797						u16	1	0	0	0	R
43798	EB105-EP15 Heat med. pump status							43798	43798	43798					%	u8	1	0	0	0	R
43799	EB105-EP15 Brine pump status							43799	43799	43799					%	u8	1	0	0	0	R
43800	EB105-EP15 Compressor starts							43800	43800	43800						u32	1	0	0	0	R
43802	EB105-EP15 Tot. op.time compr							43802	43802	43802					h	u32	1	0	0	0	R
43804	EB105-EP15 Tot. HW op.time compr							43804	43804	43804					h	u32	1	0	0	0	R
43806	EB105-EP15 Alarm number	The value indicates the most severe current alarm						43806	43806	43806						u16	1	0	0	0	R
43807	EB105-EP14-BT3 Return Temp.	Return temperature, BT3						43807	43807	43807		43807			°C	s16	10	0	0	0	R
43808	EB105-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43808	43808	43808					°C	s16	10	0	0	0	R
43809	EB105-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43809	43809	43809					°C	s16	10	0	0	0	R
43810	EB105-EP14-BT12 Condensor Out	Condensor temperature, BT12						43810	43810	43810		43810			°C	s16	10	0	0	0	R
43811	EB105-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43811	43811	43811		43811			°C	s16	10	0	0	0	R
43812	EB105-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43812	43812	43812		43812			°C	s16	10	0	0	0	R
43813	EB105-EP14-BT17 Suction	Suction temperature, BT17						43813	43813	43813		43813			°C	s16	10	0	0	0	R
43814	EB105-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43814	43814	43814					°C	s16	10	0	0	0	R
43815	EB105-EP14-BP8 Pressure Transmitter							43815	43815	43815					°C	s16	10	0	0	0	R
43816	EB105-EP14 Compressor State	On/Off						43816	43816	43816						u8	1	0	0	0	R
43817	EB105-EP14 Compr. time to start							43817	43817	43817		43817				u8	1	0	0	0	R
43818	EB105-EP14 Relay status							43818	43818	43818						u16	1	0	0	0	R
43819	EB105-EP14 Heat med. pump status							43819	43819	43819					%	u8	1	0	0	0	R
43820	EB105-EP14 Brine pump status							43820	43820	43820					%	u8	1	0	0	0	R
43821	EB105-EP14 Compressor starts							43821	43821	43821		43821				u32	1	0	9999999	0	R
43823	EB105-EP14 Tot. op.time compr							43823	43823	43823		43823			h	u32	1	0	9999999	0	R
43825	EB105-EP14 Tot. HW op.time compr							43825	43825	43825		43825			h	u32	1	0	9999999	0	R
43827	EB105-EP14 Alarm number	The value indicates the most severe current alarm						43827	43827	43827		43827				u16	1	0	0	0	R
43828	EB104 Version							43828	43828	43828		43828				u16	1	0	0	0	R
43846	EB104 Slave Type							43846	43846	43846		43846				u8	1	0	0	0	R
43847	EB104 Compressor EP14 Size							43847	43847	43847		43847			kW	u8	1	0	0	0	R
43848	EB104-EP15-BT3 Return Temp.	Return temperature, BT3						43848	43848	43848					°C	s16	10	0	0	0	R
43849	EB104-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43849	43849	43849					°C	s16	10	0	0	0	R
43850	EB104-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43850	43850	43850					°C	s16	10	0	0	0	R
43851	EB104-EP15-BT12 Condensor Out	Condensor temperature, BT12						43851	43851	43851					°C	s16	10	0	0	0	R
43852	EB104-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43852	43852	43852					°C	s16	10	0	0	0	R
43853	EB104-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43853	43853	43853					°C	s16	10	0	0	0	R
43854	EB104-EP15-BT17 Suction	Suction temperature, BT17						43854	43854	43854					°C	s16	10	0	0	0	R
43855	EB104-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43855	43855	43855					°C	s16	10	0	0	0	R
43856	EB104-EP15-BP8 Pressure Transmitter							43856	43856	43856					°C	s16	10	0	0	0	R
43857	EB104-EP15 Compressor State	On/Off						43857	43857	43857						u8	1	0	0	0	R
43858	EB104-EP15 Compr. time to start							43858	43858	43858						u8	1	0	0	0	R
43859	EB104-EP15 Relay status							43859	43859	43859						u16	1	0	0	0	R
43860	EB104-EP15 Heat med. pump status							43860	43860	43860					%	u8	1	0	0	0	R
43861	EB104-EP15 Brine pump status							43861	43861	43861					%	u8	1	0	0	0	R
43862	EB104-EP15 Compressor starts							43862	43862	43862						u32	1	0	0	0	R
43864	EB104-EP15 Tot. op.time compr							43864	43864	43864					h	u32	1	0	0	0	R
43866	EB104-EP15 Tot. HW op.time compr							43866	43866	43866					h	u32	1	0	0	0	R
43868	EB104-EP15 Alarm number	The value indicates the most severe current alarm						43868	43868	43868						u16	1	0	0	0	R
43869	EB104-EP14-BT3 Return Temp.	Return temperature, BT3						43869	43869	43869		43869			°C	s16	10	0	0	0	R
43870	EB104-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43870	43870	43870					°C	s16	10	0	0	0	R
43871	EB104-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43871	43871	43871					°C	s16	10	0	0	0	R
43872	EB104-EP14-BT12 Condensor Out	Condensor temperature, BT12						43872	43872	43872		43872			°C	s16	10	0	0	0	R
43873	EB104-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43873	43873	43873		43873			°C	s16	10	0	0	0	R
43874	EB104-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43874	43874	43874		43874			°C	s16	10	0	0	0	R
43875	EB104-EP14-BT17 Suction	Suction temperature, BT17						43875	43875	43875		43875			°C	s16	10	0	0	0	R
43876	EB104-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43876	43876	43876					°C	s16	10	0	0	0	R
43877	EB104-EP14-BP8 Pressure Transmitter							43877	43877	43877					°C	s16	10	0	0	0	R
43878	EB104-EP14 Compressor State	On/Off						43878	43878	43878						u8	1	0	0	0	R
43879	EB104-EP14 Compr. time to start							43879	43879	43879		43879				u8	1	0	0	0	R
43880	EB104-EP14 Relay status							43880	43880	43880						u16	1	0	0	0	R
43881	EB104-EP14 Heat med. pump status							43881	43881	43881					%	u8	1	0	0	0	R
43882	EB104-EP14 Brine pump status							43882	43882	43882					%	u8	1	0	0	0	R
43883	EB104-EP14 Compressor starts							43883	43883	43883		43883				u32	1	0	9999999	0	R
43885	EB104-EP14 Tot. op.time compr							43885	43885	43885		43885			h	u32	1	0	9999999	0	R
43887	EB104-EP14 Tot. HW op.time compr							43887	43887	43887		43887			h	u32	1	0	9999999	0	R
43889	EB104-EP14 Alarm number	The value indicates the most severe current alarm						43889	43889	43889		43889				u16	1	0	0	0	R
43890	EB103 Version							43890	43890	43890		43890				u16	1	0	0	0	R
43908	EB103 Slave Type							43908	43908	43908		43908				u8	1	0	0	0	R
43909	EB103 Compressor EP14 Size							43909	43909	43909		43909			kW	u8	1	0	0	0	R
43910	EB103-EP15-BT3 Return Temp.	Return temperature, BT3						43910	43910	43910					°C	s16	10	0	0	0	R
43911	EB103-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43911	43911	43911					°C	s16	10	0	0	0	R
43912	EB103-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43912	43912	43912					°C	s16	10	0	0	0	R
43913	EB103-EP15-BT12 Condensor Out	Condensor temperature, BT12						43913	43913	43913					°C	s16	10	0	0	0	R
43914	EB103-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43914	43914	43914					°C	s16	10	0	0	0	R
43915	EB103-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43915	43915	43915					°C	s16	10	0	0	0	R
43916	EB103-EP15-BT17 Suction	Suction temperature, BT17						43916	43916	43916					°C	s16	10	0	0	0	R
43917	EB103-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43917	43917	43917					°C	s16	10	0	0	0	R
43918	EB103-EP15-BP8 Pressure Transmitter							43918	43918	43918					°C	s16	10	0	0	0	R
43919	EB103-EP15 Compressor State	On/Off						43919	43919	43919						u8	1	0	0	0	R
43920	EB103-EP15 Compr. time to start							43920	43920	43920						u8	1	0	0	0	R
43921	EB103-EP15 Relay status							43921	43921	43921						u16	1	0	0	0	R
43922	EB103-EP15 Heat med. pump status							43922	43922	43922					%	u8	1	0	0	0	R
43923	EB103-EP15 Brine pump status							43923	43923	43923					%	u8	1	0	0	0	R
43924	EB103-EP15 Compressor starts							43924	43924	43924						u32	1	0	0	0	R
43926	EB103-EP15 Tot. op.time compr							43926	43926	43926					h	u32	1	0	0	0	R
43928	EB103-EP15 Tot. HW op.time compr							43928	43928	43928					h	u32	1	0	0	0	R
43930	EB103-EP15 Alarm number	The value indicates the most severe current alarm						43930	43930	43930						u16	1	0	0	0	R
43931	EB103-EP14-BT3 Return Temp.	Return temperature, BT3						43931	43931	43931		43931			°C	s16	10	0	0	0	R
43932	EB103-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43932	43932	43932					°C	s16	10	0	0	0	R
43933	EB103-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43933	43933	43933					°C	s16	10	0	0	0	R
43934	EB103-EP14-BT12 Condensor Out	Condensor temperature, BT12						43934	43934	43934		43934			°C	s16	10	0	0	0	R
43935	EB103-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43935	43935	43935		43935			°C	s16	10	0	0	0	R
43936	EB103-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43936	43936	43936		43936			°C	s16	10	0	0	0	R
43937	EB103-EP14-BT17 Suction	Suction temperature, BT17						43937	43937	43937		43937			°C	s16	10	0	0	0	R
43938	EB103-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43938	43938	43938					°C	s16	10	0	0	0	R
43939	EB103-EP14-BP8 Pressure Transmitter							43939	43939	43939					°C	s16	10	0	0	0	R
43940	EB103-EP14 Compressor State	On/Off						43940	43940	43940						u8	1	0	0	0	R
43941	EB103-EP14 Compr. time to start							43941	43941	43941		43941				u8	1	0	0	0	R
43942	EB103-EP14 Relay status							43942	43942	43942						u16	1	0	0	0	R
43943	EB103-EP14 Heat med. pump status							43943	43943	43943					%	u8	1	0	0	0	R
43944	EB103-EP14 Brine pump status							43944	43944	43944					%	u8	1	0	0	0	R
43945	EB103-EP14 Compressor starts							43945	43945	43945		43945				u32	1	0	9999999	0	R
43947	EB103-EP14 Tot. op.time compr							43947	43947	43947		43947			h	u32	1	0	9999999	0	R
43949	EB103-EP14 Tot. HW op.time compr							43949	43949	43949		43949			h	u32	1	0	9999999	0	R
43951	EB103-EP14 Alarm number	The value indicates the most severe current alarm						43951	43951	43951		43951				u16	1	0	0	0	R
43952	EB102 Version							43952	43952	43952		43952				u16	1	0	0	0	R
43970	EB102 Slave Type							43970	43970	43970		43970				u8	1	0	0	0	R
43971	EB102 Compressor EP14 Size							43971	43971	43971		43971			kW	u8	1	0	0	0	R
43972	EB102-EP15-BT3 Return Temp.	Return temperature, BT3						43972	43972	43972					°C	s16	10	0	0	0	R
43973	EB102-EP15-BT10 Brine In Temp	Brine in temperature, BT10						43973	43973	43973					°C	s16	10	0	0	0	R
43974	EB102-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						43974	43974	43974					°C	s16	10	0	0	0	R
43975	EB102-EP15-BT12 Condensor Out	Condensor temperature, BT12						43975	43975	43975					°C	s16	10	0	0	0	R
43976	EB102-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						43976	43976	43976					°C	s16	10	0	0	0	R
43977	EB102-EP15-BT15 Liquid Line	Liquid line temperature, BT15						43977	43977	43977					°C	s16	10	0	0	0	R
43978	EB102-EP15-BT17 Suction	Suction temperature, BT17						43978	43978	43978					°C	s16	10	0	0	0	R
43979	EB102-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						43979	43979	43979					°C	s16	10	0	0	0	R
43980	EB102-EP15-BP8 Pressure Transmitter							43980	43980	43980					°C	s16	10	0	0	0	R
43981	EB102-EP15 Compressor State	On/Off						43981	43981	43981						u8	1	0	0	0	R
43982	EB102-EP15 Compr. time to start							43982	43982	43982						u8	1	0	0	0	R
43983	EB102-EP15 Relay status							43983	43983	43983						u16	1	0	0	0	R
43984	EB102-EP15 Heat med. pump status							43984	43984	43984					%	u8	1	0	0	0	R
43985	EB102-EP15 Brine pump status							43985	43985	43985					%	u8	1	0	0	0	R
43986	EB102-EP15 Compressor starts							43986	43986	43986						u32	1	0	0	0	R
43988	EB102-EP15 Tot. op.time compr							43988	43988	43988					h	u32	1	0	0	0	R
43990	EB102-EP15 Tot. HW op.time compr							43990	43990	43990					h	u32	1	0	0	0	R
43992	EB102-EP15 Alarm number	The value indicates the most severe current alarm						43992	43992	43992						u16	1	0	0	0	R
43993	EB102-EP14-BT3 Return Temp.	Return temperature, BT3						43993	43993	43993		43993			°C	s16	10	0	0	0	R
43994	EB102-EP14-BT10 Brine In Temp	Brine in temperature, BT10						43994	43994	43994					°C	s16	10	0	0	0	R
43995	EB102-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						43995	43995	43995					°C	s16	10	0	0	0	R
43996	EB102-EP14-BT12 Condensor Out	Condensor temperature, BT12						43996	43996	43996		43996			°C	s16	10	0	0	0	R
43997	EB102-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						43997	43997	43997		43997			°C	s16	10	0	0	0	R
43998	EB102-EP14-BT15 Liquid Line	Liquid line temperature, BT15						43998	43998	43998		43998			°C	s16	10	0	0	0	R
43999	EB102-EP14-BT17 Suction	Suction temperature, BT17						43999	43999	43999		43999			°C	s16	10	0	0	0	R
44000	EB102-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						44000	44000	44000					°C	s16	10	0	0	0	R
44001	EB102-EP14-BP8 Pressure Transmitter							44001	44001	44001					°C	s16	10	0	0	0	R
44002	EB102-EP14 Compressor State	On/Off						44002	44002	44002						u8	1	0	0	0	R
44003	EB102-EP14 Compr. time to start							44003	44003	44003		44003				u8	1	0	0	0	R
44004	EB102-EP14 Relay status							44004	44004	44004						u16	1	0	0	0	R
44005	EB102-EP14 Heat med. pump status							44005	44005	44005					%	u8	1	0	0	0	R
44006	EB102-EP14 Brine pump status							44006	44006	44006					%	u8	1	0	0	0	R
44007	EB102-EP14 Compressor starts							44007	44007	44007		44007				u32	1	0	9999999	0	R
44009	EB102-EP14 Tot. op.time compr							44009	44009	44009		44009			h	u32	1	0	9999999	0	R
44011	EB102-EP14 Tot. HW op.time compr							44011	44011	44011		44011			h	u32	1	0	9999999	0	R
44013	EB102-EP14 Alarm number	The value indicates the most severe current alarm						44013	44013	44013		44013				u16	1	0	0	0	R
44014	EB101 Version							44014	44014	44014	44014	44014	44014	44014		u16	1	0	0	0	R
44032	EB101 Slave Type							44032	44032	44032	44032	44032	44032	44032		u8	1	0	0	0	R
44033	EB101 Compressor EP14 Size							44033	44033	44033	44033	44033	44033	44033	kW	u8	1	0	0	0	R
44034	EB101-EP15-BT3 Return Temp.	Return temperature, BT3						44034	44034	44034					°C	s16	10	0	0	0	R
44035	EB101-EP15-BT10 Brine In Temp	Brine in temperature, BT10						44035	44035	44035					°C	s16	10	0	0	0	R
44036	EB101-EP15-BT11 Brine Out Temp	Brine out temperature, BT11						44036	44036	44036					°C	s16	10	0	0	0	R
44037	EB101-EP15-BT12 Condensor Out	Condensor temperature, BT12						44037	44037	44037					°C	s16	10	0	0	0	R
44038	EB101-EP15-BT14 Hot Gas Temp	Hot gas temperature, BT14						44038	44038	44038					°C	s16	10	0	0	0	R
44039	EB101-EP15-BT15 Liquid Line	Liquid line temperature, BT15						44039	44039	44039					°C	s16	10	0	0	0	R
44040	EB101-EP15-BT17 Suction	Suction temperature, BT17						44040	44040	44040					°C	s16	10	0	0	0	R
44041	EB101-EP15-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						44041	44041	44041					°C	s16	10	0	0	0	R
44042	EB101-EP15-BP8 Pressure Transmitter							44042	44042	44042					°C	s16	10	0	0	0	R
44043	EB101-EP15 Compressor State	On/Off						44043	44043	44043						u8	1	0	0	0	R
44044	EB101-EP15 Compr. time to start							44044	44044	44044						u8	1	0	0	0	R
44045	EB101-EP15 Relay status							44045	44045	44045						u16	1	0	0	0	R
44046	EB101-EP15 Heat med. pump status							44046	44046	44046					%	u8	1	0	0	0	R
44047	EB101-EP15 Brine pump status							44047	44047	44047					%	u8	1	0	0	0	R
44048	EB101-EP15 Compressor starts							44048	44048	44048						u32	1	0	0	0	R
44050	EB101-EP15 Tot. op.time compr							44050	44050	44050					h	u32	1	0	0	0	R
44052	EB101-EP15 Tot. HW op.time compr							44052	44052	44052					h	u32	1	0	0	0	R
44054	EB101-EP15 Alarm number	The value indicates the most severe current alarm						44054	44054	44054						u16	1	0	0	0	R
44055	EB101-EP14-BT3 Return Temp.	Return temperature, BT3						44055	44055	44055	44055	44055	44055	44055	°C	s16	10	0	0	0	R
44056	EB101-EP14-BT10 Brine In Temp	Brine in temperature, BT10						44056	44056	44056					°C	s16	10	0	0	0	R
44057	EB101-EP14-BT11 Brine Out Temp	Brine out temperature, BT11						44057	44057	44057					°C	s16	10	0	0	0	R
44058	EB101-EP14-BT12 Condensor Out	Condensor temperature, BT12						44058	44058	44058	44058	44058	44058	44058	°C	s16	10	0	0	0	R
44059	EB101-EP14-BT14 Hot Gas Temp	Hot gas temperature, BT14						44059	44059	44059	44059	44059	44059	44059	°C	s16	10	0	0	0	R
44060	EB101-EP14-BT15 Liquid Line	Liquid line temperature, BT15						44060	44060	44060	44060	44060	44060	44060	°C	s16	10	0	0	0	R
44061	EB101-EP14-BT17 Suction	Suction temperature, BT17						44061	44061	44061	44061	44061	44061	44061	°C	s16	10	0	0	0	R
44062	EB101-EP14-BT29 Cpr. Oil. Temp.	Compressor oil temperature, BT29						44062	44062	44062					°C	s16	10	0	0	0	R
44063	EB101-EP14-BP8 Pressure Transmitter							44063	44063	44063					°C	s16	10	0	0	0	R
44064	EB101-EP14 Compressor State	On/Off						44064	44064	44064						u8	1	0	0	0	R
44065	EB101-EP14 Compr. time to start							44065	44065	44065	44065	44065	44065	44065		u8	1	0	0	0	R
44066	EB101-EP14 Relay status							44066	44066	44066						u16	1	0	0	0	R
44067	EB101-EP14 Heat med. pump status							44067	44067	44067					%	u8	1	0	0	0	R
44068	EB101-EP14 Brine pump status							44068	44068	44068					%	u8	1	0	0	0	R
44069	EB101-EP14 Compressor starts							44069	44069	44069	44069	44069	44069	44069		u32	1	0	9999999	0	R
44071	EB101-EP14 Tot. op.time compr							44071	44071	44071	44071	44071	44071	44071	h	u32	1	0	9999999	0	R
44073	EB101-EP14 Tot. HW op.time compr							44073	44073	44073	44073	44073	44073	44073	h	u32	1	0	9999999	0	R
44075	EB101-EP14 Alarm number	The value indicates the most severe current alarm						44075	44075	44075	44075	44075	44075	44075		u16	1	0	0	0	R
