Hej and apologies for the choice of language, but I hope I can get some good advice here, as heat pumps are still quite rare in my country.
I have a Nibe F2016 Air/Water heat pump which has stopped producing any heat. The control panel does not report any alarm. On investigation I have found that the Soft Start module (a CARLO GAVAZZI - RSBS2325A2V12C24) is flashing the red alarm LED 5 times, which translates to "End of Ramp" alarm. I understand this means the compressor has failed to start within the expected time of 1 second.
Upon closer inspection I see that the "Main winding" (R) terminal on the Soft Start module is burnt/melted. It looks like this thing got too hot. But the wire is still connected.
So my question is, how confident can I be that this fault is purely the soft start module, as opposed to the compressor itself? My instinct is to replace the Soft Start with an equivalent one (maybe the 32A version instead of 25A). But I would like to check that the compressor is still working, because if I have to replace that I will probably get somebody to do the whole job for me.
Is there a safe way for me to bypass the soft start so I can test the compressor? Take the wire from the burnt R terminal and connect it to L? Or will I do more damage? I do have a basic multimeter I can use to test things. Or should I not bother with that, and just get a new Soft Start?
Many thanks