Författare Ämne: IVT-protokoll (Rego 6xx)  (läst 97991 gÃ¥nger)

0 medlemmar och 1 gäst tittar på detta ämne.

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #90 skrivet: 14 mars 2010, 10:33:49 »
Hi everyone!

(Working on fulfilling the license agreement fulda ;) )

Long time no see.. Now I have some time to spend on the logging interface again. I sat down yesterday and started thoroughly analyzing my circuit board. Found that the problem I had may be due to me mixing concepts up..

I used a flat 9-pin cable (like a P-ATA connector cable) and I had according to Fulda's design used pins 2,3,4 and 5 on REGO-side and 2,3 and 5 on PC-side. However, my suspicion was that I had confused the leads with the RS-232 connector numbering. And therefore I re-soldered the board to use leads
3,5,7 and 9 on the REGO-side and 3,5 and 9 on the PC-side. No luck however.. the results differ almost time I run the script, the current result is:
sri@loggis:~/bosch$ ./ivt.pl
Dest:  FA 00 00 00 0B
Dest:  88 0F 00 00 00
Dest:  0B FA 00 00 00
Dest:  0B F4 00 00 00
Dest:  0B 41 08 00 00
Dest:  0B 10 D0 08 00
Dest:  00 0B 20 00 00
Dest:  00 80 00 00 00
Dest:  00 20 00 00 00
Dest:  40 00 00 00 00
Dest:  40 00 00 00 00
Dest:  20 00 00 00
Err rego version:HHHHHL
== Sun Mar 14 09:56:38 2010 ==

Obviously, I somewhere took a wrong turn and need a little guidance to at least have the interface following fulda's design before I can start trying to figure out why I only get junk from (and to?) the REGO.

From the pc-side my interface is connected to RS-232, pin 1 of the cable is connected to the power supply of the USB-port. After roughly 2m of flat cable, the cable ends in the PC-side of the interface. Between the interface hardware and the REGO RS232-port there is only about 5cm of cable.


The read leads are pin 1 on the connectors.

Thank you for reading :)
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #91 skrivet: 14 mars 2010, 12:09:02 »
(Working on fulfilling the license agreement fulda ;) )

not received yet - when I will receive, you will see it here: http://rago600.sourceforge.net/postcards/
(all received poctcards are here) {only 1 user huvuddunk}

I used a flat 9-pin cable (like a P-ATA connector cable)

yes - cables from old mainboards are fine - I'm using it so offen.

Obviously, I somewhere took a wrong turn and need a little guidance to at least have the interface following fulda's design before I can start trying to figure out why I only get junk from (and to?) the REGO.

the data you received look like noise.
If cable length is 5cm - it would be OK.

have you checked the diagram at: http://rago600.sourceforge.net/FAQ.html

it is usual, that users forgeting to connect power pins of max232 (pins 15 and 16)

Jindra

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #92 skrivet: 14 mars 2010, 13:28:17 »
Correct Fulda, it was pins 15 and 16 that I connected wrongfully (see picture). I now connected them according to the design and got:
sri@loggis:~/bosch$ ./ivt.pl
Dest:  81 02 00 04 0F
Dest:  00 00 00 0B 60
Dest:  20 04 0F 00 00
Dest:  00 0B 81 02 00
Dest:  04 0F 00 00 00
Dest:  0B 81 02 00 04
Dest:  0F 00 00 00 0B
Dest:  4C 00 04 0F 00
Dest:  00 00 0B 81 02
Dest:  00 04 0F 00 00
Dest:  00 0B 81 7F 00
Dest:  00 00 00 00 00
Err rego version:HHHHHH
== Sun Mar 14 13:25:47 2010 ==

Note; I tried both pin-configurations.
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #93 skrivet: 14 mars 2010, 15:31:21 »
Correct Fulda, it was pins 15 and 16 that I connected wrongfully (see picture). I now connected them according to the design and got:
sri@loggis:~/bosch$ ./ivt.pl
Dest:  81 02 00 04 0F
Dest:  00 00 00 0B 60
Dest:  20 04 0F 00 00
Dest:  00 0B 81 02 00
Dest:  04 0F 00 00 00
Dest:  0B 81 02 00 04
Dest:  0F 00 00 00 0B
Dest:  4C 00 04 0F 00
Dest:  00 00 0B 81 02
Dest:  00 04 0F 00 00
Dest:  00 0B 81 7F 00
Dest:  00 00 00 00 00
Err rego version:HHHHHH
== Sun Mar 14 13:25:47 2010 ==
Note; I tried both pin-configurations.