44116	EB100-EP15 Alarm Number	The value indicates the most severe current alarm							44116	44116						s16	1	0	0	0	R
44137	EB100-EP14 Alarm Number	The value indicates the most severe current alarm							44137	44137						s16	1	0	0	0	R
44138	EB108-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44138						u8	1	0	0	0	R
44139	EB108-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44139		44139		44139				u8	1	0	0	0	R
44151	EB107-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44151						u8	1	0	0	0	R
44152	EB107-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44152		44152		44152				u8	1	0	0	0	R
44164	EB106-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44164						u8	1	0	0	0	R
44165	EB106-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44165		44165		44165				u8	1	0	0	0	R
44177	EB105-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44177						u8	1	0	0	0	R
44178	EB105-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44178		44178		44178				u8	1	0	0	0	R
44190	EB104-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44190						u8	1	0	0	0	R
44191	EB104-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44191		44191		44191				u8	1	0	0	0	R
44203	EB103-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44203						u8	1	0	0	0	R
44204	EB103-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44204		44204		44204				u8	1	0	0	0	R
44216	EB102-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44216						u8	1	0	0	0	R
44217	EB102-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44217		44217		44217				u8	1	0	0	0	R
44229	EB101-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44229						u8	1	0	0	0	R
44230	EB101-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44230		44230		44230				u8	1	0	0	0	R
44242	EB100-EP15 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request								44242						u8	1	0	0	0	R
44243	EB100-EP14 Prio	Indicates what need is assigned to the compressor module, 0 = Off, 1 = Heat, 2 = Hot water, 3 = Pool 1, 4 = Pool2, 5=External Request						44243		44243		44243				u8	1	0	0	0	R
44256	Ext. Cooling Blocked											44256	44256	44256		u8	1	0	0	0	R
44258	External supply air accessory relays	Indicates the status of the relays on the external supply air accessory. The information is binary encoded. B0: relay K1 (QN40 close signal). B1: relay K2 (QN40 open signal)			44258											u8	1	0	0	0	R
44266	Cool Degree Minutes						44266	44266	44266	44266	44266	44266	44266	44266		s16	10	-30000	30000	0	R/W
44267	Calc. Cooling Supply S4	Calculated supply temperature in cooling mode for the climate system					44267	44267	44267	44267	44267	44267	44267	44267	°C	s16	10	0	0	0	R
44268	Calc. Cooling Supply S3	Calculated supply temperature in cooling mode for the climate system					44268	44268	44268	44268	44268	44268	44268	44268	°C	s16	10	0	0	0	R
44269	Calc. Cooling Supply S2	Calculated supply temperature in cooling mode for the climate system					44269	44269	44269	44269	44269	44269	44269	44269	°C	s16	10	0	0	0	R
44270	Calc. Cooling Supply S1	Calculated supply temperature in cooling mode for the climate system					44270	44270	44270	44270	44270	44270	44270	44270	°C	s16	10	0	0	0	R
44276	State ACS	The state of the ACS accessory					44276	44276	44276	44276						u8	1	0	0	0	R
44277	EQ1-QN25 State ACS Heat Dump	10=shunt off,20=shunt open,30=shunt closed					44277	44277	44277	44277						u8	1	0	0	0	R
44278	EQ1-QN18 State ACS Cool Dump	10=shunt off,20=shunt open,30=shunt closed					44278	44278	44278	44278						u8	1	0	0	0	R
44282	Used cprs. HW	The number of compressors that's currently producing hot water				44282		44282	44282	44282		44282				u8	1	0	0	0	R
44283	Used cprs. heat	The number of compressors that's currently producing heating				44283		44283	44283	44283		44283				u8	1	0	0	0	R
44284	Used cprs. pool 1	The number of compressors that's currently producing poolheating for pool 1						44284	44284	44284		44284				u8	1	0	0	0	R
44285	Used cprs. pool 2	The number of compressors that's currently producing poolheating for pool 2						44285	44285	44285		44285				u8	1	0	0	0	R
44298	Heat Meter - HW Cpr and Add EP14	Accumulated energy production as calculated by the heat meter	44298	44298	44298	44298	44298	44298	44298	44298			44298	44298	kWh	u32	10	0	0	0	R
44300	Heat Meter - Heat Cpr and Add EP14	Accumulated energy production as calculated by the heat meter	44300	44300	44300	44300	44300	44300	44300	44300			44300	44300	kWh	u32	10	0	0	0	R
44302	Heat Meter - Cooling Cpr EP14	Accumulated energy production as calculated by the heat meter					44302	44302	44302	44302			44302	44302	kWh	u32	10	0	0	0	R
44304	Heat Meter - Pool Cpr EP14	Accumulated energy production as calculated by the heat meter			44304	44304	44304	44304	44304	44304			44304	44304	kWh	u32	10	0	0	0	R
44306	Heat Meter - HW Cpr EP14	Accumulated energy production as calculated by the heat meter			44306	44306	44306	44306	44306	44306			44306	44306	kWh	u32	10	0	0	0	R
44308	Heat Meter - Heat Cpr EP14	Accumulated energy production as calculated by the heat meter			44308	44308	44308	44308	44308	44308			44308	44308	kWh	u32	10	0	0	0	R
44317	SCA accessory relays	Indicates the status of the relays on the SCA accessory. The information is binary encoded. B0: relay K1 (Solar pump). B1: relay K2 (Solar Cooling Pump) B2: relay K3 (QN28)			44317											u8	1	0	0	0	R
44320	Used cprs. cool	The number of compressors that's currently producing active cooling						44320	44320	44320		44320				u8	1	0	0	0	R
44322	Speed ext cooling pump GP12												44322	44322	%	u8	1	0	0	0	R
44323	Cooling pump manual speed	Cooling pump speed if manual											44323	44323	%	s8	1	1	100	70	R/W
44331	Software release		44331	44331	44331	44331	44331	44331	44331	44331	44331	44331	44331	44331		u8	1	0	0	0	R
44334	EB108-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44334			°C	s16	10	0	0	0	R
44335	EB108-EP14-BT16 Evaporator	Evaporator temperature, BT16										44335			°C	s16	10	0	0	0	R
44338	EB107-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44338			°C	s16	10	0	0	0	R
44339	EB107-EP14-BT16 Evaporator	Evaporator temperature, BT16										44339			°C	s16	10	0	0	0	R
44342	EB106-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44342			°C	s16	10	0	0	0	R
44343	EB106-EP14-BT16 Evaporator	Evaporator temperature, BT16										44343			°C	s16	10	0	0	0	R
44346	EB105-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44346			°C	s16	10	0	0	0	R
44347	EB105-EP14-BT16 Evaporator	Evaporator temperature, BT16										44347			°C	s16	10	0	0	0	R
44350	EB104-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44350			°C	s16	10	0	0	0	R
44351	EB104-EP14-BT16 Evaporator	Evaporator temperature, BT16										44351			°C	s16	10	0	0	0	R
44354	EB103-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44354			°C	s16	10	0	0	0	R
44355	EB103-EP14-BT16 Evaporator	Evaporator temperature, BT16										44355			°C	s16	10	0	0	0	R
44358	EB102-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28										44358			°C	s16	10	0	0	0	R
44359	EB102-EP14-BT16 Evaporator	Evaporator temperature, BT16										44359			°C	s16	10	0	0	0	R
44362	EB101-EP14-BT28 Outdoor Temp	Current outdoor temperature, BT28									44362	44362	44362	44362	°C	s16	10	0	0	0	R
44363	EB101-EP14-BT16 Evaporator	Evaporator temperature, BT16									44363	44363	44363	44363	°C	s16	10	0	0	0	R
44379	Ext. Addition Pump	On/Off												44379		u8	1	0	0	0	R
44380	Docked External Compressors	Number of compressors with external control						44380	44380	44380						u8	1	0	0	0	R
44389	EB108 Speed charge pump											44389			%	u8	1	0	0	0	R
44390	EB107 Speed charge pump											44390			%	u8	1	0	0	0	R
44391	EB106 Speed charge pump											44391			%	u8	1	0	0	0	R
44392	EB105 Speed charge pump											44392			%	u8	1	0	0	0	R
44393	EB104 Speed charge pump											44393			%	u8	1	0	0	0	R
44394	EB103 Speed charge pump											44394			%	u8	1	0	0	0	R
44395	EB102 Speed charge pump											44395			%	u8	1	0	0	0	R
44396	EB101 Speed charge pump										44396	44396	44396	44396	%	u8	1	0	0	0	R
44410	EB108 Bit Register							44410	44410	44410						u8	1	0	0	0	R
44411	EB108-BT6 Hot water load temp.							44411	44411	44411					°C	s16	10	0	0	0	R
44412	EB108-BT7 Hot water top temp.							44412	44412	44412					°C	s16	10	0	0	0	R
44413	EB108-BT2 Supply temp.							44413	44413	44413					°C	s16	10	0	0	0	R
44414	EB108-EP15 Compressor State	On/Off								44414						u8	1	0	0	0	R
44415	EB108-EP14 Compressor State	On/Off								44415		44415				u8	1	0	0	0	R
44416	EB107 Bit Register							44416	44416	44416						u8	1	0	0	0	R
44417	EB107-BT6 Hot water load temp.							44417	44417	44417					°C	s16	10	0	0	0	R
44418	EB107-BT7 Hot water top temp.							44418	44418	44418					°C	s16	10	0	0	0	R
44419	EB107-BT2 Supply temp.							44419	44419	44419					°C	s16	10	0	0	0	R
44420	EB107-EP15 Compressor State	On/Off								44420						u8	1	0	0	0	R
44421	EB107-EP14 Compressor State	On/Off						44421	44421	44421		44421				u8	1	0	0	0	R
44422	EB106 Bit Register							44422	44422	44422						u8	1	0	0	0	R
44423	EB106-BT6 Hot water load temp.							44423	44423	44423					°C	s16	10	0	0	0	R
44424	EB106-BT7 Hot water top temp.							44424	44424	44424					°C	s16	10	0	0	0	R
44425	EB106-BT2 Supply temp.							44425	44425	44425					°C	s16	10	0	0	0	R
44426	EB106-EP15 Compressor State	On/Off								44426						u8	1	0	0	0	R
44427	EB106-EP14 Compressor State	On/Off								44427		44427				u8	1	0	0	0	R
44428	EB105 Bit Register							44428	44428	44428						u8	1	0	0	0	R
44429	EB105-BT6 Hot water load temp.							44429	44429	44429					°C	s16	10	0	0	0	R
44430	EB105-BT7 Hot water top temp.							44430	44430	44430					°C	s16	10	0	0	0	R
44431	EB105-BT2 Supply temp.							44431	44431	44431					°C	s16	10	0	0	0	R
44432	EB105-EP15 Compressor State	On/Off								44432						u8	1	0	0	0	R
44433	EB105-EP14 Compressor State	On/Off								44433		44433				u8	1	0	0	0	R
44434	EB104 Bit Register							44434	44434	44434						u8	1	0	0	0	R
44435	EB104-BT6 Hot water load temp.							44435	44435	44435					°C	s16	10	0	0	0	R
44436	EB104-BT7 Hot water top temp.							44436	44436	44436					°C	s16	10	0	0	0	R
44437	EB104-BT2 Supply temp.							44437	44437	44437					°C	s16	10	0	0	0	R
44438	EB104-EP15 Compressor State	On/Off								44438						u8	1	0	0	0	R
44439	EB104-EP14 Compressor State	On/Off								44439		44439				u8	1	0	0	0	R
44440	EB103 Bit Register							44440	44440	44440						u8	1	0	0	0	R
44441	EB103-BT6 Hot water load temp.							44441	44441	44441					°C	s16	10	0	0	0	R
44442	EB103-BT7 Hot water top temp.							44442	44442	44442					°C	s16	10	0	0	0	R
44443	EB103-BT2 Supply temp.							44443	44443	44443					°C	s16	10	0	0	0	R
44444	EB103-EP15 Compressor State	On/Off								44444						u8	1	0	0	0	R
44445	EB103-EP14 Compressor State	On/Off								44445		44445				u8	1	0	0	0	R
44446	EB102 Bit Register							44446	44446	44446						u8	1	0	0	0	R
44447	EB102-BT6 Hot water load temp.							44447	44447	44447					°C	s16	10	0	0	0	R
44448	EB102-BT7 Hot water top temp.							44448	44448	44448					°C	s16	10	0	0	0	R
44449	EB102-BT2 Supply temp.							44449	44449	44449					°C	s16	10	0	0	0	R
44450	EB102-EP15 Compressor State	On/Off								44450						u8	1	0	0	0	R
44451	EB102-EP14 Compressor State	On/Off								44451		44451				u8	1	0	0	0	R
44452	EB101 Bit Register							44452	44452	44452						u8	1	0	0	0	R
44453	EB101-BT6 Hot water load temp.							44453	44453	44453					°C	s16	10	0	0	0	R
44454	EB101-BT7 Hot water top temp.							44454	44454	44454					°C	s16	10	0	0	0	R
44455	EB101-BT2 Supply temp.							44455	44455	44455					°C	s16	10	0	0	0	R
44456	EB101-EP15 Compressor State	On/Off								44456						u8	1	0	0	0	R
44457	EB101-EP14 Compressor State	On/Off								44457	44457	44457	44457	44457		u8	1	0	0	0	R
44483	State of the extra additional heat in series	0 = Off, 1 = On									44483	44483	44483	44483		u8	1	0	0	0	R
44487	Docked Cool Compressors	Number of compressors docked to cooling						44487	44487	44487	44487	44487	44487	44487		u8	1	0	0	0	R
44503	EB108-EP14 High Pressure Sensor Outdoor Unit											44503			bar	s16	10	0	0	0	R
44504	EB108-EP14 Low Pressure Sensor Outdoor Unit											44504			bar	s16	10	0	0	0	R
44505	EB108-EP14 Actual Cpr Frequency Outdoor Unit											44505			Hz	s16	10	0	0	0	R
44506	EB108-EP14 Protection Status Register Outdoor Unit											44506				u16	1	0	0	0	R
44507	EB108-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44507				u8	1	0	0	0	R
44510	EB108-EP14 Calculated Power Outdoor Unit											44510			kW	u8	1	0	0	0	R
44531	EB107-EP14 High Pressure Sensor Outdoor Unit											44531			bar	s16	10	0	0	0	R
44532	EB107-EP14 Low Pressure Sensor Outdoor Unit											44532			bar	s16	10	0	0	0	R
44533	EB107-EP14 Actual Cpr Frequency Outdoor Unit											44533			Hz	s16	10	0	0	0	R
44534	EB107-EP14 Protection Status Register Outdoor Unit											44534				u16	1	0	0	0	R
44535	EB107-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44535				u8	1	0	0	0	R
44538	EB107-EP14 Calculated Power Outdoor Unit											44538			kW	u8	1	0	0	0	R
44559	EB106-EP14 High Pressure Sensor Outdoor Unit											44559			bar	s16	10	0	0	0	R
44560	EB106-EP14 Low Pressure Sensor Outdoor Unit											44560			bar	s16	10	0	0	0	R
44561	EB106-EP14 Actual Cpr Frequency Outdoor Unit											44561			Hz	s16	10	0	0	0	R
44562	EB106-EP14 Protection Status Register Outdoor Unit											44562				u16	1	0	0	0	R
44563	EB106-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44563				u8	1	0	0	0	R
44566	EB106-EP14 Calculated Power Outdoor Unit											44566			kW	u8	1	0	0	0	R
44587	EB105-EP14 High Pressure Sensor Outdoor Unit											44587			bar	s16	10	0	0	0	R
44588	EB105-EP14 Low Pressure Sensor Outdoor Unit											44588			bar	s16	10	0	0	0	R
44589	EB105-EP14 Actual Cpr Frequency Outdoor Unit											44589			Hz	s16	10	0	0	0	R
44590	EB105-EP14 Protection Status Register Outdoor Unit											44590				u16	1	0	0	0	R
44591	EB105-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44591				u8	1	0	0	0	R
44594	EB105-EP14 Calculated Power Outdoor Unit											44594			kW	u8	1	0	0	0	R
44615	EB104-EP14 High Pressure Sensor Outdoor Unit											44615			bar	s16	10	0	0	0	R
44616	EB104-EP14 Low Pressure Sensor Outdoor Unit											44616			bar	s16	10	0	0	0	R
44617	EB104-EP14 Actual Cpr Frequency Outdoor Unit											44617			Hz	s16	10	0	0	0	R
44618	EB104-EP14 Protection Status Register Outdoor Unit											44618				u16	1	0	0	0	R
44619	EB104-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44619				u8	1	0	0	0	R
44622	EB104-EP14 Calculated Power Outdoor Unit											44622			kW	u8	1	0	0	0	R
44643	EB103-EP14 High Pressure Sensor Outdoor Unit											44643			bar	s16	10	0	0	0	R
44644	EB103-EP14 Low Pressure Sensor Outdoor Unit											44644			bar	s16	10	0	0	0	R
44645	EB103-EP14 Actual Cpr Frequency Outdoor Unit											44645			Hz	s16	10	0	0	0	R
44646	EB103-EP14 Protection Status Register Outdoor Unit											44646				u16	1	0	0	0	R
44647	EB103-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44647				u8	1	0	0	0	R
44650	EB103-EP14 Calculated Power Outdoor Unit											44650			kW	u8	1	0	0	0	R
44671	EB102-EP14 High Pressure Sensor Outdoor Unit											44671			bar	s16	10	0	0	0	R
44672	EB102-EP14 Low Pressure Sensor Outdoor Unit											44672			bar	s16	10	0	0	0	R
44673	EB102-EP14 Actual Cpr Frequency Outdoor Unit											44673			Hz	s16	10	0	0	0	R
44674	EB102-EP14 Protection Status Register Outdoor Unit											44674				u16	1	0	0	0	R
44675	EB102-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive										44675				u8	1	0	0	0	R
44678	EB102-EP14 Calculated Power Outdoor Unit											44678			kW	u8	1	0	0	0	R
44699	EB101-EP14 High Pressure Sensor Outdoor Unit										44699	44699	44699	44699	bar	s16	10	0	0	0	R
44700	EB101-EP14 Low Pressure Sensor Outdoor Unit										44700	44700	44700	44700	bar	s16	10	0	0	0	R
44701	EB101-EP14 Actual Cpr Frequency Outdoor Unit										44701	44701	44701	44701	Hz	s16	10	0	0	0	R
44702	EB101-EP14 Protection Status Register Outdoor Unit										44702	44702	44702	44702		u16	1	0	0	0	R
44703	EB101-EP14 Defrosting Outdoor Unit	0=No, 1=Active, 2 = Passive									44703	44703	44703	44703		u8	1	0	0	0	R
44706	EB101-EP14 Calculated Power Outdoor Unit										44706	44706	44706	44706	kW	u8	1	0	0	0	R
44742	HW valve QN35													44742		u8	1	0	0	0	R
44743	Internal charge pump												44743	44743		u8	1	0	0	0	R
44744	Extra heating system pump S4		44744	44744	44744	44744	44744	44744	44744	44744		44744	44744	44744		u8	1	0	0	0	R
44745	Extra heating system pump S3		44745	44745	44745	44745	44745	44745	44745	44745		44745	44745	44745		u8	1	0	0	0	R
44746	Extra heating system pump S2		44746	44746	44746	44746	44746	44746	44746	44746		44746	44746	44746		u8	1	0	0	0	R
44748	Pool 2 Pump Status	1=on,0=off					44748	44748	44748	44748		44748				u8	1	0	0	0	R
44749	Pool 1 Pump Status	1=on,0=off					44749	44749	44749	44749		44749	44749	44749		u8	1	0	0	0	R
44750	FJVM pump		44750	44750												u8	1	0	0	0	R
44751	EQ1-QN12 ACS Valve	ACS valve is 1=open,0=closed					44751	44751	44751	44751						u8	1	0	0	0	R
44752	EQ1-GP20 ACS Dump Signal	GP20 is 1=running,0=off					44752	44752	44752	44752						u8	1	0	0	0	R
44753	Passive Cool Shunt						44753	44753	44753	44753						u8	1	0	0	0	R
44754	GP13 Passive Cool Pool						44754	44754	44754	44754						u8	1	0	0	0	R
