Författare Ämne: IVT 290 =>89C !!! (English)  (läst 2396 gÃ¥nger)

0 medlemmar och 1 gäst tittar på detta ämne.

Utloggad James

  • Nybörjare
  • *
  • Antal inlägg: 5
  • Karma +0/-0
  • Värmepump eller värmepumpar?
IVT 290 =>89C !!! (English)
« skrivet: 24 april 2017, 12:19:11 »
I can read Swedish so all comments appreciated!

Executive summary (tl;dr):  GT3 (hot water temperature) goes to about 90C... almost boiling tap water.  There seems to be no way to set this temperature.

Question:  How do I control the varmvattentemperaturen?
{edit: found this post

Problem was a bad triac on a controller board.  Sound like my problem?
}

The details: I live in a rented house with an IVT 290, no heat pump.  The IVT received no maintenance for many years... seemed to work fine but every now and then I would have to reset the fuse on the bottom of the control panel.  A couple weeks ago it started to require a reset every day so I figured something was wrong.

What I've done:

Avluftning.  I went around to every radiator in the house and bled the air.  A couple of them had quite a lot.  I also bled the tank in the heater until water came out.  (using the valve next to the pressure relief valve/hose marked 2.5atm pressure.  the tank had a lot of air in it.)

Filling.  I opened the supply valve on the bottom left while avluftning to add water to the heating system.  Once the system was running and warm, I adjusted that valve again until the pressure in the system was around 1.5atm.

The system seemed to operate better now (not blowing the breaker) but the tap water in the house was really warm, close to 80C!  This causes the pressure in the heating system to go up also... above the stated max pressure of 2.5atm.

I cannot run the system now without GT3 going to max.

« Senast ändrad: 24 april 2017, 14:12:22 av James »

Inloggad Carl N

  • Manual-nörd
  • Guldmedlem
  • Dignitär inom värmepump
  • ******
  • Antal inlägg: 29338
  • Karma +18/-7
  • Kön: Man
  • Alien snowman.
SV: IVT 290 =>89C !!! (English)
« Svar #1 skrivet: 24 april 2017, 13:53:01 »
My guess is thet the relay to the electric heater is stuck.
It can also be a bad triac as in the link.
You should contact an electrician to check and repair.
Huset: NIBE 1215-5, 120 m aktivt borrdjup, 127 m2 boyta 53 m2 biyta, suterräng byggt 1970. Tidigare 2,5 kbm olja/år, huset tilläggsisolerat i samband med VP-installationen. FST34+1 som frikyla.
Ca 5500 kWh i drivenergi för VP-drift, ca 5500 kWh HH-el + komfortgolvvärme i snitt/år.
---------------------------------------------------------------------------------------------------
Fritidshuset, NIBE 1245-8, 160 m aktivt borrdjup, ca 150 m2 boarea + en liten källare från 1912.

Utloggad James

  • Nybörjare
  • *
  • Antal inlägg: 5
  • Karma +0/-0
  • Värmepump eller värmepumpar?
SV: IVT 290 =>89C !!! (English)
« Svar #2 skrivet: 24 april 2017, 14:01:46 »
I just found 8 MOC3062 triac/optocouplers in my spare parts.  They seem to be functionally equivalent (just can take higher voltage) so I plan to replace them all now and see if my problem is the same as in the link I posted above.  Unfortunately I don't have any compatible relays on hand.

Utloggad James

  • Nybörjare
  • *
  • Antal inlägg: 5
  • Karma +0/-0
  • Värmepump eller värmepumpar?
SV: IVT 290 =>89C !!! (English)
« Svar #3 skrivet: 24 april 2017, 15:48:10 »
I took out the board:

and found a problem on the back of that large component,
 lower right (appears to be a relay)
with the following marking

If I slide the solenoid on the relay, 2-2' and 3-3' go from open to closed.  1-1' stays open.

I'm not sure how a relay staying open would cause an overheating condition, so I'm now unsure how to proceed. 

Anyone have a recommendation for someone near Gothenburg?

edit:  called IVT and they referred me to this link for a 2373 SEK replacement card.  I would really prefer to figure out what this part is instead!
JSEnergi Kraftkort
« Senast ändrad: 24 april 2017, 16:17:26 av James »

Utloggad James

  • Nybörjare
  • *
  • Antal inlägg: 5
  • Karma +0/-0
  • Värmepump eller värmepumpar?
SV: IVT 290 =>89C !!! (English)
« Svar #4 skrivet: 24 april 2017, 17:07:43 »
Even if I could find out the part number for that relay, find one, replace it, and test it, there still could be another cascaded error.  And meanwhile my wife will be taking cold showers and my real work will be on hold.  Sooooo......

I called the landlord.  They will cover the cost of getting a professional to finish the job. 

In the meantime I wonder if I can run this on manual mode if I put the card back in even though that relay (and who knows what else) is bad.

Thanks to everyone that had a read, and thanks to Carl for the reply!

Inloggad Carl N

  • Manual-nörd
  • Guldmedlem
  • Dignitär inom värmepump
  • ******
  • Antal inlägg: 29338
  • Karma +18/-7
  • Kön: Man
  • Alien snowman.
SV: IVT 290 =>89C !!! (English)
« Svar #5 skrivet: 25 april 2017, 16:35:54 »
Sorry, but the manual for IVT290 don't tell so much.
But there is a switch for manual handling on the top of the electrix box, then you should be able to regulate the temperature by the thermostat (20) in the manual side 25.
You must also control the temperature in the house with the shunt.

http://doc.ivt.se/download.asp?fn=Manual_IVT290_sv.pdf
Huset: NIBE 1215-5, 120 m aktivt borrdjup, 127 m2 boyta 53 m2 biyta, suterräng byggt 1970. Tidigare 2,5 kbm olja/år, huset tilläggsisolerat i samband med VP-installationen. FST34+1 som frikyla.
Ca 5500 kWh i drivenergi för VP-drift, ca 5500 kWh HH-el + komfortgolvvärme i snitt/år.
---------------------------------------------------------------------------------------------------
Fritidshuset, NIBE 1245-8, 160 m aktivt borrdjup, ca 150 m2 boarea + en liten källare från 1912.

Utloggad James

  • Nybörjare
  • *
  • Antal inlägg: 5
  • Karma +0/-0
  • Värmepump eller värmepumpar?
SV: IVT 290 =>89C !!! (English)
« Svar #6 skrivet: 25 april 2017, 16:51:43 »
Curiously, I turned it on auto this afternoon thinking to toggle it into manual and I could see and hear a sizzle at that element relay when I switched it into manual.  I so I left it in auto and observed.  It is holding a steady normal temp and pressure currently several hours running.  Did I weld something back together?  lol.  I have a pro arriving tomorrow.

Ellgers

  • Gäst
Ellgers
Buy Viagra No Perscription EllVonalf
« Svar #7 skrivet: 16 augusti 2019, 16:57:22 »
Keflex To Treat Arthritis  cialis online Strep And Amoxicillin Lasix Overnight Shipping 

nibe, ctc, baxi, golvvärme, solenergi Mer än 20 års erfarenhet av värmepumpar
 


Annonser

Right Block

Vibrationsdämpare
Besök vår webshop, klicka här!
Energioffert.se
Energibutiken.se smarta varor på nätet, leverans till dörren
luftvärmepumpar, tillbehör, installationsmaterial, vi har allt!
Annonspriser
Ad
CitCop - Värmepumpar med installation i hela Sverige
Besök oss idag
Annonsera i Värmepumpsforum, klicka här för att ställa e-postfråga och få mer info.
140x140vpforum-11.gif
kontakta oss för pris!