OK - your question is more for autistic people. I have added colors to your example.
Dest:  81 02 00 04 0F
Dest:  00 00 00 0B 60
Dest:  20 04 0F 00 00
Dest:  00 0B 81 02 00
Dest:  04 0F 00 00 00
Dest:  0B 81 02 00 04
Dest:  0F 00 00 00 0B
Dest:  4C 00 04 0F 00
Dest:  00 00 0B 81 02
Dest:  00 04 0F 00 00
Dest:  00 0B 81 7F 00
Dest:  00 00 00 00 00

you can see, that here is some echo - it mean you have short connected transmited and received data.

check if you have not short connect between pins 2/3 on rego header, 1/5 on optocoupler, 4/7 on optocoupler, 11/12 on max232, 13/14 on max 232, or 2/3 on PC header.

Also check if you counting pins on components:
1   16
2   15
3   14
« Senast ändrad: 14 mars 2010, 15:35:10 av fulda »

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #94 skrivet: 22 mars 2010, 18:38:04 »
Hi everyone!

Out of frustation I decided to solder a new filter. I just connected it and it still doesn't work!

With my multimeter, I got the following results:
Vcc: 10.6V
pin2 (mot GND): 8.4V
pin6 (mot GND): 5.4V

However, when I out of curiosity read the specification on the Max232 in the ELFA-catalog, I noticed that the capacitors should be 1uF, not 10uF which I mounted...

Have I found the problem or what do you think?

Regards, Stefan

Edit: I am using MAX232CPE (https://www1.elfa.se/data1/wwwroot/webroot/Z_DATA/07302326.pdf), can that possibly be a potential source of errors?

Edit2: I found that I had mounted the capacitors with the wrong polarity, so hopefully my problems will disappear when I get home tonight..
« Senast ändrad: 23 mars 2010, 11:14:57 av srick »
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #95 skrivet: 23 mars 2010, 14:40:53 »
With my multimeter, I got the following results:
Vcc: 10.6V
pin2 (mot GND): 8.4V
pin6 (mot GND): 5.4V

Where you have connected ground/com of your multimeter??
Vcc is allowed between +4,5 to +5.5V not 10,6!!!!
(pins 15 = gnd and pin 16=vcc)

However, when I out of curiosity read the specification on the Max232 in the ELFA-catalog, I noticed that the capacitors should be 1uF, not 10uF which I mounted...

... some versions - mainly signed as max 3232


Edit: I am using MAX232CPE (https://www1.elfa.se/data1/wwwroot/webroot/Z_DATA/07302326.pdf), can that possibly be a potential source of errors?
CPE is fine - it mean only plastic package with temperature +5 to +55C or something like that

Edit2: I found that I had mounted the capacitors with the wrong polarity, so hopefully my problems will disappear when I get home tonight..

wrong polarity is not so bad - it dramaticaly decreasing capacity, but sometime working

Your problem can be powering of max - are you sure, that you have connected pins 15 and 16 as described in mnemotechnic schematic?

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #96 skrivet: 23 mars 2010, 15:24:27 »
Citera
Where you have connected ground/com of your multimeter??
Vcc is allowed between +4,5 to +5.5V not 10,6!!!!
(pins 15 = gnd and pin 16=vcc)
I measured Vcc between Usb-out and RS232-GND, not on MAX232.

Citera
wrong polarity is not so bad - it dramaticaly decreasing capacity, but sometime working

Your problem can be powering of max - are you sure, that you have connected pins 15 and 16 as described in mnemotechnic schematic?
Well, I have not connected 15 and 16 at all, they are not on the schematic (http://rago600.sourceforge.net/ivt_serial.gif). Pins 2 and 6 however are connected as on the schematic
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #97 skrivet: 23 mars 2010, 18:04:58 »
Ok, some new measurements:
pin15-16: 0.27V
pin2-6: 0.36V
Voltage over USB compared to serial GND is 10.5V

If I haven't misread the specification from ELFA, should there not be a capacitor between pins 2 and 16?