44755	DEW hot water valve				44755											u8	1	0	0	0	R
44756	State ground water pump						44756	44756	44756	44756						u8	1	0	0	0	R
44757	SCA hot water valve				44757											u8	1	0	0	0	R
44761	EB108-EP14 calc. ou compressor freq	Calculated compressor frequency										44761			Hz	u8	1	0	0	0	R
44763	EB107-EP14 calc. ou compressor freq	Calculated compressor frequency										44763			Hz	u8	1	0	0	0	R
44765	EB106-EP14 calc. ou compressor freq	Calculated compressor frequency										44765			Hz	u8	1	0	0	0	R
44767	EB105-EP14 calc. ou compressor freq	Calculated compressor frequency										44767			Hz	u8	1	0	0	0	R
44769	EB104-EP14 calc. ou compressor freq	Calculated compressor frequency										44769			Hz	u8	1	0	0	0	R
44771	EB103-EP14 calc. ou compressor freq	Calculated compressor frequency										44771			Hz	u8	1	0	0	0	R
44773	EB102-EP14 calc. ou compressor freq	Calculated compressor frequency										44773			Hz	u8	1	0	0	0	R
44775	EB101-EP14 calc. ou compressor freq	Calculated compressor frequency									44775	44775	44775	44775	Hz	u8	1	0	0	0	R
44778	EP10-QN41 State Brine Shunt	10=shunt off,20=shunt open,30=shunt closed							44778	44778						u8	1	0	0	0	R
44824	EB108-EP14 Current Sensor											44824				s16	10	0	0	0	R
44825	EB108-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44825				u8	1	0	0	0	R
44830	EB107-EP14 Current Sensor											44830				s16	10	0	0	0	R
44831	EB107-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44831				u8	1	0	0	0	R
44836	EB106-EP14 Current Sensor											44836				s16	10	0	0	0	R
44837	EB106-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44837				u8	1	0	0	0	R
44842	EB105-EP14 Current Sensor											44842				s16	10	0	0	0	R
44843	EB105-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44843				u8	1	0	0	0	R
44848	EB104-EP14 Current Sensor											44848				s16	10	0	0	0	R
44849	EB104-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44849				u8	1	0	0	0	R
44854	EB103-EP14 Current Sensor											44854				s16	10	0	0	0	R
44855	EB103-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44855				u8	1	0	0	0	R
44860	EB102-EP14 Current Sensor											44860				s16	10	0	0	0	R
44861	EB102-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes										44861				u8	1	0	0	0	R
44866	EB101-EP14 Current Sensor										44866	44866	44866	44866		s16	10	0	0	0	R
44867	EB101-EP14 Hz Down Mode Outdoor Unit	0=No, 1=Yes									44867	44867	44867	44867		u8	1	0	0	0	R
44874	State SG Ready		44874	44874	44874	44874	44874	44874	44874	44874	44874	44874	44874	44874		u8	1	0	0	0	R
44878	SG Ready input A		44878	44878	44878	44878	44878	44878	44878	44878	44878	44878	44878	44878		u8	1	0	0	0	R
44879	SG Ready input B		44879	44879	44879	44879	44879	44879	44879	44879	44879	44879	44879	44879		u8	1	0	0	0	R
44896	Smart Price Adaption Heating Offset		44896	44896	44896	44896	44896	44896	44896	44896	44896	44896	44896	44896		s8	10	0	0	0	R
44897	Smart Price Adaption HW Comfort Mode	0=Eco,1=Normal,2=Luxury,10=Normal+,20=Mini	44897	44897	44897	44897	44897	44897	44897	44897	44897	44897	44897	44897		s8	1	0	0	0	R
44898	Smart Price Adaption Pool Offset		44898	44898	44898	44898	44898	44898	44898	44898	44898	44898	44898	44898		s8	1	0	0	0	R
44899	Smart Price Adaption Cool Offset		44899	44899	44899	44899	44899	44899	44899	44899	44899	44899	44899	44899		s8	1	0	0	0	R
44908	State smart price adaption		44908	44908	44908	44908	44908	44908	44908	44908	44908	44908	44908	44908		u8	1	0	0	0	R
44910	Brine Pump dT Actual	Current value between set and act value on brine pumps					44910	44910	44910	44910						s16	10	0	0	0	R
44911	Brine Pump dT Set Point	Set point delta T for the brine pumps					44911	44911	44911	44911						s16	10	0	0	0	R
44935	EB108-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44935			°C	s16	10	0	0	0	R
44936	EB108-EP14 Inverter Temperature	Inverter temperature										44936			°C	s16	10	0	0	0	R
44937	EB108-EP14-Fan Speed Step											44937				u8	1	0	0	0	R
44941	EB107-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44941			°C	s16	10	0	0	0	R
44942	EB107-EP14 Inverter Temperature	Inverter temperature										44942			°C	s16	10	0	0	0	R
44943	EB107-EP14-Fan Speed Step											44943				u8	1	0	0	0	R
44947	EB106-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44947			°C	s16	10	0	0	0	R
44948	EB106-EP14 Inverter Temperature	Inverter temperature										44948			°C	s16	10	0	0	0	R
44949	EB106-EP14-Fan Speed Step											44949				u8	1	0	0	0	R
44953	EB105-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44953			°C	s16	10	0	0	0	R
44954	EB105-EP14 Inverter Temperature	Inverter temperature										44954			°C	s16	10	0	0	0	R
44955	EB105-EP14-Fan Speed Step											44955				u8	1	0	0	0	R
44959	EB104-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44959			°C	s16	10	0	0	0	R
44960	EB104-EP14 Inverter Temperature	Inverter temperature										44960			°C	s16	10	0	0	0	R
44961	EB104-EP14-Fan Speed Step											44961				u8	1	0	0	0	R
44965	EB103-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44965			°C	s16	10	0	0	0	R
44966	EB103-EP14 Inverter Temperature	Inverter temperature										44966			°C	s16	10	0	0	0	R
44967	EB103-EP14-Fan Speed Step											44967				u8	1	0	0	0	R
44971	EB102-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16										44971			°C	s16	10	0	0	0	R
44972	EB102-EP14 Inverter Temperature	Inverter temperature										44972			°C	s16	10	0	0	0	R
44973	EB102-EP14-Fan Speed Step											44973				u8	1	0	0	0	R
44977	EB101-EP14-BT16 Evaporator 2	Evaporator 2 temperature, BT16									44977	44977	44977	44977	°C	s16	10	0	0	0	R
44978	EB101-EP14 Inverter Temperature	Inverter temperature									44978	44978	44978	44978	°C	s16	10	0	0	0	R
44979	EB101-EP14-Fan Speed Step										44979	44979	44979	44979		u8	1	0	0	0	R
45001	Alarm	Indicates the alarm number of the most severe current alarm	45001	45001	45001	45001	45001	45001	45001	45001	45001	45001	45001	45001		s16	1	0	0	0	R
45171	Alarm Reset	Reset alarm by setting value 1	45171	45171	45171	45171	45171	45171	45171	45171	45171	45171	45171	45171		u8	1	0	0	0	R/W
47004	Heat Curve S4	Heat curve, see manual for more information	47004	47004	47004	47004	47004	47004	47004	47004		47004	47004	47004		s8	1	0	15	9	R/W
47005	Heat Curve S3	Heat curve, see manual for more information	47005	47005	47005	47005	47005	47005	47005	47005		47005	47005	47005		s8	1	0	15	9	R/W
47006	Heat Curve S2	Heat curve, see manual for more information	47006	47006	47006	47006	47006	47006	47006	47006		47006	47006	47006		s8	1	0	15	9	R/W
47007	Heat Curve S1	Heat curve, see manual for more information	47007	47007	47007	47007	47007	47007	47007	47007	47007	47007	47007	47007		s8	1	0	15	9	R/W
47008	Heat Offset S4	Offset of the heat curve, see manual for more information	47008	47008	47008	47008	47008	47008	47008	47008		47008	47008	47008		s8	1	-10	10	0	R/W
47009	Heat Offset S3	Offset of the heat curve, see manual for more information	47009	47009	47009	47009	47009	47009	47009	47009		47009	47009	47009		s8	1	-10	10	0	R/W
47010	Heat Offset S2	Offset of the heat curve, see manual for more information	47010	47010	47010	47010	47010	47010	47010	47010		47010	47010	47010		s8	1	-10	10	0	R/W
47011	Heat Offset S1	Offset of the heat curve, see manual for more information	47011	47011	47011	47011	47011	47011	47011	47011	47011	47011	47011	47011		s8	1	-10	10	0	R/W
47012	Min Supply System 4		47012	47012	47012	47012	47012	47012	47012	47012		47012	47012	47012	°C	s16	10	50	700	200	R/W
47013	Min Supply System 3		47013	47013	47013	47013	47013	47013	47013	47013		47013	47013	47013	°C	s16	10	50	700	200	R/W
47014	Min Supply System 2		47014	47014	47014	47014	47014	47014	47014	47014		47014	47014	47014	°C	s16	10	50	700	200	R/W
47015	Min Supply System 1		47015	47015	47015	47015	47015	47015	47015	47015	47015	47015	47015	47015	°C	s16	10	50	700	200	R/W
47016	Max Supply System 4		47016	47016	47016	47016	47016	47016	47016	47016		47016	47016	47016	°C	s16	10	50	800	600	R/W
47017	Max Supply System 3		47017	47017	47017	47017	47017	47017	47017	47017		47017	47017	47017	°C	s16	10	50	800	600	R/W
47018	Max Supply System 2		47018	47018	47018	47018	47018	47018	47018	47018		47018	47018	47018	°C	s16	10	50	800	600	R/W
47019	Max Supply System 1		47019	47019	47019	47019	47019	47019	47019	47019	47019	47019	47019	47019	°C	s16	10	50	800	600	R/W
47020	Own Heating Curve P7	User defined heating curve point	47020	47020	47020	47020	47020	47020	47020	47020		47020	47020	47020	°C	s8	1	5	80	15	R/W
47021	Own Heating Curve P6	User defined heating curve point	47021	47021	47021	47021	47021	47021	47021	47021		47021	47021	47021	°C	s8	1	5	80	15	R/W
47022	Own Heating Curve P5	User defined heating curve point	47022	47022	47022	47022	47022	47022	47022	47022		47022	47022	47022	°C	s8	1	5	80	26	R/W
47023	Own Heating Curve P4	User defined heating curve point	47023	47023	47023	47023	47023	47023	47023	47023		47023	47023	47023	°C	s8	1	5	80	32	R/W
47024	Own Heating Curve P3	User defined heating curve point	47024	47024	47024	47024	47024	47024	47024	47024		47024	47024	47024	°C	s8	1	5	80	35	R/W
47025	Own Heating Curve P2	User defined heating curve point	47025	47025	47025	47025	47025	47025	47025	47025		47025	47025	47025	°C	s8	1	5	80	40	R/W
47026	Own Heating Curve P1	User defined heating curve point	47026	47026	47026	47026	47026	47026	47026	47026	47026	47026	47026	47026	°C	s8	1	5	80	45	R/W
47027	Point offset outdoor temp.	Outdoor temperature point where the heat curve is offset	47027	47027	47027	47027	47027	47027	47027	47027	47027	47027	47027	47027	°C	s8	1	-40	30	0	R/W
47028	Point offset	Amount of offset at the point offset temperature	47028	47028	47028	47028	47028	47028	47028	47028	47028	47028	47028	47028	°C	s8	1	-10	10	0	R/W
47029	External adjustment S4	Change of the offset of the heat curve when closing the external adjustment input	47029	47029	47029	47029	47029	47029	47029	47029		47029	47029	47029		s8	1	-10	10	0	R/W
47030	External adjustment S3	Change of the offset of the heat curve when closing the external adjustment input	47030	47030	47030	47030	47030	47030	47030	47030		47030	47030	47030		s8	1	-10	10	0	R/W
47031	External adjustment S2	Change of the offset of the heat curve when closing the external adjustment input	47031	47031	47031	47031	47031	47031	47031	47031		47031	47031	47031		s8	1	-10	10	0	R/W
47032	External adjustment S1	Change of the offset of the heat curve when closing the external adjustment input	47032	47032	47032	47032	47032	47032	47032	47032	47032	47032	47032	47032		s8	1	-10	10	0	R/W
47033	External adjustment with room sensor S4	Room temperature setting when closing the external adjustment input	47033	47033	47033	47033	47033	47033	47033	47033		47033	47033	47033	°C	s16	10	50	300	200	R/W
47034	External adjustment with room sensor S3	Room temperature setting when closing the external adjustment input	47034	47034	47034	47034	47034	47034	47034	47034		47034	47034	47034	°C	s16	10	50	300	200	R/W
47035	External adjustment with room sensor S2	Room temperature setting when closing the external adjustment input	47035	47035	47035	47035	47035	47035	47035	47035		47035	47035	47035	°C	s16	10	50	300	200	R/W
47036	External adjustment with room sensor S1	Room temperature setting when closing the external adjustment input	47036	47036	47036	47036	47036	47036	47036	47036	47036	47036	47036	47036	°C	s16	10	50	300	200	R/W
47041	Hot water comfort mode	Setting in menu 2.2. 0=Economy,1=Normal,2=Luxury,4=Smart Control 0=Economy 1=Normal 2=Luxury	47041	47041	47041	47041	47041	47041	47041	47041	47041	47041	47041	47041		s8	1	0	4	1	R/W
47043	Start temperature HW Luxury	Start temperature for heating water	47043	47043	47043	47043	47043	47043	47043	47043	47043	47043	47043	47043	°C	s16	10	50	700	520	R/W
47044	Start temperature HW Normal	Start temperature for heating water	47044	47044	47044	47044	47044	47044	47044	47044	47044	47044	47044	47044	°C	s16	10	50	700	490	R/W
47045	Start temperature HW Economy	Start temperature for heating water	47045	47045	47045	47045	47045	47045	47045	47045	47045	47045	47045	47045	°C	s16	10	50	700	450	R/W
47046	Stop temperature Periodic HW	Temperature where hot water generation will stop	47046	47046	47046	47046	47046	47046	47046	47046	47046	47046	47046	47046	°C	s16	10	550	700	550	R/W
47047	Stop temperature HW Luxury	Temperature where hot water generation will stop	47047	47047	47047	47047	47047	47047	47047	47047	47047	47047	47047	47047	°C	s16	10	50	700	580	R/W
47048	Stop temperature HW Normal	Temperature where hot water generation will stop	47048	47048	47048	47048	47048	47048	47048	47048	47048	47048	47048	47048	°C	s16	10	50	700	550	R/W
47049	Stop temperature HW Economy	Temperature where hot water generation will stop	47049	47049	47049	47049	47049	47049	47049	47049	47049	47049	47049	47049	°C	s16	10	50	700	510	R/W
47050	Periodic HW	Activates the periodic hot water generation	47050	47050	47050	47050	47050	47050	47050	47050	47050	47050	47050			s8	1	0	1	1	R/W
47051	Periodic HW Interval	Interval between Periodic hot water sessions	47051	47051	47051	47051	47051	47051	47051	47051	47051	47051	47051		days	s8	1	1	90	14	R/W
47054	Run time HWC	Run time for the hot water circulation system	47054	47054	47054	47054	47054	47054	47054	47054	47054	47054	47054	47054	min	s8	1	1	60	60	R/W
47055	Still time HWC	Still time for the hot water circulation system	47055	47055	47055	47055	47055	47055	47055	47055	47055	47055	47055	47055	min	s8	1	0	60	0	R/W
47062	HW charge offset	Offset of HW charge temperature from the stop temperature			47062										°C	s8	10	0	0	0	R/W
47092	Manual compfreq HW	Should the compressor frequency be manual set in HW?			47092											u8	1	0	0	0	R/W
47093	Manual compfreq speed HW	Manual compressor frequency in HW?			47093										Hz	u16	1	0	0	0	R/W
47094	Sec per compfreq step	Time between changes of the copmpressor frequency			47094										s	u8	1	0	0	0	R/W
47095	Max compfreq step	Largest allowed change of compressor frequency in normal run			47095										Hz	u8	1	0	0	0	R/W
47096	Manual compfreq Heating	Should the compressor frequency be manual set in Heating?			47096											u8	1	0	0	0	R/W
47097	Min speed after start	Time with minimum compressor frequency when heating demand occurs			47097										Min	u8	1	0	0	0	R/W
47098	Min speed after HW	Should the compressor frequency be manual set in HW?			47098										Min	u8	1	0	0	0	R/W
47099	GMz	Compressor frequency regulator GMz			47099		47099									u8	1	0	0	0	R/W
47100	Max diff VBF-BerVBF	Largest allowed difference between Supply and calc supply			47100	47100	47100		47100						°C	u8	10	0	0	0	R/W
47101	Comp freq reg P	Compressor frequency regulator P			47101	47101	47101		47101							u8	1	0	0	0	R/W
47102	Comp freq max delta F	Maximum change of copmpressor frequency in compressor frequency regulator			47102	47102	47102		47102						Hz	s8	1	0	0	0	R/W
47103	Min comp freq	Minimum allowed compressor frequency			47103	47103	47103		47103						Hz	s16	1	0	0	0	R/W
47104	Max comp freq	Maximum allowed compressor frequency			47104	47104	47104		47104						Hz	s16	1	0	0	0	R/W
47105	Comp freq heating	Compressor frequency used in heating mode			47105										Hz	s16	1	0	0	0	R/W
47131	Language	Display language in the heat pump 0=English 1=Svenska 2=Deutsch 3=Francais 4=Espanol 5=Suomi 6=Lietuviu 7=Cesky 8=Polski 9=Nederlands 10=Norsk 11=Dansk 12=Eesti 13=Latviesu 16=Magyar	47131	47131	47131	47131	47131	47131	47131	47131	47131	47131	47131	47131		s8	1	0	21	0	R/W
47134	Period HW				47134	47134	47134	47134	47134	47134	47134	47134	47134	47134	min	u8	1	0	180	60	R/W
47135	Period Heat				47135	47135	47135	47135	47135	47135	47135	47135	47135	47135	min	u8	1	0	180	0	R/W
47136	Period Pool						47136	47136	47136	47136		47136	47136	47136	min	u8	1	0	180	0	R/W
47137	Operational mode	The operational mode of the heat pump 0=Auto 1=Manual 2=Add. heat only	47137	47137	47137	47137	47137	47137	47137	47137	47137	47137	47137	47137		u8	1	0	2	0	R/W
47138	Operational mode heat medium pump	 10=Intermittent 20=Continous 30=Economy 40=Auto	47138	47138	47138	47138	47138	47138	47138	47138	47138	47138	47138	47138		u8	1	10	40	40	R/W
47139	Operational mode brine medium pump	 10=Intermittent 20=Continuous 30=Economy 40=Auto					47139	47139	47139	47139						u8	1	10	30	10	R/W
47206	DM start heating	The value the degree minutes needed to be reached for the pump to start heating			47206	47206	47206	47206	47206	47206	47206	47206	47206	47206		s16	1	-1000	-30	-60	R/W
47209	DM between add. steps	The number of degree minutes between start of each electric addition step			47209	47209	47209	47209	47209	47209	47209	47209	47209	47209		s16	1	0	0	0	R/W
47210	DM start add. with shunt				47210		47210	47210	47210	47210		47210	47210			s16	1	-2000	-30	-400	R/W
47212	Max int add. power		47212	47212	47212	47212	47212	47212					47212	47212	kW	s16	100	0	4500	600	R/W
47214	Fuse	Size of the fuse that the HP is connected to	47214	47214	47214	47214	47214	47214	47214	47214	47214	47214	47214	47214	A	u16	1	1	400	16	R/W
47261	Exhaust Fan speed 4		47261	47261	47261	47261	47261	47261	47261	47261					%	u8	1	0	100	100	R/W
47262	Exhaust Fan speed 3		47262	47262	47262	47262	47262	47262	47262	47262					%	u8	1	0	100	80	R/W
47263	Exhaust Fan speed 2		47263	47263	47263	47263	47263	47263	47263	47263					%	u8	1	0	100	30	R/W
