Skrivet av: coolmanbhn
« skrivet: 03 februari 2009, 21:35:31 »Heisann! For det første har du helt feil Nickname! Sanyo og din modell er noe av det ypperste innenfor det komersielle luft-luft VP markedet! Så å kalle seg Sanyohater fordi man har problem som du har blir helt feil!
Kjør selvdiagnostikk på følgende måte:
If the operation lamp flashes every half-second as soon as the power is
plugged in, there is either a faulty external ROM (for OTP data) on the
board of the indoor unit, an insertion fault, or the ROM is not installed.
Even when power is not being supplied, the malfunction mode will remain
in memory, so carry out the diagnosis as follows:
Procedure
(1) Restore power.
(2) Set the operation selector of the indoor unit to OFF (Self-Diagnosis).
(3) If an abnormality is sensed or an automatic protective action is taken, the self-diagnostic lamps No. 1, 2 and 3
respectively alternately blink on for 5 seconds and off for 2 seconds (the buzzer sounds when they go off).
When there is no abnormality detected, there will be no indication on self-diagnostic lamps
No. 1, 2 and 3, nor will the buzzer sound.
(4) The buzzer sounds three times to inform that the diagnosis has been completed.
(5) After the repair, always set the operation selector to DEMO and restore power to delete the contents of the
diagnosis. After that, set the operation selector to OFF to check that the contents were deleted.
Deretter kommer sannsynligvis People sensor til å blinke, samt Timer og Operation til å lyse! Dette betyr som følger:
Compressor motor revolution abnormality som igjen betyr: Failure in DC compressor rotation which is not
caused by defective HIC!
Som igjen betyr at din kompressor er "worn out" denne må byttes! Sjekk dette og kom tilbake med hvilken blinking din innedel indikerer!
Mvh
Bjarne Betjent
Kjør selvdiagnostikk på følgende måte:
If the operation lamp flashes every half-second as soon as the power is
plugged in, there is either a faulty external ROM (for OTP data) on the
board of the indoor unit, an insertion fault, or the ROM is not installed.
Even when power is not being supplied, the malfunction mode will remain
in memory, so carry out the diagnosis as follows:
Procedure
(1) Restore power.
(2) Set the operation selector of the indoor unit to OFF (Self-Diagnosis).
(3) If an abnormality is sensed or an automatic protective action is taken, the self-diagnostic lamps No. 1, 2 and 3
respectively alternately blink on for 5 seconds and off for 2 seconds (the buzzer sounds when they go off).
When there is no abnormality detected, there will be no indication on self-diagnostic lamps
No. 1, 2 and 3, nor will the buzzer sound.
(4) The buzzer sounds three times to inform that the diagnosis has been completed.
(5) After the repair, always set the operation selector to DEMO and restore power to delete the contents of the
diagnosis. After that, set the operation selector to OFF to check that the contents were deleted.
Deretter kommer sannsynligvis People sensor til å blinke, samt Timer og Operation til å lyse! Dette betyr som følger:
Compressor motor revolution abnormality som igjen betyr: Failure in DC compressor rotation which is not
caused by defective HIC!
Som igjen betyr at din kompressor er "worn out" denne må byttes! Sjekk dette og kom tilbake med hvilken blinking din innedel indikerer!
Mvh
Bjarne Betjent