Could the MAX232 be faulty? I have now checked this implementation a number of times
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #98 skrivet: 23 mars 2010, 20:04:08 »
Ok, some new measurements:
pin15-16: 0.27V
pin2-6: 0.36V
Voltage over USB compared to serial GND is 10.5V

If I haven't misread the specification from ELFA, should there not be a capacitor between pins 2 and 16?

Could the MAX232 be faulty? I have now checked this implementation a number of times

see: http://rago600.sourceforge.net/ivt_ser2a.GIF
serial GND (pin 5) is connected to pin 15
USB power (red) is connected to pin 16

You saying, that have 10,5V between GND and power, and 0,27V between pins 15 and 16???

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #99 skrivet: 23 mars 2010, 20:47:42 »
Hi fulda and thanks for you reply,

I haven't seen that schematic before. I've implemented my filter according to http://rago600.sourceforge.net/ivt_serial.gif, is that wrong?

Thanks again  Thumbsup
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #100 skrivet: 24 mars 2010, 09:59:03 »
I haven't seen that schematic before. I've implemented my filter according to http://rago600.sourceforge.net/ivt_serial.gif, is that wrong?

I informed you about this schematic 14 Mars 2010, 12:09:02 - you not read my post cerrfully   ::)

as statet on page FAQ - the schematic is same, only this is standard electrical schematic and this is mnemotechnic.

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #101 skrivet: 24 mars 2010, 10:15:23 »
I'm sorry fulda but I don't understand the mnemotechnic one, it seems to do the opposite of the electrical schematic..  ;D

However, one important question; in which manner are you labeling the pins? The 9-pin DSUBconnector label the pins:
   1
2
   3
4
   5
6
   7
8
   9

(this is the way I soldered the connectors)

but in the schematic you instead use

   1
6
   2
7
   3
8
   4
9
   5

I'm sorry if this sounds like complains - it's not! - I just want to know what I did wrong :) I tried both ways but none worked..

Thank you for your patience
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad srick

  • Expert pÃ¥ värmepump
  • ****
  • Antal inlägg: 458
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #102 skrivet: 24 mars 2010, 13:50:01 »
I just re-soldered the connector pins according to the electric schematic, now I'll just have to wait until I get home to see the results...  studs
Bosch EHP9-LW/M med 150m aktivt borrhål och Nibe UKV-100, Veneto FST34 fyrrörskonvektor, innegivare. Bytte från vattenburen el i oktober 2009, enrörssystem med klena enpanelsradiatorer. Souterränghus på 140+50 (inkl 30m2 garage, ca 15grader) från 1982, två mil norr om Göteborg, välisolerad vind men oisolerad platta.

Utloggad fulda

  • Kan värmepumpar
  • ***
  • Antal inlägg: 79
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #103 skrivet: 24 mars 2010, 15:52:16 »
I just re-soldered the connector pins according to the electric schematic, now I'll just have to wait until I get home to see the results...  studs

Regarding pinout - in my notes is refetence to this page, where is example. I'm not writing it into docs, because there are numbers on pins. If you will use zoom magnifier to see it.
Also in both schematics is picture of connector which presenting that pinout is:
1 2 3 4 5
 6 7 8 9

Utloggad markwyllie

  • Nybörjare
  • *
  • Antal inlägg: 6
  • Karma +0/-0
SV: IVT-protokoll (Rego 6xx)
« Svar #104 skrivet: 31 mars 2010, 10:43:07 »
I have version  3.05 and i can reach the pump with an ethernet cabel.

Best regards

Clarre
Clarre - I have this working with Wifi (see previous post), using the Wifly GSX interface from roving networks (and all Fuldas code). It allows me to do what you want - remote control of heat pump. But it does need some soldering. Maybe you could learn ?
I want to control mine from the web , not just the lounge.

nibe, ctc, baxi, golvvärme, solenergi Energibutiken.se smarta varor på nätet, leverans till dörren
 


Annonser

Right Block

Vibrationsdämpare
Besök vår webshop, klicka här!
Energioffert.se
Energibutiken.se smarta varor på nätet, leverans till dörren
luftvärmepumpar, tillbehör, installationsmaterial, vi har allt!
Annonspriser
Ad
Energibutiken.se smarta varor på nätet, leverans till dörren
Besök oss idag
Annonsera i Värmepumpsforum, klicka här för att ställa e-postfråga och få mer info.
140x140vpforum-11.gif
kontakta oss för pris!