47264	Exhaust Fan speed 1		47264	47264	47264	47264	47264	47264	47264	47264					%	u8	1	0	100	0	R/W
47265	Exhaust Fan speed normal		47265	47265	47265	47265	47265	47265	47265	47265					%	u8	1	0	100	65	R/W
47266	Supply Fan speed 4		47266	47266	47266										%	u8	1	0	100	90	R/W
47267	Supply Fan speed 3		47267	47267	47267										%	u8	1	0	100	70	R/W
47268	Supply Fan speed 2		47268	47268	47268										%	u8	1	0	100	25	R/W
47269	Supply Fan speed 1		47269	47269	47269										%	u8	1	0	100	0	R/W
47270	Supply Fan speed normal		47270	47270	47270										%	u8	1	0	100	60	R/W
47271	Fan return time 4	Time from a changed fan speed until it returns to normal speed	47271	47271	47271	47271	47271	47271	47271	47271		47271	47271	47271	h	u8	1	1	99	4	R/W
47272	Fan return time 3	Time from a changed fan speed until it returns to normal speed	47272	47272	47272	47272	47272	47272	47272	47272		47272	47272	47272	h	u8	1	1	99	4	R/W
47273	Fan return time 2	Time from a changed fan speed until it returns to normal speed	47273	47273	47273	47273	47273	47273	47273	47273		47273	47273	47273	h	u8	1	1	99	4	R/W
47274	Fan return time 1	Time from a changed fan speed until it returns to normal speed	47274	47274	47274	47274	47274	47274	47274	47274		47274	47274	47274	h	u8	1	1	99	4	R/W
47275	Filter Reminder period	Time between the reminder of filter replacement/cleaning.	47275	47275	47275	47275	47275	47275	47275	47275		47275	47275	47275	Months	u8	1	1	24	3	R/W
47276	Floor drying	 0=Off 1=On	47276	47276	47276	47276	47276	47276	47276	47276	47276	47276	47276	47276		u8	1	0	1	0	R/W
47277	Floor drying period 7	Days each period is active	47277	47277	47277	47277	47277	47277	47277	47277	47277	47277	47277	47277	days	u8	1	0	30	2	R/W
47278	Floor drying period 6	Days each period is active	47278	47278	47278	47278	47278	47278	47278	47278	47278	47278	47278	47278	days	u8	1	0	30	2	R/W
47279	Floor drying period 5	Days each period is active	47279	47279	47279	47279	47279	47279	47279	47279	47279	47279	47279	47279	days	u8	1	0	30	2	R/W
47280	Floor drying period 4	Days each period is active	47280	47280	47280	47280	47280	47280	47280	47280	47280	47280	47280	47280	days	u8	1	0	30	3	R/W
47281	Floor drying period 3	Days each period is active	47281	47281	47281	47281	47281	47281	47281	47281	47281	47281	47281	47281	days	u8	1	0	30	2	R/W
47282	Floor drying period 2	Days each period is active	47282	47282	47282	47282	47282	47282	47282	47282	47282	47282	47282	47282	days	u8	1	0	30	2	R/W
47283	Floor drying period 1	Days each period is active	47283	47283	47283	47283	47283	47283	47283	47283	47283	47283	47283	47283	days	u8	1	0	30	2	R/W
47284	Floor drying temp. 7	Supply temperature each period	47284	47284	47284	47284	47284	47284	47284	47284	47284	47284	47284	47284	°C	u8	1	15	70	20	R/W
47285	Floor drying temp. 6	Supply temperature each period	47285	47285	47285	47285	47285	47285	47285	47285	47285	47285	47285	47285	°C	u8	1	15	70	30	R/W
47286	Floor drying temp. 5	Supply temperature each period	47286	47286	47286	47286	47286	47286	47286	47286	47286	47286	47286	47286	°C	u8	1	15	70	40	R/W
47287	Floor drying temp. 4	Supply temperature each period	47287	47287	47287	47287	47287	47287	47287	47287	47287	47287	47287	47287	°C	u8	1	15	70	45	R/W
47288	Floor drying temp. 3	Supply temperature each period	47288	47288	47288	47288	47288	47288	47288	47288	47288	47288	47288	47288	°C	u8	1	15	70	40	R/W
47289	Floor drying temp. 2	Supply temperature each period	47289	47289	47289	47289	47289	47289	47289	47289	47289	47289	47289	47289	°C	u8	1	15	70	30	R/W
47290	Floor drying temp. 1	Supply temperature each period	47290	47290	47290	47290	47290	47290	47290	47290	47290	47290	47290	47290	°C	u8	1	15	70	20	R/W
47291	Floor drying timer		47291	47291	47291	47291	47291	47291	47291	47291	47291	47291	47291	47291	hrs	u16	1	0	10000	0	R
47292	Trend temperature	Above the set outdoor temperature the addition activation time is limited to give the compressor more time to raise the hot water temperature.	47292	47292											°C	s16	10	0	200	70	R/W
47293	Transfer time HW-Heat	Time between hot water and heating operating mode	47293	47293											mins	s8	1	1	60	45	R/W
47294	Use airflow defrost	If reduced airflow should start defrost			47294											u8	1	0	0	0	R/W
47295	Airflow reduction trig	How much the airflow is allowed to be reduced before a defrost is trigged			47295										%	u8	1	0	0	0	R/W
47296	Airflow defrost done	How much the airflow has to raise before a defrost is ended			47296										%	u8	1	0	0	0	R/W
47299	Min time defrost	Minimum duration of the defrost			47299										min	u8	1	0	0	0	R/W
47300	DOT	Dimensioning outdoor temperature	47300	47300	47300	47300	47300	47300	47300	47300	47300	47300	47300	47300	°C	s16	10	-400	200	-180	R/W
47301	delta T at DOT	Delta T (BT12-BT3)at dimensioning outdoor temperature	47301	47301	47301	47301	47301	47301	47301	47301	47301	47301	47301	47301	°C	s16	10	10	250	100	R/W
47302	Climate system 2 accessory	Activates the climate system 2 accessory 0=Off 1=On	47302	47302	47302	47302	47302	47302	47302	47302		47302	47302	47302		u8	1	0	1	0	R/W
47303	Climate system 3 accessory	Activates the climate system 3 accessory 0=Off 1=On	47303	47303	47303	47303	47303	47303	47303	47303		47303	47303	47303		u8	1	0	1	0	R/W
47304	Climate system 4 accessory	Activates the climate system 4 accessory 0=Off 1=On	47304	47304	47304	47304	47304	47304	47304	47304		47304	47304	47304		u8	1	0	1	0	R/W
47305	Climate system 4 mixing valve amp.	Mixing valve amplification for extra climate systems	47305	47305	47305	47305	47305	47305	47305	47305		47305	47305	47305		s8	10	1	100	10	R/W
47306	Climate system 3 mixing valve amp.	Mixing valve amplification for extra climate systems	47306	47306	47306	47306	47306	47306	47306	47306		47306	47306	47306		s8	10	1	100	10	R/W
47307	Climate system 2 mixing valve amp.	Mixing valve amplification for extra climate systems	47307	47307	47307	47307	47307	47307	47307	47307		47307	47307	47307		s8	10	1	100	10	R/W
47308	Climate system 4 shunt wait	Wait time between changes of the shunt in extra climate systems	47308	47308	47308	47308	47308	47308	47308	47308		47308	47308	47308	secs	s16	10	10	300	30	R/W
47309	Climate system 3 shunt wait	Wait time between changes of the shunt in extra climate systems	47309	47309	47309	47309	47309	47309	47309	47309		47309	47309	47309	secs	s16	10	10	300	30	R/W
47310	Climate system 2 shunt wait	Wait time between changes of the shunt in extra climate systems	47310	47310	47310	47310	47310	47310	47310	47310		47310	47310	47310	secs	s16	10	10	300	30	R/W
47312	FLM pump 1	Operating mode for the FLM pump 1|Operating mode for the FLM pump 2|Operating mode for the FLM pump 3|Operating mode for the FLM pump 4 0=Off 1=On					47312	47312	47312	47312						u8	1	0	1	0	R/W
47313	FLM 1 defrost	Minimum time between defrost in FLM 1|Minimum time between defrost in FLM 2|Minimum time between defrost in FLM 3|Minimum time between defrost in FLM 4					47313	47313	47313	47313					hrs	u8	1	1	30	10	R/W
47317	Shunt controlled add. accessory	Activates the shunt controlled addition accessory. 1=on,0=off 0=Off 1=On			47317		47317	47317	47317	47317		47317	47317	47317		u8	1	0	1	0	R/W
47318	Shunt controlled add. min. temp.				47318		47318	47318	47318	47318		47318	47318	47318	°C	s8	1	5	90	55	R/W
47319	Shunt controlled add. min. runtime				47319		47319	47319	47319	47319		47319	47319	47319	hrs	u8	1	0	48	12	R/W
47320	Shunt controlled add. mixing valve amp.	Mixing valve amplification for shunt controlled add.			47320		47320	47320	47320	47320		47320	47320	47320		s8	10	1	100	10	R/W
47321	Shunt controlled add. mixing valve wait	Wait time between changes of the shunt in shunt controlled add.			47321		47321	47321	47321	47321		47321	47321	47321	secs	s16	1	10	300	30	R/W
47322	Step controlled add. accessory	Activates the step controlled addition accessory 0=Off 1=On					47322	47322	47322	47322		47322	47322			u8	1	0	1	0	R/W
47323	Step controlled add. start DM	DM where the first step of step controlled add. starts									47323		47323			s16	1	-2000	-30	-400	R/W
47324	Step controlled add. diff. DM	Difference in DM of each step in the step controlled add.					47324	47324	47324	47324	47324	47324	47324	47324		s16	1	0	1000	100	R/W
47325	Step controlled add. max. step	Maximum number of steps allowed in step controlled add.					47325	47325	47325	47325	47325	47325	47325	47325		u8	1	0	7	3	R
47326	Step controlled add. mode	Binary or linear stepping method. 0=Linear 1=Binary					47326	47326	47326	47326	47326	47326	47326	47326		u8	1	0	1	0	R/W
47327	Ground water pump accessory	Ground water pump using AXC40 0=Off 1=On					47327	47327	47327	47327						u8	1	0	1	0	R/W
47329	Cooling 2-pipe accessory	Activates the 2-pipe cooling accessory 0=Off 1=On					47329	47329	47329	47329						u8	1	0	1	0	R/W
47330	Cooling 4-pipe accessory	Activates the 4-pipe cooling accessory 0=Off 1=On					47330	47330	47330	47330						u8	1	0	1	0	R/W
47335	Time betw. switch heat/cool	Time between switching from heating to cooling or vice versa.					47335	47335	47335	47335	47335	47335	47335	47335	h	s8	1	0	48	2	R/W
47336	Heat at room under temp.	This value indicates how many degrees under set room temp heating will be allowed					47336	47336	47336	47336	47336	47336	47336	47336	°C	s8	10	5	100	10	R/W
47337	Cool at room over temp.	This value indicates how many degrees over set room temp cooling will be allowed					47337	47337	47337	47337	47337	47337	47337	47337	°C	s8	10	5	100	30	R/W
47338	Cooling mix. valve amp.	Mixing valve amplification for the cooling valve					47338	47338	47338	47338						s8	10	1	100	10	R/W
47339	Cooling mix. valve step delay						47339	47339	47339	47339		47339		47339	s	s16	1	10	300	30	R/W
47340	Cooling with room sensor	Enables use of room sensor together with cooling 0=Off 1=On					47340	47340	47340	47340	47340	47340	47340	47340		u8	10	0	18	0	R/W
47341	HPAC accessory	Activates the HPAC accessory					47341	47341	47341	47341						u8	1	0	1	0	R/W
47342	Start Passive Cooling DM	Value the degree minutes have to reach to start passive cooling					47342	47342	47342	47342						s16	1	10	500	30	R/W
47343	Start Active Cooling DM	Value the degree minutes have to reach to start active cooling					47343	47343	47343	47343	47343	47343	47343	47343		s16	1	10	300	90	R/W
47351	FJVM accessory	Activates the FJVM accessory 0=Off 1=On	47351	47351												u8	1	0	1	0	R/W
47352	SMS40 accessory	Activates the SMS40 accessory	47352	47352	47352	47352	47352	47352	47352	47352		47352	47352	47352		u8	1	0	1	0	R/W
47365	RMU System 1	Activates the RMU accessory for system 1	47365	47365	47365		47365	47365	47365	47365		47365	47365	47365		u8	1	0	1	0	R/W
47366	RMU System 2	Activates the RMU accessory for system 2	47366	47366	47366		47366	47366	47366	47366		47366	47366	47366		u8	1	0	1	0	R/W
47367	RMU System 3	Activates the RMU accessory for system 3	47367	47367	47367		47367	47367	47367	47367		47367	47367	47367		u8	1	0	1	0	R/W
47368	RMU System 4	Activates the RMU accessory for system 4	47368	47368	47368		47368	47368	47368	47368		47368	47368	47368		u8	1	0	1	0	R/W
47370	Allow Additive Heating	Whether to allow additive heating (only valid for operational mode Manual)	47370	47370	47370	47370	47370	47370	47370	47370	47370	47370	47370	47370		u8	1	0	1	1	R/W
47371	Allow Heating	Whether to allow heating (only valid for operational mode Manual or Add. heat only)	47371	47371	47371	47371	47371	47371	47371	47371	47371	47371	47371	47371		u8	1	0	1	1	R/W
47372	Allow Cooling	Whether to allow cooling (only valid for operational mode Manual or Add. heat only)	47372	47372			47372	47372	47372	47372	47372	47372	47372	47372		u8	1	0	1	1	R/W
47374	Start Temperature Cooling	Start temperature for cooling, as set in menu 4.9.2 0=Off 1=On	47374	47374	47374	47374	47374	47374	47374	47374	47374	47374	47374	47374	°C	s16	10	-200	400	250	R/W
47375	Stop Temperature Heating	Stop temperature for heating, as set in menu 4.9.2	47375	47375	47375	47375	47375	47375	47375	47375	47375	47375	47375	47375	°C	s16	10	-200	400	170	R/W
47376	Stop Temperature Additive	Stop temperature for additive, as set in menu 4.9.2	47376	47376	47376	47376	47376	47376	47376	47376	47376	47376	47376	47376	°C	s16	10	-250	400	150	R/W
47377	Outdoor Filter Time	 12=12 Hours 24=24 Hours	47377	47377	47377	47377	47377	47377	47377	47377	47377	47377	47377	47377	h	u8	1	0	48	24	R/W
47378	Max diff. comp.		47378	47378	47378	47378	47378	47378	47378	47378	47378	47378	47378	47378	°C	s16	10	10	250	100	R/W
47379	Max diff. add.		47379	47379	47379	47379	47379	47379	47379	47379	47379	47379	47379	47379	°C	s16	10	10	240	70	R/W
47380	Low brine out autoreset	 0=Off 1=On					47380	47380	47380	47380						u8	1	0	1	0	R/W
47381	Low brine out temp.EP14						47381	47381	47381	47381					°C	s16	10	-120	150	-80	R/W
47382	High brine in	Activates the High brine in temperature alarm. 0=Off 1=On					47382	47382	47382	47382						u8	1	1	1	1	R/W
47383	High brine in temp.	The brine in temperature that triggers the high brine in temperature alarm (if active).					47383	47383	47383	47383					°C	s16	10	100	300	300	R/W
47384	Date format	 1=DD-MM-YY 2=YY-MM-DD	47384	47384	47384	47384	47384	47384	47384	47384	47384	47384	47384	47384		u8	1	1	2	1	R/W
47385	Time format	 12=12 hours 24=24 Hours	47385	47385	47385	47385	47385	47385	47385	47385	47385	47385	47385	47385		u8	1	12	24	24	R/W
47387	HW production	Activates hot water production where applicable 0=Off 1=On	47387	47387	47387	47387	47387	47387	47387	47387	47387	47387	47387	47387		u8	1	0	1	0	R/W
47388	Alarm lower room temp.	Lowers the room temperature during red light alarms to notify the occupants of the building that something is the matter 0=Off 1=On	47388	47388	47388	47388	47388	47388	47388	47388	47388	47388	47388	47388		u8	1	0	1	0	R/W
47389	Alarm lower HW temp.	Lowers the hot water temperature during red light alarms to notify the occupants of the building that something is the matter 0=Off 1=On	47389	47389	47389	47389	47389	47389	47389	47389	47389	47389	47389	47389		u8	1	0	1	1	R/W
47391	Use room sensor S4	When activated the system uses the room sensor 0=Off 1=On	47391	47391	47391	47391	47391	47391	47391	47391		47391	47391	47391		u8	1	0	1	0	R/W
47392	Use room sensor S3	When activated the system uses the room sensor 0=Off 1=On	47392	47392	47392	47392	47392	47392	47392	47392		47392	47392	47392		u8	1	0	1	0	R/W
47393	Use room sensor S2	When activated the system uses the room sensor 0=Off 1=On	47393	47393	47393	47393	47393	47393	47393	47393		47393	47393	47393		u8	1	0	1	0	R/W
47394	Use room sensor S1	When activated the system uses the room sensor 0=Off 1=On	47394	47394	47394	47394	47394	47394	47394	47394	47394	47394	47394	47394		u8	1	0	1	0	R/W
47395	Room sensor setpoint S4	Sets the room temperature setpoint for the system	47395	47395	47395	47395	47395	47395	47395	47395		47395	47395	47395	°C	s16	10	50	300	200	R/W
47396	Room sensor setpoint S3	Sets the room temperature setpoint for the system	47396	47396	47396	47396	47396	47396	47396	47396		47396	47396	47396	°C	s16	10	50	300	200	R/W
47397	Room sensor setpoint S2	Sets the room temperature setpoint for the system	47397	47397	47397	47397	47397	47397	47397	47397		47397	47397	47397	°C	s16	10	50	300	200	R/W
47398	Room sensor setpoint S1	Sets the room temperature setpoint for the system	47398	47398	47398	47398	47398	47398	47398	47398	47398	47398	47398	47398	°C	s16	10	50	300	200	R/W
47399	Room sensor factor S4	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	47399	47399	47399	47399	47399	47399	47399	47399		47399	47399	47399		u8	10	0	60	10	R/W
47400	Room sensor factor S3	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	47400	47400	47400	47400	47400	47400	47400	47400		47400	47400	47400		u8	10	0	60	10	R/W
47401	Room sensor factor S2	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	47401	47401	47401	47401	47401	47401	47401	47401		47401	47401	47401		u8	10	0	60	10	R/W
47402	Room sensor factor S1	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	47402	47402	47402	47402	47402	47402	47402	47402	47402	47402	47402	47402		u8	10	0	60	10	R/W
47413	Speed circ.pump HW						47413	47413	47413	47413					%	u8	1	1	100	70	R/W
47414	Speed circ.pump Heat						47414	47414	47414	47414					%	u8	1	1	100	70	R/W
47415	Speed circ.pump Pool						47415	47415	47415	47415					%	u8	1	1	100	70	R/W
47416	Speed circ.pump Economy						47416	47416	47416	47416					%	u8	1	1	100	30	R/W
47417	Speed Circulation Pump Passive Cooling EP14						47417	47417	47417	47417					%	u8	1	1	100	70	R/W
47418	Speed brine pump						47418	47418	47418	47418					%	u8	1	1	100	100	R/W
47442	preset flow clim. sys.	Preset flow setting for climate system. 0 = manual setting, 1 = radiator, 2 = floor heating, 3 = radiator + floor heating.	47442	47442	47442	47442	47442	47442	47442	47442	47442	47442	47442	47442		u8	1	0	3	1	R/W
47473	Max time defrost	Maximum duration of the defrost			47473										min	u8	1	0	0	0	R/W
47525	Heat Curve S8	Heat curve, see manual for more information	47525	47525	47525	47525	47525	47525	47525	47525		47525	47525	47525		s8	1	0	15	9	R/W
47536	Fan synch mode	If the fan should have a lower speed when the compressor is not running 0=Off 1=On	47536	47536												u8	1	0	1	0	R/W
47537	Night cooling	If the fan should have a higher speed when there is a high room temp and a low outdoor temp. 0=Off 1=On	47537	47537	47537	47537	47537	47537	47537	47537		47537	47537	47537		u8	1	0	1	0	R/W
47538	Start room temp. night cooling		47538	47538	47538	47538	47538	47538	47538	47538		47538	47538	47538	°C	u8	1	20	30	25	R/W
47539	Night Cooling Min. diff.	Minimum difference between room temp and outdoor temp to start night cooling	47539	47539	47539	47539	47539	47539	47539	47539		47539	47539	47539	°C	u8	1	3	10	6	R/W
47540	Heat DM diff	Difference in DM between compressor starts in heating mode						47540	47540	47540		47540				s16	1	10	2000	60	R/W
47543	Cooling DM diff	Difference in DM between compressor starts in cooling mode						47543	47543	47543		47543				s16	1	10	150	30	R/W
47555	DEW accessory	Activates the DEW accessory			47555											u8	1	0	1	0	R/W
47556	DEH accessory	Activates the DEH accessory	47556	47556												u8	1	0	1	0	R/W
47564	Allow Heating Sys1	Whether to allow heating for system 1 (only valid for operational mode Manual or Add. heat only)	47564	47564												u8	1	0	1	1	R/W
47565	Allow Heating Sys2	Whether to allow heating for system 2 (only valid for operational mode Manual or Add. heat only)	47565	47565												u8	1	0	1	1	R/W
47567	Heat Curve S7	Heat curve, see manual for more information	47567	47567	47567	47567	47567	47567	47567	47567		47567	47567	47567		s8	1	0	15	9	R/W
47613	Max Internal Add	Maximum allowed steps for the internally connected addition.							47613	47613	47613	47613				u8	1	0	7	3	R/W
47614	Int. connected add. mode	Binary or linear stepping method for the internally connected external addition. 0=Linear 1=Binary							47614	47614	47614	47614				u8	1	0	1	0	R/W
47631	External add step controlled	Puts the external addition i step mode												47631		u8	1	0	1	0	R/W
47632	External add. min. runtime	Min. runtime, only relevant if not step mode												47632	hrs	u8	1	0	48	12	R/W
47633	State ext. add.	Only relevant if not in step mode												47633		u8	1	0	0	0	R
48043	Holiday - Activated	0=inactive, 10=active	48043	48043	48043	48043	48043	48043	48043	48043	48043	48043	48043	48043		u8	1	0	10	0	R/W
48053	FLM 2 speed 4						48053	48053	48053	48053					%	u8	1	0	100	100	R/W
48054	FLM 2 speed 3						48054	48054	48054	48054					%	u8	1	0	100	80	R/W
48055	FLM 2 speed 2						48055	48055	48055	48055					%	u8	1	0	100	30	R/W
48056	FLM 2 speed 1						48056	48056	48056	48056					%	u8	1	0	100	0	R/W
48057	FLM 2 speed normal						48057	48057	48057	48057					%	u8	1	0	100	65	R/W
48058	FLM 3 speed 4						48058	48058	48058	48058					%	u8	1	0	100	100	R/W
48059	FLM 3 speed 3						48059	48059	48059	48059					%	u8	1	0	100	80	R/W
48060	FLM 3 speed 2						48060	48060	48060	48060					%	u8	1	0	100	30	R/W
48061	FLM 3 speed 1						48061	48061	48061	48061					%	u8	1	0	100	0	R/W
48062	FLM 3 speed normal						48062	48062	48062	48062					%	u8	1	0	100	65	R/W
48063	FLM 4 speed 4						48063	48063	48063	48063					%	u8	1	0	100	100	R/W
48064	FLM 4 speed 3						48064	48064	48064	48064					%	u8	1	0	100	80	R/W
48065	FLM 4 speed 2						48065	48065	48065	48065					%	u8	1	0	100	30	R/W
48066	FLM 4 speed 1						48066	48066	48066	48066					%	u8	1	0	100	0	R/W
48067	FLM 4 speed normal						48067	48067	48067	48067					%	u8	1	0	100	65	R/W
48068	FLM 4 accessory	Activates the FLM 4 accessory					48068	48068	48068	48068						u8	1	0	1	0	R/W
48069	FLM 3 accessory	Activates the FLM 3 accessory					48069	48069	48069	48069						u8	1	0	1	0	R/W
48070	FLM 2 accessory	Activates the FLM 2 accessory					48070	48070	48070	48070						u8	1	0	1	0	R/W
48071	FLM 1 accessory	Activates the FLM 1 accessory					48071	48071	48071	48071						u8	1	0	1	0	R/W
48072	DM diff start add.	The value below the last compressor step the degree minutes needed to be reached for the pump to start electric addition			48072	48072	48072	48072	48072	48072	48072	48072	48072	48072		s16	1	10	2400	700	R/W
48073	FLM 1 cooling	FLM 1 cooling activated|FLM 2 cooling activated|FLM 3 cooling activated|FLM 4 cooling activated					48073	48073	48073	48073						u8	1	0	1	0	R/W
48074	Cool/Heat Sensor Set Point	Set point for change between cooling and heating when using the cool/heat sensor					48074	48074	48074	48074	48074	48074	48074	48074		s16	10	50	400	210	R/W
48083	Solar Pool Heating Active	1=Yes, 0=No												48083		u8	1	0	0	0	R
48085	Heat medium pump manual speed	Heat medium pump speed if manual									48085	48085		48085	%	s8	1	1	100	70	R/W
48086	Hot water tank type	 10=VPB 20=VPA								48086						u8	1	10	20	20	R/W
48087	Pool 2 accessory	Activate the pool 2 accessory					48087	48087	48087	48087		48087				u8	1	0	1	0	R/W
48088	Pool 1 accessory	Activates the pool 1 accessory					48088	48088	48088	48088		48088	48088	48088		u8	1	0	1	0	R/W
48089	Pool 2 start temp.	The Temperature below which the pool heating should start					48089	48089	48089	48089		48089			°C	s16	10	50	800	220	R/W
48090	Pool 1 start temp.	The Temperature below which the pool heating should start					48090	48090	48090	48090		48090	48090	48090	°C	s16	10	50	800	220	R/W
48091	Pool 2 stop temp.	The Temperature at which the pool heating will stop					48091	48091	48091	48091		48091			°C	s16	10	50	800	240	R/W
48092	Pool 1 stop temp.	The Temperature at which the pool heating will stop					48092	48092	48092	48092		48092	48092	48092	°C	s16	10	50	800	240	R/W
48093	Pool 2 Activated	Activates pool heating					48093	48093	48093	48093		48093				u8	1	0	1	1	R/W
48094	Pool 1 Activated	Activates pool heating					48094	48094	48094	48094		48094	48094	48094		u8	1	0	1	1	R/W
48099	External add. accessory	Activates the external addition accessory												48099		u8	1	0	1	0	R/W
48107	Charge pump manual speed	Charge pump speed if manual												48107	%	s8	1	1	100	70	R/W
48120	HW Comfort	Activates the HW Comfort Accessory.					48120	48120	48120	48120			48120			u8	1	0	1	0	R/W
48130	Manual heat medium pump speed	Manual heat medium pump speed?									48130	48130		48130	%	s8	1	0	1	0	R/W
48131	Manual charge pump speed	Manual charge pump speed?												48131	%	s8	1	0	1	0	R/W
48132	Temporary Lux	0=Off, 1=3h, 2=6h, 3=12h, 4=One time increase	48132	48132	48132	48132	48132	48132	48132	48132	48132	48132	48132	48132		s8	1	0	0	0	R/W
48133	Period Pool 2						48133	48133	48133	48133		48133			min	u8	1	0	180	30	R/W
48139	DM startdiff add. with shunt				48139		48139	48139	48139	48139		48139	48139			s16	1	0	2000	400	R/W
48140	Max pool 2 compr.	Maximum number of compressors that are simultaneously charging the pool							48140	48140		48140				u8	1	1	18	18	R/W
48141	Max pool 1 compr.	Maximum number of compressors that are simultaneously charging the pool							48141	48141		48141				u8	1	1	18	18	R/W
48142	Step controlled add. start diff DM	DM diff from last compressor step where the first step of step controlled add. starts					48142	48142	48142	48142		48142				s16	1	0	2000	400	R/W
48144	HW Comfort add during Heat	Allows the HW Comfort addition to run during heating.					48144	48144	48144	48144						u8	1	0	1	0	R/W
48145	HW Comfort mixing valve	Activates the HW Comfort Shunt.					48145	48145	48145	48145						u8	1	0	1	0	R/W
48146	HW Comfort mixing valve amp.	Mixing valve amplification for the HW Comfort Accessory					48146	48146	48146	48146						s8	10	1	100	10	R/W
48147	HW Comfort mixing valve wait	Wait time between changes of the mixing valve for the HW Comfort Accessory					48147	48147	48147	48147					secs	s16	10	10	300	30	R/W
48148	HW Comfort hotwater temperature	The desired hotwater temperature					48148	48148	48148	48148					°C	s8	10	40	65	55	R/W
48156	External cooling accessory	Activates the external cooling accessory										48156	48156	48156		u8	1	0	1	0	R/W
48157	HW Comfort add.	Activates the HW Comfort Addition.					48157	48157	48157	48157						u8	1	0	1	0	R/W
48158	SAM supply air curve: outdoor temp T3	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48158										°C	s16	10	-400	200	150	R/W
48159	SAM supply air curve: outdoor temp T2	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48159										°C	s16	10	-390	190	0	R/W
48160	SAM supply air curve: outdoor temp T1	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48160										°C	s16	10	-400	200	-150	R/W
48161	SAM supply air curve: supply air temp at T3	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48161										°C	s16	10	160	520	180	R/W
48162	SAM supply air curve: supply air temp at T2	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48162										°C	s16	10	160	520	180	R/W
48163	SAM supply air curve: supply air temp at T1	The supply air curve is defined by 3 supply air temperatures at 3 different outdoor temperatures T1, T2 and T3.			48163										°C	s16	10	160	520	180	R/W
48174	Min cooling supply temp S4	Minimum allowed supply temperature during cooling					48174	48174	48174	48174		48174	48174	48174	°C	s8	1	-5	30	18	R/W
48175	Min cooling supply temp S3	Minimum allowed supply temperature during cooling					48175	48175	48175	48175		48175	48175	48175	°C	s8	1	-5	30	18	R/W
48176	Min cooling supply temp S2	Minimum allowed supply temperature during cooling					48176	48176	48176	48176		48176	48176	48176	°C	s8	1	-5	30	18	R/W
48177	Min cooling supply temp S1	Minimum allowed supply temperature during cooling					48177	48177	48177	48177	48177	48177	48177	48177	°C	s8	1	-5	30	18	R/W
48181	Own Cooling Curve P3	User defined cooling curve point					48181	48181	48181	48181	48181	48181	48181	48181	°C	s8	1	-5	40	20	R/W
48185	Own Cooling Curve P5	User defined cooling curve point					48185	48185	48185	48185	48185	48185	48185	48185	°C	s8	1	-5	40	20	R/W
48186	Cooling use mix. valve S4	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48186	48186	48186	48186		48186	48186	48186		u8	1	0	1	0	R/W
48187	Cooling use mix. valve S3	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48187	48187	48187	48187		48187	48187	48187		u8	1	0	1	0	R/W
48188	Cooling use mix. valve S2	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48188	48188	48188	48188		48188	48188	48188		u8	1	0	1	0	R/W
48189	Cooling use mix. valve S1	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48189	48189	48189	48189	48189	48189	48189	48189		u8	1	0	0	0	R/W
48190	Heatdump mix. valve delay	Mixing valve step delay for the heatdump valve					48190	48190	48190	48190					s	s16	1	10	500	30	R/W
48191	Heatdump mix. valve amp.	Mixing valve amplification for the heatdump valve					48191	48191	48191	48191						s8	10	1	100	10	R/W
48192	Cooldump mix. valve delay	Mixing valve step delay for the cooldump valve for the ACS-system					48192	48192	48192	48192					s	s16	1	10	500	30	R/W
48193	Cooldump mix. valve amp.	Mixing valve amplification for the cooldump valve for the ACS-system					48193	48193	48193	48193						s8	10	1	100	10	R/W
48194	ACS accessory	Activate the ACS accessory					48194	48194	48194	48194						u8	1	0	1	0	R/W
48195	ACS heat dump 24h-function						48195	48195	48195	48195						u8	1	0	1	0	R/W
48197	ACS closingtime for cool dump						48197	48197	48197	48197					s	u8	1	0	100	0	R/W
48198	ACS max cprs in active cooling							48198	48198	48198						u8	1	0	18	18	R/W
48201	SCA accessory	Activates the SCA accessory			48201	48201										u8	1	0	1	0	R/W
48206	Silent Mode Status	1 = active, 0 = inactive			48206	48206					48206	48206	48206	48206		u8	1	0	0	0	R
48207	Period Cool											48207	48207	48207	min	u8	1	0	180	30	R/W
48208	Operational mode cool pump												48208	48208		u8	1	0	1	1	R/W
48214	Cooling delta temp. at 20°C	Delta Temperature at 20°C. Used to control charge pump speed									48214	48214	48214	48214	°C	s8	1	3	10	3	R/W
48215	Cooling delta temp. at 40°C	Delta Temperature at 40°C. Used to control charge pump speed									48215	48215	48215	48215	°C	s8	1	3	20	6	R/W
48228	Operational mode charge pump S8											48228				u8	1	0	1	0	R/W
48229	Operational mode charge pump S7											48229				u8	1	0	1	0	R/W
48230	Operational mode charge pump S6											48230				u8	1	0	1	0	R/W
48231	Operational mode charge pump S5											48231				u8	1	0	1	0	R/W
48232	Operational mode charge pump S4											48232				u8	1	0	1	0	R/W
48233	Operational mode charge pump S3											48233				u8	1	0	1	0	R/W
48234	Operational mode charge pump S2											48234				u8	1	0	1	0	R/W
48235	Operational mode charge pump S1										48235	48235	48235			u8	1	0	1	1	R/W
48264	Brine shunt accessory	Activates the Brine shunt accessory					48264	48264	48264	48264						u8	1	0	1	0	R/W
48265	Brine shunt amplication	The Brine shunt accessory, shunt amplication					48265	48265	48265	48265						s8	10	0	100	10	R/W
48266	Brine shunt wait time	The Brine shunt accessory, wait time					48266	48266	48266	48266					s	s16	1	10	300	30	R/W
48267	Brine shunt, max brine temp	The Brine shunt accessory, max brine temperature					48267	48267	48267	48267					°C	u8	1	0	30	20	R/W
48274	Hot Water Stepdiff Compressor							48274	48274	48274		48274				s16	10	0	400	100	R/W
48275	Max charge pump reg speed	Max heat medium pump reg speed			48275	48275	48275	48275	48275	48275				48275	%	u8	1	50	100	100	R/W
48278	DM start ext. add.													48278		s16	1	50	2000	1400	R/W
48279	Position of Addition	Addition before QN10:0, Addition after QN10:1									48279	48279				u8	1	0	0	0	R/W
48280	Internal HW add in tank	Internal HW add in tank							48280	48280		48280				u8	1	0	1	0	R/W
48281	Charge method HW	Heating medium pump control when hot water is charged				48281	48281	48281	48281	48281		48281				u8	1	0	1	1	R/W
48282	SG Ready heating	Sets whether or not SG Ready should affect heating	48282	48282	48282	48282	48282	48282	48282	48282	48282	48282	48282	48282		u8	1	0	1	1	R/W
48283	SG Ready cooling	Sets whether or not SG Ready should affect cooling	48283	48283	48283	48283	48283	48283	48283	48283	48283	48283	48283	48283		u8	1	0	1	1	R/W
48284	SG Ready hot water	Sets whether or not SG Ready should affect hot water	48284	48284	48284	48284	48284	48284	48284	48284	48284	48284	48284	48284		u8	1	0	1	1	R/W
48285	SG Ready pool	Sets whether or not SG Ready should affect pool	48285	48285	48285	48285	48285	48285	48285	48285	48285	48285	48285	48285		u8	1	0	1	1	R/W
48286	Pool 2 Cpr Percentage						48286								%	u8	1	1	100	1	R/W
48287	Pool 1 Cpr Percentage						48287								%	u8	1	1	100	1	R/W
48288	Cool Cpr Percentage						48288								%	u8	1	1	100	1	R/W
48367	Speed circ.pump Heat Slave 8											48367			%	u8	1	1	100	70	R/W
48368	Speed circ.pump Heat Slave 7											48368			%	u8	1	1	100	70	R/W
48369	Speed circ.pump Heat Slave 6											48369			%	u8	1	1	100	70	R/W
48370	Speed circ.pump Heat Slave 5											48370			%	u8	1	1	100	70	R/W
48371	Speed circ.pump Heat Slave 4											48371			%	u8	1	1	100	70	R/W
48372	Speed circ.pump Heat Slave 3											48372			%	u8	1	1	100	70	R/W
48373	Speed circ.pump Heat Slave 2											48373			%	u8	1	1	100	70	R/W
48374	Speed circ.pump Heat Slave 1										48374	48374	48374		%	u8	1	1	100	70	R/W
48375	Op mode circ.pump Heat Slave 8											48375				u8	1	0	1	1	R/W
48376	Op mode circ.pump Heat Slave 7											48376				u8	1	0	1	1	R/W
48377	Op mode circ.pump Heat Slave 6											48377				u8	1	0	1	1	R/W
48378	Op mode circ.pump Heat Slave 5											48378				u8	1	0	1	1	R/W
48379	Op mode circ.pump Heat Slave 4											48379				u8	1	0	1	1	R/W
48380	Op mode circ.pump Heat Slave 3											48380				u8	1	0	1	1	R/W
48381	Op mode circ.pump Heat Slave 2											48381				u8	1	0	1	1	R/W
48382	Op mode circ.pump Heat Slave 1										48382	48382	48382			u8	1	0	1	1	R/W
48390	Speed circ.pump HW Slave 1										48390	48390	48390		%	u8	1	1	100	70	R/W
48391	Op mode circ.pump HW Slave 8											48391				u8	1	0	1	1	R/W
48392	Op mode circ.pump HW Slave 7											48392				u8	1	0	1	1	R/W
48393	Op mode circ.pump HW Slave 6											48393				u8	1	0	1	1	R/W
48394	Op mode circ.pump HW Slave 5											48394				u8	1	0	1	1	R/W
48395	Op mode circ.pump HW Slave 4											48395				u8	1	0	1	1	R/W
48396	Op mode circ.pump HW Slave 3											48396				u8	1	0	1	1	R/W
48397	Op mode circ.pump HW Slave 2											48397				u8	1	0	1	1	R/W
48398	Op mode circ.pump HW Slave 1										48398	48398	48398			u8	1	0	1	1	R/W
48399	Speed circ.pump Pool Slave 8											48399			%	u8	1	1	100	70	R/W
48400	Speed circ.pump Pool Slave 7											48400			%	u8	1	1	100	70	R/W
48401	Speed circ.pump Pool Slave 6											48401			%	u8	1	1	100	70	R/W
48402	Speed circ.pump Pool Slave 5											48402			%	u8	1	1	100	70	R/W
48403	Speed circ.pump Pool Slave 4											48403			%	u8	1	1	100	70	R/W
48404	Speed circ.pump Pool Slave 3											48404			%	u8	1	1	100	70	R/W
48405	Speed circ.pump Pool Slave 2											48405			%	u8	1	1	100	70	R/W
48406	Speed circ.pump Pool Slave 1											48406	48406		%	u8	1	1	100	70	R/W
48407	Op mode circ.pump Pool Slave 8											48407				u8	1	0	1	1	R/W
48408	Op mode circ.pump Pool Slave 7											48408				u8	1	0	1	1	R/W
48409	Op mode circ.pump Pool Slave 6											48409				u8	1	0	1	1	R/W
48410	Op mode circ.pump Pool Slave 5											48410				u8	1	0	1	1	R/W
48411	Op mode circ.pump Pool Slave 4											48411				u8	1	0	1	1	R/W
48412	Op mode circ.pump Pool Slave 3											48412				u8	1	0	1	1	R/W
48413	Op mode circ.pump Pool Slave 2											48413				u8	1	0	1	1	R/W
48414	Op mode circ.pump Pool Slave 1											48414	48414			u8	1	0	1	1	R/W
48415	Speed circ.pump Cooling Slave 8											48415			%	u8	1	1	100	70	R/W
48416	Speed circ.pump Cooling Slave 7											48416			%	u8	1	1	100	70	R/W
48417	Speed circ.pump Cooling Slave 6											48417			%	u8	1	1	100	70	R/W
48418	Speed circ.pump Cooling Slave 5											48418			%	u8	1	1	100	70	R/W
48419	Speed circ.pump Cooling Slave 4											48419			%	u8	1	1	100	70	R/W
48420	Speed circ.pump Cooling Slave 3											48420			%	u8	1	1	100	70	R/W
48421	Speed circ.pump Cooling Slave 2											48421			%	u8	1	1	100	70	R/W
48422	Speed circ.pump Cooling Slave 1										48422	48422	48422		%	u8	1	1	100	70	R/W
48424	Op mode circ.pump Cooling Slave 8											48424				u8	1	0	1	1	R/W
48425	Op mode circ.pump Cooling Slave 7											48425				u8	1	0	1	1	R/W
48426	Op mode circ.pump Cooling Slave 6											48426				u8	1	0	1	1	R/W
48427	Op mode circ.pump Cooling Slave 5											48427				u8	1	0	1	1	R/W
48428	Op mode circ.pump Cooling Slave 4											48428				u8	1	0	1	1	R/W
48429	Op mode circ.pump Cooling Slave 3											48429				u8	1	0	1	1	R/W
48430	Op mode circ.pump Cooling Slave 2											48430				u8	1	0	1	1	R/W
48431	Op mode circ.pump Cooling Slave 1										48431	48431	48431			u8	1	0	1	1	R/W
48433	Speed circ.pump Waiting Slave 8											48433			%	u8	1	1	100	30	R/W
48434	Speed circ.pump Waiting Slave 7											48434			%	u8	1	1	100	30	R/W
48435	Speed circ.pump Waiting Slave 6											48435			%	u8	1	1	100	30	R/W
48436	Speed circ.pump Waiting Slave 5											48436			%	u8	1	1	100	30	R/W
48437	Speed circ.pump Waiting Slave 4											48437			%	u8	1	1	100	30	R/W
48438	Speed circ.pump Waiting Slave 3											48438			%	u8	1	1	100	30	R/W
48439	Speed circ.pump Waiting Slave 2											48439			%	u8	1	1	100	30	R/W
48440	Speed circ.pump Waiting Slave 1										48440	48440	48440		%	u8	1	1	100	30	R/W
48452	Auto heat medium pump speed, hw	Auto heat medium pump speed hw			48452	48452	48452	48452	48452	48452					%	s8	1	0	1	1	R/W
48453	Auto heat medium pump speed, heat	Auto heat medium pump speed heat			48453	48453	48453	48453	48453	48453					%	s8	1	0	1	1	R/W
48454	Auto heat medium pump speed, pool	Auto heat medium pump speed pool			48454	48454	48454	48454	48454	48454					%	s8	1	0	1	1	R/W
48455	Auto heat medium pump speed, cool	Auto heat medium pump speed cool			48455	48455	48455	48455	48455	48455					%	s8	1	0	1	0	R/W
48456	Operational mode heat medium pump, cooling						48456	48456	48456	48456						u8	1	10	20	10	R/W
48457	Int shunt controlled add.								48457	48457		48457				u8	1	0	1	0	R/W
48458	Max speed circ.pump Heat						48458	48458	48458	48458					%	u8	1	50	100	100	R/W
48459	Speed brine pump passive cooling						48459	48459	48459	48459					%	u8	1	0	100	75	R/W
48460	EB108 Max charge pump reg speed	Max charge pump reg speed										48460			%	u8	1	80	100	100	R/W
48461	EB107 Max charge pump reg speed	Max charge pump reg speed										48461			%	u8	1	80	100	100	R/W
48462	EB106 Max charge pump reg speed	Max charge pump reg speed										48462			%	u8	1	80	100	100	R/W
48463	EB105 Max charge pump reg speed	Max charge pump reg speed										48463			%	u8	1	80	100	100	R/W
48464	EB104 Max charge pump reg speed	Max charge pump reg speed										48464			%	u8	1	80	100	100	R/W
48465	EB103 Max charge pump reg speed	Max charge pump reg speed										48465			%	u8	1	80	100	100	R/W
48466	EB102 Max charge pump reg speed	Max charge pump reg speed										48466			%	u8	1	80	100	100	R/W
48467	EB101 Max charge pump reg speed	Max charge pump reg speed									48467	48467	48467	48467	%	u8	1	80	100	100	R/W
48468	Operational mode charge pump in cooling mode S8											48468				u8	1	0	1	0	R/W
48469	Operational mode charge pump in cooling mode S7											48469				u8	1	0	1	0	R/W
48470	Operational mode charge pump in cooling mode S6											48470				u8	1	0	1	0	R/W
48471	Operational mode charge pump in cooling mode S5											48471				u8	1	0	1	0	R/W
48472	Operational mode charge pump in cooling mode S4											48472				u8	1	0	1	0	R/W
48473	Operational mode charge pump in cooling mode S3											48473				u8	1	0	1	0	R/W
48474	Operational mode charge pump in cooling mode S2											48474				u8	1	0	1	0	R/W
48475	Operational mode charge pump in cooling mode S1										48475	48475	48475			u8	1	0	1	1	R/W
48486	Prioritize Addition AXC40												48486	48486		u8	1	0	1	0	R/W
48487	Speed Circulation Pump Active Cooling EP14						48487	48487	48487	48487					%	u8	1	1	100	70	R/W
48488	Heat Curve S6	Heat curve, see manual for more information	48488	48488	48488	48488	48488	48488	48488	48488		48488	48488	48488		s8	1	0	15	9	R/W
48489	Heat Curve S5	Heat curve, see manual for more information	48489	48489	48489	48489	48489	48489	48489	48489		48489	48489	48489		s8	1	0	15	9	R/W
48491	Heat Offset S8	Offset of the heat curve, see manual for more information	48491	48491	48491	48491	48491	48491	48491	48491		48491	48491	48491		s8	1	-10	10	0	R/W
48492	Heat Offset S7	Offset of the heat curve, see manual for more information	48492	48492	48492	48492	48492	48492	48492	48492		48492	48492	48492		s8	1	-10	10	0	R/W
48493	Heat Offset S6	Offset of the heat curve, see manual for more information	48493	48493	48493	48493	48493	48493	48493	48493		48493	48493	48493		s8	1	-10	10	0	R/W
48494	Heat Offset S5	Offset of the heat curve, see manual for more information	48494	48494	48494	48494	48494	48494	48494	48494		48494	48494	48494		s8	1	-10	10	0	R/W
48495	Min Supply System 8		48495	48495	48495	48495	48495	48495	48495	48495		48495	48495	48495	°C	s16	10	50	700	200	R/W
48496	Min Supply System 7		48496	48496	48496	48496	48496	48496	48496	48496		48496	48496	48496	°C	s16	10	50	700	200	R/W
48497	Min Supply System 6		48497	48497	48497	48497	48497	48497	48497	48497		48497	48497	48497	°C	s16	10	50	700	200	R/W
48498	Min Supply System 5		48498	48498	48498	48498	48498	48498	48498	48498		48498	48498	48498	°C	s16	10	50	700	200	R/W
48499	Max Supply System 8		48499	48499	48499	48499	48499	48499	48499	48499		48499	48499	48499	°C	s16	10	50	800	600	R/W
48500	Max Supply System 7		48500	48500	48500	48500	48500	48500	48500	48500		48500	48500	48500	°C	s16	10	50	800	600	R/W
48501	Max Supply System 6		48501	48501	48501	48501	48501	48501	48501	48501		48501	48501	48501	°C	s16	10	50	800	600	R/W
48502	Max Supply System 5		48502	48502	48502	48502	48502	48502	48502	48502		48502	48502	48502	°C	s16	10	50	800	600	R/W
48503	External adjustment S8	Change of the offset of the heat curve when closing the external adjustment input	48503	48503	48503	48503	48503	48503	48503	48503		48503	48503	48503		s8	1	-10	10	0	R/W
48504	External adjustment S7	Change of the offset of the heat curve when closing the external adjustment input	48504	48504	48504	48504	48504	48504	48504	48504		48504	48504	48504		s8	1	-10	10	0	R/W
48505	External adjustment S6	Change of the offset of the heat curve when closing the external adjustment input	48505	48505	48505	48505	48505	48505	48505	48505		48505	48505	48505		s8	1	-10	10	0	R/W
48506	External adjustment S5	Change of the offset of the heat curve when closing the external adjustment input	48506	48506	48506	48506	48506	48506	48506	48506		48506	48506	48506		s8	1	-10	10	0	R/W
48507	External adjustment with room sensor S8	Room temperature setting when closing the external adjustment input	48507	48507	48507	48507	48507	48507	48507	48507		48507	48507	48507	°C	s16	10	50	300	200	R/W
48508	External adjustment with room sensor S7	Room temperature setting when closing the external adjustment input	48508	48508	48508	48508	48508	48508	48508	48508		48508	48508	48508	°C	s16	10	50	300	200	R/W
48509	External adjustment with room sensor S6	Room temperature setting when closing the external adjustment input	48509	48509	48509	48509	48509	48509	48509	48509		48509	48509	48509	°C	s16	10	50	300	200	R/W
48510	External adjustment with room sensor S5	Room temperature setting when closing the external adjustment input	48510	48510	48510	48510	48510	48510	48510	48510		48510	48510	48510	°C	s16	10	50	300	200	R/W
48567	Initiate inverter	Start initiation process of the inverter			48567											u8	1	0	0	0	R/W
48568	Force inverter init	Force inverter initiation process of the inverter			48568											u8	1	0	0	0	R/W
48569	Climate system 5 accessory	Activates the climate system 5 accessory	48569	48569	48569	48569	48569	48569	48569	48569		48569	48569	48569		u8	1	0	1	0	R/W
48570	Climate system 6 accessory	Activates the climate system 6 accessory	48570	48570	48570	48570	48570	48570	48570	48570		48570	48570	48570		u8	1	0	1	0	R/W
48571	Climate system 7 accessory	Activates the climate system 7 accessory	48571	48571	48571	48571	48571	48571	48571	48571		48571	48571	48571		u8	1	0	1	0	R/W
48572	Climate system 8 accessory	Activates the climate system 8 accessory	48572	48572	48572	48572	48572	48572	48572	48572		48572	48572	48572		u8	1	0	1	0	R/W
48573	Climate system 8 mixing valve amp.	Mixing valve amplification for extra climate systems	48573	48573	48573	48573	48573	48573	48573	48573		48573	48573	48573		s8	10	1	100	10	R/W
48574	Climate system 7 mixing valve amp.	Mixing valve amplification for extra climate systems	48574	48574	48574	48574	48574	48574	48574	48574		48574	48574	48574		s8	10	1	100	10	R/W
48575	Climate system 6 mixing valve amp.	Mixing valve amplification for extra climate systems	48575	48575	48575	48575	48575	48575	48575	48575		48575	48575	48575		s8	10	1	100	10	R/W
48576	Climate system 5 mixing valve amp.	Mixing valve amplification for extra climate systems	48576	48576	48576	48576	48576	48576	48576	48576		48576	48576	48576		s8	10	1	100	10	R/W
48577	Climate system 8 shunt wait	Wait time between changes of the shunt in extra climate systems	48577	48577	48577	48577	48577	48577	48577	48577		48577	48577	48577	secs	s16	10	10	300	30	R/W
48578	Climate system 7 shunt wait	Wait time between changes of the shunt in extra climate systems	48578	48578	48578	48578	48578	48578	48578	48578		48578	48578	48578	secs	s16	10	10	300	30	R/W
48579	Climate system 6 shunt wait	Wait time between changes of the shunt in extra climate systems	48579	48579	48579	48579	48579	48579	48579	48579		48579	48579	48579	secs	s16	10	10	300	30	R/W
48580	Climate system 5 shunt wait	Wait time between changes of the shunt in extra climate systems	48580	48580	48580	48580	48580	48580	48580	48580		48580	48580	48580	secs	s16	10	10	300	30	R/W
48581	Min cooling supply temp S8	Minimum allowed supply temperature during cooling					48581	48581	48581	48581		48581	48581	48581	°C	s8	1	-5	30	18	R/W
48582	Min cooling supply temp S7	Minimum allowed supply temperature during cooling					48582	48582	48582	48582		48582	48582	48582	°C	s8	1	-5	30	18	R/W
48583	Min cooling supply temp S6	Minimum allowed supply temperature during cooling					48583	48583	48583	48583		48583	48583	48583	°C	s8	1	-5	30	18	R/W
48584	Min cooling supply temp S5	Minimum allowed supply temperature during cooling					48584	48584	48584	48584		48584	48584	48584	°C	s8	1	-5	30	18	R/W
48593	Cooling use mix. valve S8	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48593	48593	48593	48593		48593	48593	48593		u8	1	0	1	0	R/W
48594	Cooling use mix. valve S7	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48594	48594	48594	48594		48594	48594	48594		u8	1	0	1	0	R/W
48595	Cooling use mix. valve S6	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48595	48595	48595	48595		48595	48595	48595		u8	1	0	1	0	R/W
48596	Cooling use mix. valve S5	Sets if the valve should be used or not in cooling mode. Only applies if cooling is available in the system					48596	48596	48596	48596		48596	48596	48596		u8	1	0	1	0	R/W
48597	Heating use mix. valve S8	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48597	48597	48597	48597		48597	48597	48597		u8	1	0	1	1	R/W
48598	Heating use mix. valve S7	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48598	48598	48598	48598		48598	48598	48598		u8	1	0	1	1	R/W
48599	Heating use mix. valve S6	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48599	48599	48599	48599		48599	48599	48599		u8	1	0	1	1	R/W
48600	Heating use mix. valve S5	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48600	48600	48600	48600		48600	48600	48600		u8	1	0	1	1	R/W
48601	Heating use mix. valve S4	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48601	48601	48601	48601		48601	48601	48601		u8	1	0	1	1	R/W
48602	Heating use mix. valve S3	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48602	48602	48602	48602		48602	48602	48602		u8	1	0	1	1	R/W
48603	Heating use mix. valve S2	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48603	48603	48603	48603		48603	48603	48603		u8	1	0	1	1	R/W
48604	Heating use mix. valve S1	Sets if the valve should be used or not in heating mode. Only applies if cooling is available in the system. Otherwise the valve is always used in heating mode.					48604	48604	48604	48604	48604	48604	48604	48604		u8	1	0	1	1	R/W
48607	ERS 1 accessory	Activates the ERS accessory					48607	48607	48607	48607		48607	48607	48607		u8	1	0	1	0	R/W
48637	AHPS docking accessory	0=not activated, 1=activated			48637											u8	1	0	1	0	R/W
48638	AHPS docking: solar heating	The specific AHPS docking: 0=not activated, 1=activated			48638											u8	1	0	1	0	R/W
48639	AHPS docking: prioritized add.	The specific AHPS docking: 0=not activated, 1=activated			48639											u8	1	0	1	0	R/W
48640	AHPS docking: ext. addition	The specific AHPS docking: 0=not activated, 1=activated			48640											u8	1	0	1	0	R/W
48641	AHPS docking: ext. hot water	The specific AHPS docking: 0=not activated, 1=activated			48641											u8	1	0	1	0	R/W
48647	EB103/104-GP12	Activates the EB103/104-GP12 Accessory.										48647				u8	1	0	1	0	R/W
48648	EB105/106-GP12	Activates the EB105/106-GP12 Accessory.										48648				u8	1	0	1	0	R/W
48649	EB107/108-GP12	Activates the EB107/108-GP12 Accessory.										48649				u8	1	0	1	0	R/W
48659	Cut off frequency activated 2	Cut off frequency activated			48659	48659	48659									s8	1	0	1	0	R/W
48660	Cut off frequency activated 1	Cut off frequency activated			48660	48660	48660									s8	1	0	1	0	R/W
48661	Cut off frequency start 2	Cut off frequency start			48661	48661	48661								Hz	u8	1	17	115	17	R/W
48662	Cut off frequency start 1	Cut off frequency start			48662	48662	48662								Hz	u8	1	17	115	17	R/W
48663	Cut off frequency stop 2	Cut off frequency stop			48663	48663	48663								Hz	u8	1	22	120	22	R/W
48664	Cut off frequency stop 1	Cut off frequency stop			48664	48664	48664								Hz	u8	1	22	120	22	R/W
48675	Use room sensor S8	When activated the system uses the room sensor	48675	48675	48675	48675	48675	48675	48675	48675		48675	48675	48675		u8	1	0	1	0	R/W
48676	Use room sensor S7	When activated the system uses the room sensor	48676	48676	48676	48676	48676	48676	48676	48676		48676	48676	48676		u8	1	0	1	0	R/W
48677	Use room sensor S6	When activated the system uses the room sensor	48677	48677	48677	48677	48677	48677	48677	48677		48677	48677	48677		u8	1	0	1	0	R/W
48678	Use room sensor S5	When activated the system uses the room sensor	48678	48678	48678	48678	48678	48678	48678	48678		48678	48678	48678		u8	1	0	1	0	R/W
48680	Room sensor setpoint S8	Sets the room temperature setpoint for the system	48680	48680	48680	48680	48680	48680	48680	48680		48680	48680	48680	°C	s16	10	50	300	200	R/W
48681	Room sensor setpoint S7	Sets the room temperature setpoint for the system	48681	48681	48681	48681	48681	48681	48681	48681		48681	48681	48681	°C	s16	10	50	300	200	R/W
48682	Room sensor setpoint S6	Sets the room temperature setpoint for the system	48682	48682	48682	48682	48682	48682	48682	48682		48682	48682	48682	°C	s16	10	50	300	200	R/W
48683	Room sensor setpoint S5	Sets the room temperature setpoint for the system	48683	48683	48683	48683	48683	48683	48683	48683		48683	48683	48683	°C	s16	10	50	300	200	R/W
48685	Room sensor factor S8	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	48685	48685	48685	48685	48685	48685	48685	48685		48685	48685	48685		u8	10	0	60	10	R/W
48686	Room sensor factor S7	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	48686	48686	48686	48686	48686	48686	48686	48686		48686	48686	48686		u8	10	0	60	10	R/W
48687	Room sensor factor S6	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	48687	48687	48687	48687	48687	48687	48687	48687		48687	48687	48687		u8	10	0	60	10	R/W
48688	Room sensor factor S5	Setting of how much the difference between set and actual room temperature should affect the supply temperature.	48688	48688	48688	48688	48688	48688	48688	48688		48688	48688	48688		u8	10	0	60	10	R/W
48724	Cool curve S8	Cool curve, see manual for more information					48724	48724	48724	48724		48724	48724	48724		s8	1	0	9	0	R/W
48725	Cool curve S7	Cool curve, see manual for more information					48725	48725	48725	48725		48725	48725	48725		s8	1	0	9	0	R/W
48726	Cool curve S6	Cool curve, see manual for more information					48726	48726	48726	48726		48726	48726	48726		s8	1	0	9	0	R/W
48727	Cool curve S5	Cool curve, see manual for more information					48727	48727	48727	48727		48727	48727	48727		s8	1	0	9	0	R/W
48728	Cool curve S4	Cool curve, see manual for more information					48728	48728	48728	48728		48728	48728	48728		s8	1	0	9	0	R/W
48729	Cool curve S3	Cool curve, see manual for more information					48729	48729	48729	48729		48729	48729	48729		s8	1	0	9	0	R/W
48730	Cool curve S2	Cool curve, see manual for more information					48730	48730	48730	48730		48730	48730	48730		s8	1	0	9	0	R/W
48731	Cool curve S1	Cool curve, see manual for more information					48731	48731	48731	48731	48731	48731	48731	48731		s8	1	0	9	0	R/W
48732	Cool offset S8	Offset of the cool curve, see manual for more information 	48732	48732	48732	48732	48732	48732	48732	48732	48732	48732	48732	48732	 	s8	1	-10	10	0	R/W
48733	Cool offset S7	Offset of the cool curve, see manual for more information 	48733	48733	48733	48733	48733	48733	48733	48733	48733	48733	48733	48733	 	s8	1	-10	10	0	R/W
48734	Cool offset S6	Offset of the cool curve, see manual for more information 	48734	48734	48734	48734	48734	48734	48734	48734	48734	48734	48734	48734	 	s8	1	-10	10	0	R/W
48735	Cool offset S5	Offset of the cool curve, see manual for more information 	48735	48735	48735	48735	48735	48735	48735	48735	48735	48735	48735	48735	 	s8	1	-10	10	0	R/W
48736	Cool offset S4	Offset of the cool curve, see manual for more information 	48736	48736	48736	48736	48736	48736	48736	48736	48736	48736	48736	48736	 	s8	1	-10	10	0	R/W
48737	Cool offset S3	Offset of the cool curve, see manual for more information 	48737	48737	48737	48737	48737	48737	48737	48737	48737	48737	48737	48737	 	s8	1	-10	10	0	R/W
48738	Cool offset S2	Offset of the cool curve, see manual for more information 	48738	48738	48738	48738	48738	48738	48738	48738	48738	48738	48738	48738	 	s8	1	-10	10	0	R/W
48739	Cool offset S1	Offset of the cool curve, see manual for more information 	48739	48739	48739	48739	48739	48739	48739	48739	48739	48739	48739	48739	 	s8	1	-10	10	0	R/W
48740	Own Cooling Curve P4	User defined cooling curve point					48740	48740	48740	48740	48740	48740	48740	48740	°C	s8	1	-5	40	20	R/W
48741	Own Cooling Curve P2	User defined cooling curve point					48741	48741	48741	48741	48741	48741	48741	48741	°C	s8	1	-5	40	20	R/W
48742	Own Cooling Curve P1	User defined cooling curve point					48742	48742	48742	48742	48742	48742	48742	48742	°C	s8	1	-5	40	20	R/W
48743	Hot water high power mode				48743	48743	48743		48743		48743	48743	48743	48743		s8	1	0	1	0	R/W
48755	Transformer ratio	Ratio of the current measurement transformers	48755	48755	48755	48755	48755	48755	48755	48755		48755	48755	48755		u16	1	300	2500	300	R/W
48778	Room sensor cool setpoint S8	Sets the room temperature setpoint for the system in cooling mode					48778	48778	48778	48778		48778	48778	48778	°C	s16	10	50	350	250	R/W
48779	Room sensor cool setpoint S7	Sets the room temperature setpoint for the system in cooling mode					48779	48779	48779	48779		48779	48779	48779	°C	s16	10	50	350	250	R/W
48780	Room sensor cool setpoint S6	Sets the room temperature setpoint for the system in cooling mode					48780	48780	48780	48780		48780	48780	48780	°C	s16	10	50	350	250	R/W
48781	Room sensor cool setpoint S5	Sets the room temperature setpoint for the system in cooling mode					48781	48781	48781	48781		48781	48781	48781	°C	s16	10	50	350	250	R/W
48782	Room sensor cool setpoint S4	Sets the room temperature setpoint for the system in cooling mode					48782	48782	48782	48782		48782	48782	48782	°C	s16	10	50	350	250	R/W
48783	Room sensor cool setpoint S3	Sets the room temperature setpoint for the system in cooling mode					48783	48783	48783	48783		48783	48783	48783	°C	s16	10	50	350	250	R/W
48784	Room sensor cool setpoint S2	Sets the room temperature setpoint for the system in cooling mode					48784	48784	48784	48784		48784	48784	48784	°C	s16	10	50	350	250	R/W
48785	Room sensor cool setpoint S1	Sets the room temperature setpoint for the system in cooling mode					48785	48785	48785	48785	48785	48785	48785	48785	°C	s16	10	50	350	250	R/W
48786	Room sensor cool factor S8	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48786	48786	48786	48786		48786	48786	48786		u8	10	0	60	10	R/W
48787	Room sensor cool factor S7	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48787	48787	48787	48787		48787	48787	48787		u8	10	0	60	10	R/W
48788	Room sensor cool factor S6	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48788	48788	48788	48788		48788	48788	48788		u8	10	0	60	10	R/W
48789	Room sensor cool factor S5	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48789	48789	48789	48789		48789	48789	48789		u8	10	0	60	10	R/W
48790	Room sensor cool factor S4	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48790	48790	48790	48790		48790	48790	48790		u8	10	0	60	10	R/W
48791	Room sensor cool factor S3	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48791	48791	48791	48791		48791	48791	48791		u8	10	0	60	10	R/W
48792	Room sensor cool factor S2	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48792	48792	48792	48792		48792	48792	48792		u8	10	0	60	10	R/W
48793	Room sensor cool factor S1	Setting of how much the difference between set and actual room temperature should affect the supply temperature in cooling mode.					48793	48793	48793	48793	48793	48793	48793	48793		u8	10	0	60	10	R/W
48794	RH set value	RH set value	48794	48794	48794	48794	48794	48794	48794	48794	48794	48794	48794	48794	%	s8	1	30	90	60	R/W
48808	HTS accessory	HTS accessory					48808	48808	48808	48808		48808	48808	48808		u8	1	0	1	0	R/W
48810	Prevent humidity S8 	 	48810	48810	48810	48810	48810	48810	48810	48810	48810	48810	48810	48810	 	s8	1	0	1	0	R/W
48811	Prevent humidity S7	 	48811	48811	48811	48811	48811	48811	48811	48811	48811	48811	48811	48811	 	s8	1	0	1	0	R/W
48812	Prevent humidity S6	 	48812	48812	48812	48812	48812	48812	48812	48812	48812	48812	48812	48812	 	s8	1	0	1	0	R/W
48813	Prevent humidity S5	 	48813	48813	48813	48813	48813	48813	48813	48813	48813	48813	48813	48813	 	s8	1	0	1	0	R/W
48814	Prevent humidity S4	 	48814	48814	48814	48814	48814	48814	48814	48814	48814	48814	48814	48814	 	s8	1	0	1	0	R/W
48815	Prevent humidity S3	 	48815	48815	48815	48815	48815	48815	48815	48815	48815	48815	48815	48815	 	s8	1	0	1	0	R/W
48816	Prevent humidity S2	 	48816	48816	48816	48816	48816	48816	48816	48816	48816	48816	48816	48816	 	s8	1	0	1	0	R/W
48817	Prevent humidity S1	 	48817	48817	48817	48817	48817	48817	48817	48817	48817	48817	48817	48817	 	s8	1	0	1	0	R/W
48819	Limit humidity in room, heating S8	Limit humidity in room, heating					48819	48819	48819	48819		48819	48819	48819		s8	1	0	1	0	R/W
48820	Limit humidity in room, heating S7	Limit humidity in room, heating					48820	48820	48820	48820		48820	48820	48820		s8	1	0	1	0	R/W
48821	Limit humidity in room, heating S6	Limit humidity in room, heating					48821	48821	48821	48821		48821	48821	48821		s8	1	0	1	0	R/W
48822	Limit humidity in room, heating S5	Limit humidity in room, heating					48822	48822	48822	48822		48822	48822	48822		s8	1	0	1	0	R/W
48823	Limit humidity in room, heating S4	Limit humidity in room, heating					48823	48823	48823	48823		48823	48823	48823		s8	1	0	1	0	R/W
48824	Limit humidity in room, heating S3	Limit humidity in room, heating					48824	48824	48824	48824		48824	48824	48824		s8	1	0	1	0	R/W
48825	Limit humidity in room, heating S2	Limit humidity in room, heating					48825	48825	48825	48825		48825	48825	48825		s8	1	0	1	0	R/W
48826	Limit humidity in room, heating S1	Limit humidity in room, heating					48826	48826	48826	48826		48826	48826	48826		s8	1	0	1	0	R/W
48828	OPT	Activates the OPT Accessory.					48828	48828	48828	48828		48828	48828	48828		u8	1	0	1	0	R/W
48829	OPT DM startdiff	The number of degree minutes below the last compressor the OPT is allowed to start					48829	48829	48829	48829		48829	48829	48829		s16	1	10	2000	700	R/W
48849	Speed brine pump active cooling						48849	48849	48849	48849					%	u8	1	0	100	75	R/W
48850	Delta brine pump active cooling						48850	48850	48850	48850					°C	u8	1	2	10	5	R/W
48851	Waiting speed brine pump cooling						48851	48851	48851	48851					%	u8	1	0	100	30	R/W
48852	Modbus40 Word Swap	"If set; swapping the words in 32-bit variables when value requested via ''read holding register'' commando."	48852	48852	48852		48852	48852	48852	48852		48852	48852	48852		u8	1	0	1	1	R/W
48853	ERS 1 Exhaust Fan speed 4						48853	48853	48853	48853		48853	48853	48853	%	u8	1	0	100	100	R/W
48854	ERS 1 Exhaust Fan speed 3						48854	48854	48854	48854		48854	48854	48854	%	u8	1	0	100	80	R/W
48855	ERS 1 Exhaust Fan speed 2						48855	48855	48855	48855		48855	48855	48855	%	u8	1	0	100	30	R/W
48856	ERS 1 Exhaust Fan speed 1						48856	48856	48856	48856		48856	48856	48856	%	u8	1	0	100	0	R/W
48857	ERS 1 Exhaust Fan speed normal						48857	48857	48857	48857		48857	48857	48857	%	u8	1	1	100	75	R/W
48858	ACS Thermostat accessory	Activate the ACS thermostat accessory						48858	48858	48858						u8	1	0	1	0	R/W
48859	Filter time BT64 	ACS thermostate BT64 filter time						48859	48859	48859					min	u8	1	5	30	5	R/W
48860	ACS-therm, Hyst between cpr	ACS thermosate, Hysteresis between cpr						48860	48860	48860					°C	s8	1	1	10	2	R/W
48861	ACS-therm start temp.	ACS thermostate start temp.						48861	48861	48861					°C	s8	1	-8	30	10	R/W
48862	temp, shift to borehole	ACS thermostate temperature to shift to borehole						48862	48862	48862					°C	s8	1	-8	30	0	R/W
48889	MODBUS40 Disable LOG.SET	If set, the system will ignore the existing LOG.SET on the USB stick.1=ignore LOG.SET,0=use LOG.SET	48889	48889	48889		48889	48889	48889	48889		48889	48889	48889		u8	1	0	1	0	R/W
48890	Outdoor Air Fan Speed					48890									%	u8	1	10	100	100	R/W
48891	Setting up ventilation	Setting up ventilation for normal speed.			48891	48891										u8	1	0	0	0	R/W
48892	Setting up ventilation, OA mixing	Setting up ventilation for outdoor air mixing when used.				48892										u8	1	0	0	0	R/W
48893	F135 Heat pump	0=not activated, 1=activated										48893	48893	48893		u8	1	0	1	0	R/W
48894	F135 Pump Speed											48894	48894	48894	%	u8	1	1	100	70	R/W
48895	F135 HW-Cool	If activated, F135 will take care of all the hot water need when cooling is running										48895	48895	48895		u8	1	0	1	0	R/W
48896	ERS 1 Supply Fan speed 4						48896	48896	48896	48896		48896	48896	48896	%	u8	1	0	100	100	R/W
48897	ERS 1 Supply Fan speed 3						48897	48897	48897	48897		48897	48897	48897	%	u8	1	0	100	80	R/W
48898	ERS 1 Supply Fan speed 2						48898	48898	48898	48898		48898	48898	48898	%	u8	1	0	100	30	R/W
48899	ERS 1 Supply Fan speed 1						48899	48899	48899	48899		48899	48899	48899	%	u8	1	0	100	0	R/W
48900	ERS 1 Supply Fan speed normal						48900	48900	48900	48900		48900	48900	48900	%	u8	1	1	100	75	R/W
48901	External ERS 1 accessory min exhaust temp.						48901	48901	48901	48901		48901	48901	48901	°C	u8	1	0	10	5	R/W
48902	External ERS 1 accessory bypass temp.						48902	48902	48902	48902		48902	48902	48902	°C	u8	1	2	10	4	R/W
48904	Pool Pump Type												48904	48904		u8	1	0	1	0	R/W
48905	External cooling accessory Pump Type											48905	48905	48905		u8	1	0	1	0	R/W
48908	Energy Meter Factor X23	Energy meter factor X23, energy per pulse			48908	48908	48908	48908	48908	48908		48908	48908	48908	Wh	u16	1	1	10000	1000	R/W
48909	Energy Meter Factor X22	Energy meter factor X22, energy per pulse			48909	48909	48909	48909	48909	48909		48909	48909	48909	Wh	u16	1	1	10000	1000	R/W
48910	Energy Meter X23	Activates the external energy meter			48910	48910	48910	48910	48910	48910		48910	48910	48910		u8	1	0	1	0	R/W
48911	Energy Meter X22	Activates the external energy meter			48911	48911	48911	48911	48911	48911		48911	48911	48911		u8	1	0	1	0	R/W
48914	Max int add. power, SG Ready				48914	48914							48914	48914	kW	s16	100	0	4500	650	R/W
48915	Real air flow	Externally measured air flow during ventilation adjustments.			48915	48915										s16	1	70	400	-32768	R/W
48918	Limit humidity in room, cooling S8	Limit humidity in room, cooling					48918	48918	48918	48918		48918	48918	48918		s8	1	0	0	0	R/W
48919	Limit humidity in room, cooling S7	Limit humidity in room, cooling					48919	48919	48919	48919		48919	48919	48919		s8	1	0	0	0	R/W
48920	Limit humidity in room, cooling S6	Limit humidity in room, cooling					48920	48920	48920	48920		48920	48920	48920		s8	1	0	0	0	R/W
48921	Limit humidity in room, cooling S5	Limit humidity in room, cooling					48921	48921	48921	48921		48921	48921	48921		s8	1	0	0	0	R/W
48922	Limit humidity in room, cooling S4	Limit humidity in room, cooling					48922	48922	48922	48922		48922	48922	48922		s8	1	0	0	0	R/W
48923	Limit humidity in room, cooling S3	Limit humidity in room, cooling					48923	48923	48923	48923		48923	48923	48923		s8	1	0	0	0	R/W
48924	Limit humidity in room, cooling S2	Limit humidity in room, cooling					48924	48924	48924	48924		48924	48924	48924		s8	1	0	0	0	R/W
48925	Limit humidity in room, cooling S1	Limit humidity in room, cooling					48925	48925	48925	48925		48925	48925	48925		s8	1	0	0	0	R/W
48926	Humidity factor	Setting of how much the difference between set and actual room humidity should affect the supply temperature.	48926	48926	48926	48926	48926	48926	48926	48926	48926	48926	48926	48926		u8	10	5	100	10	R/W
48927	Humidity cool factor	Setting of how much the difference between set and actual room humidity should affect the supply temperature in cooling mode.	48927	48927	48927	48927	48927	48927	48927	48927	48927	48927	48927	48927		u8	10	0	0	0	R/W
48928	OPT Hystereses	The hystereses in OPT system					48928	48928	48928	48928		48928	48928	48928		s16	1	10	2000	100	R/W
48930	EME10 Activated	0=not activated, 1=activated	48930	48930	48930	48930	48930	48930								u8	1	0	1	0	R/W
48931	EME PV Panel Affect Heating	0=not affecting, 1=affecting	48931	48931	48931	48931	48931	48931	48931	48931	48931	48931	48931	48931		u8	1	0	1	0	R/W
48932	EME PV Panel Affect Hot Water	0=not affecting, 1=affecting	48932	48932	48932	48932	48932	48932	48932	48932	48932	48932	48932	48932		u8	1	0	1	0	R/W
48944	 Low brine out temp.EP15								48944	48944					°C	s16	10	-120	150	-80	R/W
48947	Outdoor Air Fan Speed, high temp.					48947									%	u8	1	0	100	35	R/W
48948	FLM pump 4	Operating mode for the FLM pump 4					48948	48948	48948	48948						u8	1	0	1	0	R/W
48949	FLM pump 3	Operating mode for the FLM pump 3					48949	48949	48949	48949						u8	1	0	1	0	R/W
48950	FLM pump 2	Operating mode for the FLM pump 2					48950	48950	48950	48950						u8	1	0	1	0	R/W
48951	FLM 4 defrost	Minimum time between defrost in FLM 4					48951	48951	48951	48951					hrs	u8	1	1	30	10	R/W
48952	FLM 3 defrost	Minimum time between defrost in FLM 3					48952	48952	48952	48952					hrs	u8	1	1	30	10	R/W
48953	FLM 2 defrost	Minimum time between defrost in FLM 2					48953	48953	48953	48953					hrs	u8	1	1	30	10	R/W
48954	FLM 4 cooling	FLM 4 cooling activated					48954	48954	48954	48954						u8	1	0	1	0	R/W
48955	FLM 3 cooling	FLM 3 cooling activated					48955	48955	48955	48955						u8	1	0	1	0	R/W
48956	FLM 2 cooling	FLM 2 cooling activated					48956	48956	48956	48956						u8	1	0	1	0	R/W
48957	FLM 4 pump speed	FLM 4 pump speed					48957	48957	48957	48957						u8	1	1	100	100	R/W
48958	FLM 3 pump speed	FLM 3 pump speed					48958	48958	48958	48958						u8	1	1	100	100	R/W
48959	FLM 2 pump speed	FLM 2 pump speed					48959	48959	48959	48959						u8	1	1	100	100	R/W
48960	FLM 1 pump speed	FLM 1 pump speed					48960	48960	48960	48960						u8	1	1	100	100	R/W
48961	FLM 4 over temp	Over temp for cooling active, when using FLM cooling					48961	48961	48961	48961					°C	u8	10	10	100	30	R/W
48962	FLM 3 over temp	Over temp for cooling active, when using FLM cooling					48962	48962	48962	48962					°C	u8	10	10	100	30	R/W
48963	FLM 2 over temp	Over temp for cooling active, when using FLM cooling					48963	48963	48963	48963					°C	u8	10	10	100	30	R/W
48964	FLM 1 over temp	Over temp for cooling active, when using FLM cooling					48964	48964	48964	48964					°C	u8	10	10	100	30	R/W
48965	FLM 4 set point, cooling	Set point, cooling, when using FLM cooling					48965	48965	48965	48965					°C	s16	10	50	400	210	R/W
48966	FLM 3 set point, cooling	Set point, cooling, when using FLM cooling					48966	48966	48966	48966					°C	s16	10	50	400	210	R/W
48967	FLM 2 set point, cooling	Set point, cooling, when using FLM cooling					48967	48967	48967	48967					°C	s16	10	50	400	210	R/W
48968	FLM 1 set point, cooling	Set point, cooling, when using FLM cooling	48968	48968	48968	48968	48968	48968	48968	48968	48968	48968	48968	48968	°C	s16	10	50	400	210	R/W
48969	AUX block OPT	AUX block OPT			48969		48969	48969	48969	48969		48969	48969	48969		u8	1	0	0	0	R/W
48970	Outdoor Air Mixing function	Activates the Outdoor Air Mixing function.	48970	48970	48970	48970	48970	48970	48970	48970	48970	48970	48970	48970		u8	1	0	1	0	R/W
48971	Outdoor air max. temp.	Maximum outdoor air temperature set.				48971										s8	1	0	40	10	R/W
48972	Outdoor air min. temp.	Minimum outdoor air temperature set.			48972	48972										s8	1	-10	10	-5	R/W
48973	Reduced ventilation	Outdoor air reduced ventilation. 0 = deactivated, 1 = activated.			48973	48973										u8	1	0	1	0	R/W
48974	High outdoor air temperature	Above this limit the ventilation is reduced.				48974									°C	s16	1	20	50	25	R/W
48975	OEK accessory	Activates the OEK Accessory.			48975	48975										u8	1	0	1	0	R/W
48976	Smart home room control		48976	48976	48976	48976	48976	48976	48976	48976	48976	48976	48976	48976		u8	1	0	1	0	R/W
48977	Speed brine pump wait mode 						48977	48977	48977	48977					%	u8	1	0	100	30	R/W
48979	Smart energy source	Smart energy source activated.					48979	48979	48979	48979		48979	48979	48979		u8	1	0	1	0	R/W
48980	Smart energy source, ctrl method	Smart energy source, ctrl method. 0 = price. 1 = primary factor.					48980	48980	48980	48980		48980	48980	48980		u8	1	0	1	0	R/W
48981	Smart energy source, electricity price source	Smart energy source, electricity price source. 0 = fixed price. 1 = tariff. 2= spot price.					48981	48981	48981	48981		48981	48981	48981		u8	1	0	2	0	R/W
48982	Smart energy source, electricity price	Smart energy source, electricity fixed price.					48982	48982	48982	48982		48982	48982	48982		u16	1	0	10000	100	R/W
48983	Smart energy source, fixed elec. price from	Smart energy source, fixed electricity price part source, if spot electricity price are used. 0 = fixed price. 1 = tariff.					48983	48983	48983	48983		48983	48983	48983		u8	1	0	1	0	R/W
48984	Smart energy source, fixed part electricity price	Smart energy source, fixed part (if spot price are used) electricity price					48984	48984	48984	48984		48984	48984	48984		u16	1	0	10000	100	R/W
48985	Smart energy source, shunt add price source	Smart energy source, shunted addition price part source. From tariff or fixed price. 0 = fixed price. 1 = tariff.					48985	48985	48985	48985		48985	48985	48985		u8	1	0	1	0	R/W
48986	Smart energy source, shunt add price	Smart energy source, shunted add price					48986	48986	48986	48986		48986	48986	48986		u16	1	0	10000	100	R/W
48987	Smart energy source, ext step add price from	Smart energy source, external step add source. From tariff or fixed price. 0 = fixed price. 1 = tariff.					48987	48987	48987	48987		48987	48987	48987		u8	1	0	1	0	R/W
48988	Smart energy source, ext step add price	Smart energy source, ext step add price					48988	48988	48988	48988		48988	48988	48988		u16	1	0	10000	100	R/W
48989	Smart energy source, OPT10 price source	Smart energy source, OPT10 addition price source. 0 = fixed price. 1 = tariff.					48989	48989	48989	48989		48989	48989	48989		u8	1	0	1	0	R/W
48990	Smart energy source, OPT10 price	Smart energy source, OPT10 addition price.					48990	48990	48990	48990		48990	48990	48990		u16	1	0	10000	100	R/W
48991	Smart energy source, primary factor elec.	Smart energy source, primary factor electricity					48991	48991	48991	48991		48991	48991	48991		u8	10	0	50	25	R/W
48992	Smart energy source, primary factor shunted add.	Smart energy source, primary factor shunted addition					48992	48992	48992	48992		48992	48992	48992		u8	10	0	50	10	R/W
48993	Smart energy source, primary factor ext step add	Smart energy source, primary factor external step addition					48993	48993	48993	48993		48993	48993	48993		u8	10	0	50	10	R/W
48994	Smart energy source, primary factor OPT10 add.	Smart energy source, primary factor OPT10 addition					48994	48994	48994	48994		48994	48994	48994		u8	10	0	50	10	R/W
48995	Smart energy source, OPT10 high tariff price	Smart energy source, OPT10 addition high tariff price					48995	48995	48995	48995		48995	48995	48995		u16	1	1	10000	100	R/W
48996	Smart energy source, OPT10 low tariff price	Smart energy source, OPT10 addition low tariff price					48996	48996	48996	48996		48996	48996	48996		u16	1	1	10000	100	R/W
48997	Smart energy source, ext step add high tariff price	Smart energy source, external step addition high tariff price					48997	48997	48997	48997		48997	48997	48997		u16	1	1	10000	100	R/W
48998	Smart energy source, ext step add low tariff price	Smart energy source, external step addition low tariff price					48998	48998	48998	48998		48998	48998	48998		u16	1	1	10000	100	R/W
48999	Smart energy source, shunt add high tariff price	Smart energy source, shunt addition high tariff price					48999	48999	48999	48999		48999	48999	48999		u16	1	1	10000	100	R/W
49000	Smart energy source, shunt add low tariff price	Smart energy source, shunt addition low tariff price					49000	49000	49000	49000		49000	49000	49000		u16	1	1	10000	100	R/W
49001	Smart energy source, fixed elec. high tariff price	Smart energy source, fixed electricity part high tariff price					49001	49001	49001	49001		49001	49001	49001		u16	1	1	10000	100	R/W
49002	Smart energy source, fixed elec. low tariff price	Smart energy source, fixed electricity part low tariff price					49002	49002	49002	49002		49002	49002	49002		u16	1	1	10000	100	R/W
49003	Smart energy source, electricity high tariff price	Smart energy source, electricity high tariff price					49003	49003	49003	49003		49003	49003	49003		u16	1	1	10000	100	R/W
49004	Smart energy source, electricity high low price	Smart energy source, electricity low tariff price					49004	49004	49004	49004		49004	49004	49004		u16	1	1	10000	100	R/W
49005	Smart energy source, DM diff source prio 5	Smart energy source, DM diff source with prio 5					49005	49005	49005	49005		49005	49005	49005		s16	1	100	2000	400	R/W
49006	Smart energy source, DM diff source prio 4	Smart energy source, DM diff source with prio 4					49006	49006	49006	49006		49006	49006	49006		s16	1	100	2000	400	R/W
49007	Smart energy source, DM diff source prio 3	Smart energy source, DM diff source with prio 3					49007	49007	49007	49007		49007	49007	49007		s16	1	100	2000	400	R/W
49008	Smart energy source, DM diff source prio 2	Smart energy source, DM diff source with prio 2					49008	49008	49008	49008		49008	49008	49008		s16	1	100	2000	400	R/W
49009	Smart energy source, DM start source prio 1	Smart energy source, DM start source with prio 1					49009	49009	49009	49009		49009	49009	49009		s16	1	-2000	-10	-60	R/W
49190	Ground water pump temp alarm	Ground water pump temperature alarm					49190	49190	49190	49190						u8	1	0	1	0	R/W
49191	Ground water pump temp alarm level	Ground water pump temperature alarm level					49191	49191	49191	49191					°C	s8	1	-15	20	3	R/W
49192	Fixed delta t, brine pump						49192	49192	49192	49192					°C	u8	1	2	10	4	R/W
49193	Brine pump auto controlled	Brine pump auto controlled, 0= manual, 1 = auto controlled, 2 = fixed delta controlled					49193	49193	49193	49193						s8	1	0	2	1	R/W
49208	Max diff. SES prio 1.												49208	49208	°C	s16	10	10	250	100	R/W
49209	Max diff. SES.other prios												49209	49209	°C	s16	10	10	250	70	R/W
49221	Delta brine pump passive cooling						49221	49221							°C	u8	1	1	15	4	R/W
49223	SCA solar heating	SCA solar heating: 0=not activated, 1=activated			49223	49223										u8	1	0	1	0	R/W
49224	SCA ext. hot water	SCA external hot water: 0=not activated, 1=activated			49224	49224										u8	1	0	1	0	R/W
49225	max add power	max addition power											49225		kW	s16	100	250	2500	2500	R/W
49226	OPT Gas Type	0 = G20/G25, 1 = G31											49226			u8	1	0	1	0	R/W
49227	Block top frequencies	Block compressor top frequencies			49227	49227									Hz	u8	1	0	1	0	R/W
49228	DM start value EP15.	The value the degree minutes needed to be reached for the pump to start heating with EP15							49228							s16	1	-1000	-30	-60	R/W
49229	DM start value EP14	The value the degree minutes needed to be reached for the pump to start heating with EP14							49229							s16	1	-1000	-30	-200	R/W
49230	Internal HW add in tank, use in heat	Internal HW add in tank, use in heat										49230				u8	1	0	1	1	R/W
49232	EB108 Installed							49232	49232	49232		49232				u8	1	0	1	0	R
49233	EB107 Installed							49233	49233	49233		49233				u8	1	0	1	0	R
49234	EB106 Installed							49234	49234	49234		49234				u8	1	0	1	0	R
49235	EB105 Installed							49235	49235	49235		49235				u8	1	0	1	0	R
49236	EB104 Installed							49236	49236	49236		49236				u8	1	0	1	0	R
49237	EB103 Installed							49237	49237	49237		49237				u8	1	0	1	0	R
49238	EB102 Installed							49238	49238	49238		49238				u8	1	0	1	0	R
49239	EB101 Installed						49239	49239	49239	49239	49239	49239	49239	49239		u8	1	0	1	0	R
49241	External ERS 1 accessory bypass set temp.						49241	49241	49241	49241		49241	49241	49241	°C	u8	1	5	30	25	R/W
49242	External ERS 1 accessory bypass at heat						49242	49242	49242	49242		49242	49242	49242		u8	1	0	1	0	R/W
49243	Speed circ.pump HW EP15								49243						%	u8	1	1	100	70	R/W
49244	Speed circ.pump Heat EP15								49244						%	u8	1	1	100	70	R/W
49245	Speed circ.pump Pool EP15								49245						%	u8	1	1	100	70	R/W
49246	Speed Circulation Pump Passive Cooling EP15								49246						%	u8	1	1	100	70	R/W
49247	Speed Circulation Pump Active Cooling EP15								49247						%	u8	1	1	100	70	R/W
49248	Speed brine pump EP15 								49248						%	u8	1	1	100	100	R/W
49249	Speed brine pump passive cooling EP15								49249						%	u8	1	0	100	75	R/W
49250	Speed brine pump active cooling EP15								49250						%	u8	1	0	100	75	R/W
49251	Waiting speed brine pump cooling EP15								49251						%	u8	1	0	100	30	R/W
49252	 Speed brine pump wait mode EP15								49252						%	u8	1	0	100	30	R/W
49277	FLM 4 fan	FLM 4 fan					49277	49277	49277	49277						u8	1	6	6	6	R/W
49278	FLM 3 fan	FLM 3 fan					49278	49278	49278	49278						u8	1	6	6	6	R/W
49279	FLM 2 fan	FLM 2 fan					49279	49279	49279	49279						u8	1	6	6	6	R/W
49280	FLM 1 fan	FLM 1 fan					49280	49280	49280	49280						u8	1	6	6	6	R/W
49281	SAM fan model	SAM fan model			49281											u8	1	6	6	6	R/W
49282	Silent Mode Max Speed				49282	49282									Hz	u8	1	80	120	120	R/W
49285	Energy Meter pulses per kWh X23	Energy meter factor X23, pulses per kWh			49285	49285	49285	49285	49285	49285		49285	49285	49285		u16	1	1	10000	500	R/W
49286	Energy Meter pulses per kWh X22	Energy meter factor X22, pulses per kWh			49286	49286	49286	49286	49286	49286		49286	49286	49286		u16	1	1	10000	500	R/W
49287	Energy Meter mode X23	Energy meter X23 in mode Wh/pulse = 0 or pulses/kWh = 1			49287	49287	49287	49287	49287	49287		49287	49287	49287		u8	1	0	1	0	R/W
49288	Energy Meter mode X22	Energy meter X22 in mode Wh/pulse = 0 or pulses/kWh = 1			49288	49288	49288	49288	49288	49288		49288	49288	49288		u8	1	0	1	0	R/W
49289	Ground water pump speed control 	 	49289	49289	49289	49289	49289	49289	49289	49289	49289	49289	49289	49289	 	s8	1	0	1	0	R/W
49290	Ground water pump auto speed control	Ground water pump auto speed control					49290	49290	49290	49290						s8	1	0	1	1	R/W
49291	Ground water pump manual speed	Ground water pump temperature alarm level					49291	49291	49291	49291					%	u8	1	1	100	75	R/W
49292	Ground water pump control signal	"Ground water pump control signal (0 = 0V-10V; 1= 10V-0V)"					49292	49292	49292	49292						s8	1	0	0	0	R/W
49293	Ground water pump min speed	Ground water pump voltage at min speed					49293	49293	49293	49293					V	u8	1	0	80	30	R/W
49295	AHPS External Addition start temperature.				49295										°C	u8	1	40	55	50	R/W
49296	AHPS External Addition stop temperature.				49296										°C	u8	1	44	59	54	R/W
49297	EME20 Activated	0=not activated, 1=activated	49297	49297	49297	49297	49297	49297	49297	49297	49297	49297	49297	49297		u8	1	0	1	0	R/W
49298	EME PV Panel Affect Pool	0=not affecting, 1=affecting	49298	49298	49298	49298	49298	49298	49298	49298		49298	49298	49298		u8	1	0	0	0	R/W
49301	Speed circ.pump add prio												49301		%	u8	1	0	0	0	R/W
49328	ERS 4 Exhaust Fan speed 4						49328	49328	49328	49328		49328	49328	49328	%	u8	1	0	100	100	R/W
49329	ERS 3 Exhaust Fan speed 4						49329	49329	49329	49329		49329	49329	49329	%	u8	1	0	100	100	R/W
49330	ERS 2 Exhaust Fan speed 4						49330	49330	49330	49330		49330	49330	49330	%	u8	1	0	100	100	R/W
49331	ERS 4 Exhaust Fan speed 3						49331	49331	49331	49331		49331	49331	49331	%	u8	1	0	100	80	R/W
49332	ERS 3 Exhaust Fan speed 3						49332	49332	49332	49332		49332	49332	49332	%	u8	1	0	100	80	R/W
49333	ERS 2 Exhaust Fan speed 3						49333	49333	49333	49333		49333	49333	49333	%	u8	1	0	100	80	R/W
49334	ERS 4 Exhaust Fan speed 2						49334	49334	49334	49334		49334	49334	49334	%	u8	1	0	100	30	R/W
49335	ERS 3 Exhaust Fan speed 2						49335	49335	49335	49335		49335	49335	49335	%	u8	1	0	100	30	R/W
49336	ERS 2 Exhaust Fan speed 2						49336	49336	49336	49336		49336	49336	49336	%	u8	1	0	100	30	R/W
49337	ERS 4 Exhaust Fan speed 1						49337	49337	49337	49337		49337	49337	49337	%	u8	1	0	100	0	R/W
49338	ERS 3 Exhaust Fan speed 1						49338	49338	49338	49338		49338	49338	49338	%	u8	1	0	100	0	R/W
49339	ERS 2 Exhaust Fan speed 1						49339	49339	49339	49339		49339	49339	49339	%	u8	1	0	100	0	R/W
49340	ERS 4 Exhaust Fan speed normal						49340	49340	49340	49340		49340	49340	49340	%	u8	1	1	100	75	R/W
49341	ERS 3 Exhaust Fan speed normal						49341	49341	49341	49341		49341	49341	49341	%	u8	1	1	100	75	R/W
49342	ERS 2 Exhaust Fan speed normal						49342	49342	49342	49342		49342	49342	49342	%	u8	1	1	100	75	R/W
49343	ERS 4 Supply Fan speed 4						49343	49343	49343	49343		49343	49343	49343	%	u8	1	0	100	100	R/W
49344	ERS 3 Supply Fan speed 4						49344	49344	49344	49344		49344	49344	49344	%	u8	1	0	100	100	R/W
49345	ERS 2 Supply Fan speed 4						49345	49345	49345	49345		49345	49345	49345	%	u8	1	0	100	100	R/W
49346	ERS 4 Supply Fan speed 3						49346	49346	49346	49346		49346	49346	49346	%	u8	1	0	100	80	R/W
49347	ERS 3 Supply Fan speed 3						49347	49347	49347	49347		49347	49347	49347	%	u8	1	0	100	80	R/W
49348	ERS 2 Supply Fan speed 3						49348	49348	49348	49348		49348	49348	49348	%	u8	1	0	100	80	R/W
49349	ERS 4 Supply Fan speed 2						49349	49349	49349	49349		49349	49349	49349	%	u8	1	0	100	30	R/W
49350	ERS 3 Supply Fan speed 2						49350	49350	49350	49350		49350	49350	49350	%	u8	1	0	100	30	R/W
49351	ERS 2 Supply Fan speed 2						49351	49351	49351	49351		49351	49351	49351	%	u8	1	0	100	30	R/W
49352	ERS 4 Supply Fan speed 1						49352	49352	49352	49352		49352	49352	49352	%	u8	1	0	100	0	R/W
49353	ERS 3 Supply Fan speed 1						49353	49353	49353	49353		49353	49353	49353	%	u8	1	0	100	0	R/W
49354	ERS 2 Supply Fan speed 1						49354	49354	49354	49354		49354	49354	49354	%	u8	1	0	100	0	R/W
49355	ERS 4 Supply Fan speed normal						49355	49355	49355	49355		49355	49355	49355	%	u8	1	1	100	75	R/W
49356	ERS 3 Supply Fan speed normal						49356	49356	49356	49356		49356	49356	49356	%	u8	1	1	100	75	R/W
49357	ERS 2 Supply Fan speed normal						49357	49357	49357	49357		49357	49357	49357	%	u8	1	1	100	75	R/W
49358	Night cooling	If the fan should have a higher speed when there is a high room temp and a low outdoor temp.	49358	49358	49358	49358	49358	49358	49358	49358		49358	49358	49358		u8	1	0	1	0	R/W
49359	Night cooling	If the fan should have a higher speed when there is a high room temp and a low outdoor temp.	49359	49359	49359	49359	49359	49359	49359	49359		49359	49359	49359		u8	1	0	1	0	R/W
49360	Night cooling	If the fan should have a higher speed when there is a high room temp and a low outdoor temp.	49360	49360	49360	49360	49360	49360	49360	49360		49360	49360	49360		u8	1	0	1	0	R/W
49361	Start room temp. night cooling		49361	49361	49361	49361	49361	49361	49361	49361		49361	49361	49361	°C	u8	1	20	30	25	R/W
49362	Start room temp. night cooling		49362	49362	49362	49362	49362	49362	49362	49362		49362	49362	49362	°C	u8	1	20	30	25	R/W
49363	Start room temp. night cooling		49363	49363	49363	49363	49363	49363	49363	49363		49363	49363	49363	°C	u8	1	20	30	25	R/W
49364	Night Cooling Min. diff.	Minimum difference between room temp and outdoor temp to start night cooling	49364	49364	49364	49364	49364	49364	49364	49364		49364	49364	49364	°C	u8	1	3	10	6	R/W
49365	Night Cooling Min. diff.	Minimum difference between room temp and outdoor temp to start night cooling	49365	49365	49365	49365	49365	49365	49365	49365		49365	49365	49365	°C	u8	1	3	10	6	R/W
49366	Night Cooling Min. diff.	Minimum difference between room temp and outdoor temp to start night cooling	49366	49366	49366	49366	49366	49366	49366	49366		49366	49366	49366	°C	u8	1	3	10	6	R/W
49367	ERS 4 accessory	Activates the ERS accessory					49367	49367	49367	49367		49367	49367	49367		u8	1	0	1	0	R/W
49368	ERS 3 accessory	Activates the ERS accessory					49368	49368	49368	49368		49368	49368	49368		u8	1	0	1	0	R/W
49369	ERS 2 accessory	Activates the ERS accessory					49369	49369	49369	49369		49369	49369	49369		u8	1	0	1	0	R/W
49370	External ERS 4 accessory min exhaust temp.						49370	49370	49370	49370		49370	49370	49370	°C	u8	1	0	10	5	R/W
49371	External ERS 3 accessory min exhaust temp.						49371	49371	49371	49371		49371	49371	49371	°C	u8	1	0	10	5	R/W
49372	External ERS 2 accessory min exhaust temp.						49372	49372	49372	49372		49372	49372	49372	°C	u8	1	0	10	5	R/W
49373	External ERS 4 accessory bypass temp.						49373	49373	49373	49373		49373	49373	49373	°C	u8	1	2	10	4	R/W
49374	External ERS 3 accessory bypass temp.						49374	49374	49374	49374		49374	49374	49374	°C	u8	1	2	10	4	R/W
49375	External ERS 2 accessory bypass temp.						49375	49375	49375	49375		49375	49375	49375	°C	u8	1	2	10	4	R/W
49376	External ERS 4 accessory bypass set temp.						49376	49376	49376	49376		49376	49376	49376	°C	u8	1	5	30	25	R/W
49377	External ERS 3 accessory bypass set temp.						49377	49377	49377	49377		49377	49377	49377	°C	u8	1	5	30	25	R/W
49378	External ERS 2 accessory bypass set temp.						49378	49378	49378	49378		49378	49378	49378	°C	u8	1	5	30	25	R/W
49379	External ERS 4 accessory bypass at heat						49379	49379	49379	49379		49379	49379	49379		u8	1	0	1	0	R/W
49380	External ERS 3 accessory bypass at heat						49380	49380	49380	49380		49380	49380	49380		u8	1	0	1	0	R/W
49381	External ERS 2 accessory bypass at heat						49381	49381	49381	49381		49381	49381	49381		u8	1	0	1	0	R/W
49430	AUX ERS Fire Place Guard	Activates ERS Fire Place Guard					49430	49430	49430	49430		49430	49430	49430		u8	1	0	0	0	R/W
49431	Stop Temperature Supply Air Heating	Stop temperature for supply air heating	49431	49431											°C	s16	1	100	400	170	R/W
